Home / Technical Articles / 9 rules for correct cabling of the Modbus RS485 communication systems
Modbus RS485 cabling rules
The cabling of the industrial communication systems (Modbus RS485) is different in some ways from the cabling used for power cabling and the electrician may experience some difficulties if he is not an expert in Modbus communication networks.
9 rules for correct cabling of the Modbus RS485 industrial communication systems
9 rules for correct cabling of the Modbus RS485 industrial communication systems (photo credit: Jose Rivas via Flickr)
A Modbus RS485 connects a Master device to one or more Slave devices. Henceforth, we shall consider Slave devices to be measuring instruments with serial communication, even if the cabling is similar for all Modbus devices.
The main rules are set out below that must be followed for the cabling of this type of network:
  1. Connection port
  2. Connection between the devices
  3. Maximum distance and maximum number of devices
  4. Use of repeaters
  5. Type of cable to use
  6. Connecting to the terminals
  7. Earth connection of the shield
  8. Termination resistance
  9. Connection to personal computer
1. Connection port
Each device has a communication port with two terminals, which are indicated for the sake of convenience as A and B. In these two terminals the communication cable is connected so that all the devices that take part in the communication are connected in parallel.
All the ‘A’ terminals must be connected together and all the ‘B’ terminals must be connected together respectively.
Inverting the ‘A’ and ‘B’ connections of a device does not only prevent it from communicating but may also stop the entire communication system from working owing to incorrect direct (polarisation) voltage found on the terminals of the incorrectly connected device.
In order to avoid errors when many devices are connected, cables of the same colour should be used for all the connections to the terminals A and cables of the same colour should be used for all the connections to the terminals B of the various devices (e.g. white for A and blue for B).
This makes it easier to identify cabling errors. The communication port on the Master device, whatever it is, has two terminals that correspond to A and B.
Go back to Modbus RS485 cabling rules ↑
Unlike what happens in many energy distribution systems, the manner in which the devices are connected in parallel is important. The RS485 system used for Modbus communication provides a main cable (Bus or backbone), to which all the devices have to be connected with branches (also known as stubs) that are as short as possible.
The branches must be no longer than 1200 m! Longer branches could cause signal reflections and generate disturbances and consequent errors in the reception of data.
Figure 1 shows an example of a correct Bus connection.
Network with Bus structure
Examples of incorrect Bus connections
Figure 2 – Examples of incorrect Bus connections
The main cable must be no longer than 700 m! This distance does not include the branches (which must nevertheless be short). The maximum number of devices that can be connected to a main cable is 32, including the Master.
4. Use of repeaters
In order to increase the extent of the Modbus network, repeaters can be used; and signal amplifying and regenerating devices provided with two communication ports that transfer to each what they receive from the other.
If the distance segment exceeds 1200 m or the number of drivers in the segment more than 32 pieces, you should use a repeater (repeater), to create the next segment. Moreover, each segment of the network must be connected to the terminator.
If the distance segment exceeds 1200 m or the number of drivers in the segment more than 32 pieces, you should use a repeater (repeater), to create the next segment. Moreover, each segment of the network must be connected to the terminator. (scheme credit: softelectro.ru)
Using a repeater, the main cable is divided into different segments, each of which can be up to 700 m in length and connect 32 devices (this number includes the repeaters). The maximum number of repeaters that should be serially connected is 3. A higher number introduces excessive delays in the communication system.
The cable to be used is a shielded twisted pair (telephone type). For example, Belden 3105A cable can be specified, but different types of cable with equivalent characteristics can be used. The twin consists of two conductors that are twisted together.
This arrangement improves immunity to electromagnetic disturbances because the cable forms a series of successive coils, each of which faces in the opposite direction to the next one: in this manner any magnetic field in the environment traverses each pair of coils in opposite directions and its effect is thus very reduced (theoretically, the effect on each coil is exactly the opposite of the effect on the next one and thus the effect is cancelled).
The shielding may be braided (be formed by a mesh of thin conducting wires) or be a foil (consisting of a sheet of metal wound around the conductors): the two types are equivalent.
Detail of a shielded twisted pair
Figure 3 – Detail of a shielded twisted pair
In some countries, inserting two cables into the same screw terminal is permitted. In this case it is possible to connect the main inlet and outlet terminal directly to the terminals of an instrument without creating a branch.
If on the other hand each terminal can accept only a single cable, a proper branch must be created using three auxiliary terminals for each instrument to be connected.
The cable shield must be earthed only in one point. Normally, this connection is made at one end of the main cable.
2-wire RS485 connection
In order to avoid signal reflections, a 120 Ohm termination resistance must be fitted on each end of the main cable. The end resistance must be used only at the ends of the main cable. If the total length of the main cable is less than 50 m termination resistances can be avoided at the ends of the main cable.
120 ohm resistance connection
Figure 4 – 120 ohm resistance connection
If the master used is a personal computer, in general an RS232/RS485 serial converter provides the connection to the bus.
Reference // Practical guide to electrical measurements in low voltage switchboards by ABB
6 Comments
  1. dinesh
    Jul 16, 2017
    Awesome stuffs!!!!
  2. Ronald Immanuel
    May 23, 2017
    Hi Edward,
    Why you so smart & you know everything!!??!! my I copy your artickle?? two thumbs for you
    R.immanuel
  3. Florin PANAZAN
    Feb 28, 2017
    Regarding maximum length of the cable, it depends of the communication speed. For 9600-19200 baud, the total cable length could go up to 1000m and even more (depending on the cable quality). For higher speeds cable length should be reduced. Also stubs cannot be longer than 1-2m. The value of 1200m from the article might refer to millimeter…
    Another good idea for noise immunity is to use bus polarization, e.g. to insert a bias resistor network on the bus.
  4. Joy Chang
    Dec 14, 2016
    Hi Edvard,
    I am a digital content manager at CFE Media, which publishing Control Engineering, Plant Engineering, and Consulting-Specifying Engineer.
    I would like to offer you a publishing opportunity at Control Engineering. Would you be interested in writing one, or a series of articles to be published on our website and possibly print publications?
    Here is the link explain the reach of Control Engineering: http://www.controleng.com/single-article/control-engineering-professional-profile/42f7d3fd47128265ab3a0204ee09d3dc.html
    I can send you more documents if you’d provide your email address. :)
    My email address is: jchang@cfemedia.com
    Hope to hear from you soon.
    Thanks,
    Joy
  5. vignesh waran
    Dec 10, 2016
    In some cases , Our communication system(RS 485) is working fine. but the slave port is failure.
    At the time can we check the system through Multi-meter?
    how much voltage will flow through the terminal A,B?
    In BMS, am facing many problems while communicating the VFD through controller. Kindly provide some troubleshooting ideas.
  6. ULHAS VAJRE
    Dec 09, 2016
    Dear Edvard,
    You are really doing great service to the electrical engineering fraternity. In order to disseminate the information, can we publish the articles in some other forums?? Pl. let me know, so that young engineers can be provided with basics as well as in depth knowledge on electrical engineering subjects.
    thanks,