Testing of electrical installations
Before any testing of low voltage electrical installations (and equipment) is carried out, a detailed physical inspection must be made to ensure that everything is to a relevant National standard, erected/installed in compliance with the IEE Regulations and not damaged in such a way that it could cause danger.
In order to comply with these requirements, the Regulations give a checklist of items that, where relevant, should be inspected. However, before such an inspection, and test for that matter, is carried out, certain information must be available to the verifier.
Interestingly, one of the items on the checklist isthe presence of diagrams, instructions and similar information. If these are missing, there is a deviation from the Regulations.
Another item on the list is the verification of conductors for current carrying capacity and voltage drop in accordance with the design. How could this be verified without all the information?
A 32A type B circuit breaker protecting a length of 4.0 mm2 conductor may look reasonable, but is it correct and, unless you are sure, are you prepared to sign to say that it is?
General testing checklist
Let us look then at the general content of the checklist:
Check #1 – Connection of conductors
Are terminations electrically and mechanically sound? Is insulation and sheathing removed only to a minimum to allow satisfactory termination?
Check #2 – Identification of conductors
Are conductors correctly identified in accordance with the regulations?
Check #3 – Routing of cables
Are cables installed such that account is taken of external influences, such as mechanical damage, corrosion and heat?
Check #4 – Conductor selection
Are conductors selected for current carrying capacity and voltage drop in accordance with the design?
Check #5 – Connection of single pole devices
Are single pole protective and switching devices connected in the line conductor only?
Check #6 – Accessories and equipment
Are all accessories and items of equipment correctly connected?
Check #7 – Thermal effects
Are fire barriers present where required and protection against thermal effects provided?
Check #8 – Protection against shock
What methods have been used to provide protection against electric shock?
Check #9 – Mutual detrimental influence
Are wiring systems installed so that they can have no harmful effect on non-electrical systems or so that systems of different currents or voltages are segregated where necessary?
Check #10 – Isolation and switching
Are the appropriate devices for isolation and switching correctly located and installed?
Check #11 – Undervoltage
Where undervoltage may give rise for concern, are there protective devices present?
Check #12 – Protective devices
Are protective and monitoring devices correctly chosen and set to ensure automatic disconnection and/or overcurrent?
Check #13 – Labelling
Are all protective devices, switches (where necessary) and terminals correctly labelled?
Check #14 – External influences
Have all items of equipment and protective measures been selected in accordance with the appropriate external influences?
Check #15 – Access
Are all means of access to switchgear and equipment adequate?
Check #16 – Notices and signs
Are danger notices and warning signs present?
Check #17 – Single line diagrams / Wiring schemes
Are diagrams, instructions and similar information relating to the installation available?
Check #18 – Erection methods
Have all wiring systems, accessories and equipment been selected and installed in accordance with the requirements of the Regulations? Are fixings for equipment adequate for the environment?
Once all the relevant items have been inspected, providing there are no defects that may lead to a dangerous situation when testing, the actual testing procedure can start.
Reference // Electric Wiring: Domestic – Brian Scaddan IEng, MIET
HI. thats great explaination but i like to discuss about glands requirements? I understand that if is mandatory cor power cabld that one gland one cable? But what about numerous controls cable or we can create a rectangle cut with rubber ipx rating insulation to protect wires from damage.
Great information, I’m a professional electrition and I highly appreciate the information you provide, I suggest that you provide more information about how to do safety tests for houses insulation.
Dear sir,Csanyi;
you do the best job for all around the world so that many Electricians can improve their ability of areas of electrical and technology fields.
Just I am an Electrical and Computer Engineering student, interested in all what you provide in this site.
I would like to thank you at all.
Dear Sir,
I would like to thank you very much. I am one of the beneficiary of this web site. please keep it up.
Tesfaye Abebe.
Ethiopia.