Home / Technical Articles / Cable sizing of sub-main electrical circuits (working examples)
Few words about Sub-main circuits
A sub-main electrical circuit can be defined as a circuit connected directly from the main LV switchboard to a sub-main distribution panel or a rising main for final connection of the minor current-using equipment.
Cable Sizing Of Sub-Main Electrical Circuits (Working Examples)
The Code requires that the maximum copper loss in every sub-main circuit should not exceed 1.5% of the total active power transmitted along the circuit conductors at rated circuit current.
Similar approach could be followed for sizing conductor as for feeder circuit. However, assumption has to be made in the design for various characteristics of the sub-main circuit including design current, expected harmonic current (THD) in the circuit, degree of unbalance, etc.
Alternatively, an energy efficiency method introduced by the Code could also be used for preliminary cable sizing. This energy efficiency method for cable sizing requires the calculation of the maximum allowable conductor resistance based on the maximum copper loss requirement as stipulated in the code.
For a 3-phase 4-wire circuit (assuming balanced, linear or non-linear):
Active power transmitted via the circuit conductors //
P = √3 · UL · I· cosθ
Total copper losses in conductors //
Pcopper =  (3 · Ib2 + IN2) · r · L
where:
  • UL – Line to line voltage, 380V
  • Ib – Design current of the circuit in ampere
  • I1 – Fundamental current of the circuit in ampere
  • IN – Neutral current of the circuit in ampere
  • cosθ – Displacement power factor of the circuit
  • r – a.c. resistance / conductor/ metre at the conductor operating temperature
  • L – Length of the cable in metre
Percentage copper loss with respect to the total active power transmitted:
Therefore,
Max. a.c. resistance
Table 4.2A and 4.2B in the Code provide a quick initial assessment of cable size required for the common cable types and installation methods used in Hong Kong for this example.
The tabulated current rating of the selected cable could then be corrected by applying the correction factors accordingly. The effective-current carrying capacity of the selected cable must be checked so that its value is larger than or equal to the nominal rating of the circuit protective device.
Calculate an appropriate cable size
A 3-phase sub-main circuit having a design fundamental current of 100A is to be wired with 4/C PVC/SWA/PVC cable on a dedicated cable tray. Assuming an ambient temperature of 30°C and a circuit length of 40m, calculate an appropriate cable size for the following conditions:
  1. CASE 1 // Undistorted balanced condition using traditional method (cosθ = 0.85)
  2. CASE 2 // Undistorted balanced condition with a max. copper loss of 1.5% (cosθ = 0.85)
Case #1
Undistorted balanced condition using conventional method:
  • Ib = 100A
  • In = 100A
  • It(min) = 100A
Assume the correction factors Ca, Cp, Cg and Ci are all unity.
Itmin
Refer to BS7671:2008, The Requirements for Electrical Installations,
Table 4D4A for 25mm2 – 4/C PVC/SWA/PVC cable  – It = 110A
Table 4D4B for r = 1.5mV/A/m x = 0.145mV/A/m (negligible)
Conductor operating temperaturet= 30 + 1002 / 1102 · (70 – 30) = 63°C
Ratio of conductor resistance at 63°C to 70°Cr = (230 + 63) / (230 + 70) = 0.98
Voltage dropu = 1.5mV/A/m · 0.85 · 0.98 · 100A · 40m = 5V (1.3%)
Active power transferred (P)P = √3 · 380V · 100A · 0.85 = 56kW
Total copper losses in conductors (Pcu)= 3 · 1002 A2 · 0.0015Ω/m / √3 · 0.98 · 40m
= 1.02kW (1.82%)
(Cable size selected is not acceptable if the maximum allowable copper loss is 1.5%)
Case #2
Undistorted balanced condition with a maximum copper loss of 1.5%
(cosθ = 0.85)
Maximum copper loss method using Table 4.2A in the Code for initial assessment of an approximate conductor size required by calculating the max. conductor resistance at 1.5% power loss:
From Table 4.2A 35 mm2 – 4/C PVC/SWA/PVC cable having a conductor resistance of 0.625mΩ/m is required. Refer to BS7671:2008, The Requirements for Electrical Installations:
Table 4D4A for 35mm2 4/C PVC/SWA/PVC cable It = 135A
Table 4D4B for r = 1.1mV/A/m x = 0.145mV/A/m
Conductor operating temperaturet= 30 + 1002 / 1352 · (70 – 30) = 52°C
Ratio of conductor resistance at 52°C to 70°Cr = (230 + 52) / (230 + 70) = 0.94
Voltage dropu = 1.1mV/A/m · 0.85 · 0.94 · 100A · 40m = 3.5V (0.92%)
Total copper losses in conductors (Pcu)= 3 · 1002 A2 · 0.0011Ω/m / √3 · 0.94 · 40m
= 716kW (1.28%)
(Cable size selected is acceptable, i.e. power loss < 1.5%, under undistorted and balanced conditions)
RELATED TABLES //
TABLE 4.2A
Multicore Armoured and Non-armoured Cables (Copper Conductor), Conductor Resistance at 50 Hz Single-phase or Three-phase a.c.
Go back to Cases ↑
TABLE 4.2B
Single-core PVC/XLPE Non-armoured Cables, with or without sheath (Copper Conductor), Conductor Resistance at 50 Hz Single-phase or Three-phase a.c.
TABLE 4.2B Single-core PVC/XLPE Non-armoured Cables, with or without sheath (Copper Conductor), Conductor Resistance at 50 Hz Single-phase or Three-phase a.c.
TABLE 4.2B
Go back to Cases ↑
TABLE 4D4A
Multicore armoured 70C thermoplastic insulated cable
TABLE 4D4A - Multicore armoured 70C thermoplastic insulated cable
TABLE 4D4A – Multicore armoured 70C thermoplastic insulated cable
Go back to Cases ↑
TABLE 4D4B
Voltage drop (per ampere per-metre)
TABLE 4D4B - Voltage drop (per ampere per-metre)
TABLE 4D4B – Voltage drop (per ampere per-metre)
Go back to Cases ↑
Reference // Code of Practice for Energy Efficiency of Electrical Installations – Electrical and Mechanical Services Department – The Government of the Hong KongSpecial Administrative Region
21 Comments
  1. Abdirahman
    Aug 15, 2020
    Hello well calculation, how about distribution transformed cable in 100Kva in secondery side and distance?
  2. Md Fazlul Haque
    Jun 29, 2020
    Dear Sir,
    How can I upload data/article at this page.
    Best Regards
    Md Fazlul Haque
    Bangladesh
  3. Md Fazlul Haque
    Jun 29, 2020
    how do u get the vale of 230 in case of ratio of resistance calculation, please. overall nice article..
  4. Raghupathy
    Jun 26, 2020
    Articles are very useful for Project engineers
  5. Maximus
    Jun 26, 2020
    It means 35mmsq size of L1, L2, and L3, with 16mmsq size of Neutral, and 16mmsq size of Earth Cable.
  6. demewoz
    Jan 17, 2019
    i am interested on electrical engineering work
  7. hossain
    Jul 04, 2018
    Can pls explain me what is mean 3×35+16+16 for the cable size ?
    • Milione Fenias Changala
      May 21, 2020
      Good article..
      The designation of size cable means 3 line with cross section 35, plus neutral and earth cable with 16 mm of cross section..
      Kindly regards.
      m.Changala
  8. Muhammad Kuraan
    Jun 07, 2018
    Dear
    If the main feeder cable is 70 mm, what is the size of the cable connected between Busbar and Main Circuit Breaker
    Muhammad Kuraan
    Ambassador
  9. Kgashane Junior Shai
    Jun 06, 2018
    I’m looking for a 40m supply cable for a distribution board
  10. nitin
    May 10, 2015
    Good one
  11. Tariku Tesfaye
    May 08, 2015
    I need sample disign for building electrical installation
  12. D.V.SHIVANAND
    May 06, 2015
    very good article
  13. D.V.SHIVANAND
    May 06, 2015
    it is a very good article
    we being in practical electrical training is very usefull
  14. IMTIYAZ
    May 04, 2015
    Good article, however would be good to know the table/code reference for the tables. Please comment on references and standard used,, thanks
  15. Robert Yates, EE/PE, Specifying Engineer
    Apr 30, 2015
    Please cite the code, chapter & verse(s) being referenced herein. Good examples but I’m not familiar with the tables used. Thank you!
  16. mohammed
    Apr 30, 2015
    mr. Manuel Bolotinha
    i humbly request you to mail me electrical (&other related material whether its electrical or instrumentation or electronics) design & installation material.
    regards
    [email protected]
    [email protected]
  17. Omar Cerda
    Apr 30, 2015
    Good presentation.
  18. Manuel Bolotinha
    Apr 30, 2015
    To size a cable, no matter if it is LV a sub-main circuit or not, is also necessary to verify if the cable withstand the thermal stress due to short-circuit current.
    The standars on which the tables are based should be indicated (IEC; ANSI/IEEE; BSI; CENELEC?)
    I would like to see these articles written in a more professional way, showing all the required calculations and considerations.
    Please let me know how I can cooperate with this p+latform and upload articles.
    Manuel Bolotinha – Electrical Engineer and Certified Professional Instructor.
    • mohammed
      Apr 30, 2015
      regards
      [email protected]
      [email protected]
      • sontakke.s.v.
        May 01, 2015
        Dear E,K. Greetings.Thanks for a very imp.technical info. about data to be considered for selection for sub circuits.
        Pl. arrange to e mail such useful tech data for Electrical designs.
        Warmest regards.
  +  fifty seven  =  65