Home / Technical Articles / What Is The Basic Insulation Level (BIL)
Estimated Study Time: 16 minutes
Introduction to BIL – Basic Insulation Level
Insulation levels are designed to withstand surge voltages, rather than only normal operating voltages. Since the transmission & distribution lines and substation equipment are protected by surge arresters draining the surges rapidly before the insulation is damaged, the arrester must operate below the minimum insulation level that must withstand the surges.
What Is The Basic Insulation Level (BIL) – photo credit by David Parrish via Flickr
An example is shown in Figure 1 below. The minimum level is known as the Basic Insulation Level (BIL) that must be that of all of the components of a system.
Insulation values above this level for the lines and equipment in the system must be so coordinated that specific protective devices operate satisfactorily below that minimum level.
In the design of lines and equipment considering the minimum level of insulation required, it is necessary to define surge voltage in terms of its peak value and return to lower values in terms of time or duration. Although the peak voltage may be considerably higher than normal voltage, the stress in the insulation may exist for only a very short period of time.
Figure 1 – Insulation coordination
For purposes of design, the voltage surge is defined as one that peaks in 1.5 microseconds and falls to one-half that value in 40 microseconds (thousandths of a second).
It is referred to as a 1.5/40 wave, the steep rising portion is called the wave front and the receding portion the wave tail, Figure 2.
Figure 2 – Surge Voltage 1.5 by 4.0 Wave
Insulation levels recommended for a number of voltage classes are listed in Table 1. As the operating voltages become higher, the effect of a surge voltage becomes less; hence, the ratio of the Basic Insulation Level (BIL) to the voltage class decreases as the latter increases.
Table 1[/highlight2] – Typical Basic Insulation Levels
Basic insulation level, kV
(standard 1.5- × 40-μs wave)
Voltage class, kVDistribution classPower class (station, transmission lines)
1.23045
2.54560
5.06075
8.77595
1595110
23110150
34.5150200
46200250
69250350
*For current industry recommended values, refer to the latest revision of the National Electric Safety Code.
Distribution class BIL is less than that for power class substation and transmission lines as well as consumers’ equipment, so that should a surge result in failure, it will be on the utility’s distribution system where interruptions to consumers are limited and the utility better equipped to handle such failures.
The insulating characteristics of the line and equipment must exceed the voltage level at which the protection arrester initiates sparking to ground, and there must be a sufficient voltage differential between the two.
The characteristics of the several type arresters are shown in the curves of Figure 3.
Figure 3 – (a) Sparkover Characteristics of Distribution Value Arresters; (b) Sparkover Characteristics of Expulsion Arresters
Sparkover Characteristics of Distribution Value / Expulsion Arresters
The impulse level of lines and equipment must be high enough for the arresters to provide protection but low enough to be economically practical. Surges, on occasion, may damage the insulation of the protective device; hence, insulation coordination should include that of the protective devices.
As there are a number of protective devices, mentioned earlier, each having characteristics of its own, the characteristics of all of these must be coordinated for proper operation and protection.
Before leaving the subject of insulation coordination, such coordination also applies within a piece of equipment itself. The insulation associated with the several parts of the equipment must not only withstand the normal operating voltage, but also the higher surge voltage that may find its way into the equipment.
So, while the insulation of the several parts is kept nearly equal, that of certain parts is deliberately made lower than others; usually this means the bushing. Since the bushing is usually protected by an air gap or arrester whose insulation under surge is lower than its own, flashover will occur across the bushing and the grounded tank.
The weakest insulation should be weaker by a sufficient margin than that of the principal equipment it is protecting. Such coordinated arrangement restricts damage not only to the main parts of the equipment, but less so to parts more easily accessible for repair or replacement.
The insulation of all parts of the equipment should exceed the basic insulation level (BIL).
Figure 4 – Simplistic diagram illustrating Basic insulation level (BIL) and Insulation coordination
Switching and Non-Switching Substation Equipment
Other equipment that may be present in a distribution substation comprises switch disconnectors, earthing switches, instrument transformers (CTs, VTs), measuring devices, protective relays, and occasionally, reactors, capacitors, street lighting equipment, and storage batteries.
Disconnect Switches and Earth Switches
Switches can be of various sorts, but their primary characteristic is that none are intended to interrupt fault currents; the insulation or insulators connected with them must coordinate with the overall system and have a Basic Insulation Level (BIL) sufficient for withstanding voltage spikes. Typically, they comprise a conductive blade, hinged at one end, and a fixed contact at the opposite end, with both terminals connected to appropriate insulators that meet the standard insulator specifications for BIL coordination.
Nearly every significant line or equipment in power substation is equipped with a mechanism for complete isolation from other powered components, serving as a sensible measure to ensure safety by averting accidental energization. These basic devices, referred to as disconnects or disconnecting switches, are often positioned on either side of the equipment or line where maintenance is required. .
They should not be operated while the circuit to which they are connected is energized but ONLY AFTER the circuit has been deenergized.
For added safety, they may be operated using an insulated stick that enables the operator to maintain distance from the switch. Locking devices are occasionally installed to prevent disconnects from being inadvertently opened or from being forcefully opened during instances of substantial fault currents.
Figure 5 – 400 KV Disconnector Close Operation
400 KV DBR type Disconnector Close Operation
While not intended for closure to activate the connected line or equipment, they may be closed under specific situations, provided that they close firmly and swiftly with due caution. Disconnects can be either single-blade devices or several units functioning in unison.
Air break switches has properties comparable to disconnects; however, their stationary contacts are fitted with arc suppression mechanisms, allowing them to be opened while powered, but with a limitation on the current that may be safely interrupted. The equipment may be a basic arcing horn that stretches the arc that may develop until it becomes unsustainable.
Another variant features a flexible “whip” connected to the fixed contact, which maintains contact with the moving blade until a threshold is reached, at which time the whip swiftly snaps open, effectively extinguishing any potential arc.[/info_box]
Yet another variant features an interrupting unit affixed to the free end of the switch blade, which mitigates the arc within the unit as the switch disengages; this interrupting unit may incorporate a vacuum chamber or a series of grids that fragment the arc into smaller arcs, facilitating their extinguishment. Both versions operate similarly to larger units found in circuit breakers.
Oil switches utilize a blade that remains open from its contact submerged in oil, effectively suppressing any potential arc formation. They provide a greater current breaking capability than air break switches and are especially appropriate for underground systems or environments where moisture or pollution render air switches unfeasible.
Nevertheless, they involve higher initial costs, operational expenses, and maintenance requirements.
Figure 6 – 110kV oil switch disconnectors
Instrument Transformers (CTs, PTs)
Instrument transformers are utilized in substations due to the impracticality of measuring current and voltage values with standard meters, as these values may exceed the instruments’ range and the insulating challenges render direct usage unfeasible.
Instrument transformers function similarly to distribution transformers, although have significantly enhanced accuracy in their transformation ratios. Current transformers (CT) and potential transformers (PT) are insulated for withstanding the voltage of their connected circuits and comply with the Basic Insulation Level (BIL) and insulation coordination of their respective systems.
Current transformers typically possess a secondary rating of 5 amperes, while potential transformers have secondary ratings of 150 or 300 volts, and occasionally 250 or 500 volts. Both instrument transformers isolate the meters and relay circuits from the high voltages of the incoming and outgoing feeds. They are rated in volt-amperes, and the load they support is termed their burden.
The turn ratios of the current transformer typically lead to an increase in voltage in its secondary winding. The voltage is significantly reduced by the impedance of the instrument or device connected to the secondary terminals; if the secondary is left open with no connection, the generated voltage may reach hazardous levels, necessitating a short circuit device for the current transformer when it is opened.
Current transformers are equipped with polarity indicators to facilitate their correct connection when paralleled with other current transformers.
The good and bad practices in the commissioning of current transformers in a substation
Protection Relays and Meters
The reader is presumed to possess knowledge of the functioning of meters that display and document data necessary for monitoring substation operations, encompassing both incoming and outgoing feeds.
Figure 7 – Metering control panels
Capacitor Bank
Where needed, capacitors may be installed at distribution substations to regulate bus voltage through power factor correction. Provisions exist for activating and deactivating certain units inside the capacitor bank as necessary to sustain voltage regulation.
Capacitors are connected to the bus via fuses that isolate a faulty capacitor unit, hence preventing impact on other energized equipment inside the substation.
Figure 8 – High voltage capacitor banks
HV capacitors and their practical applications in modern electric power systems
Figure 7 – High voltage capacitor banks
Reactors
Reactors can be arranged in series with the line or equipment to restrict the flow of fault current that may pass through them. They may also be connected in series with a transformer that can be paralleled with one of differing characteristics to achieve an equitable split of loads between them.
In distribution feeders, which are cables with metallic sheaths operating at elevated voltages, reactors may be implemented to mitigate the capacitance impact of the cables.
Lighting Systems
Street lighting systems providing series illumination may occasionally be located in distribution substations. Appendix E in this study contains the specifications of the equipment and the operational procedures.
Substation Batteries for Auxiliary supply
Storage batteries are typically located at certain distribution substations, particularly the larger and more significant ones. Circuit breakers, indication lamps, and other equipment are typically powered by alternating current from a dedicated transformer at the substation.
When the operation of these devices, particularly the reclosing of circuit breaker mechanisms, is critical, they are powered by a direct current source from a bank of storage batteries.
Operation may occur at nominal voltages of 6, 12, 24, 48, or 120 volts; however, 24, 48, and 120 volt systems are favored, as potential voltage drop from inadequate connections will still provide sufficient voltage for the appropriate functioning of relays, breakers, and auxiliaries.
The batteries are perpetually charged by being linked to a 120-volt alternating current supply via rectifiers. Lead-acid batteries require ventilation due to the release of hydrogen and oxygen gasses, which form a potentially explosive mixture. Batteries are rated in ampere-hours.
AC Auxiliary Systems In Power Substations (Design Requirements and Equipment)
Fuses
Fuses offer protection by melting a fusible connection when the current above their rated capacity. They are available in many types and ratings for both voltage and current specifications. All fuses, from the relatively low voltage line fuses linked to distribution transformers to those on high voltage transmission lines, function on the same principle and possess distinct time-clearing characteristics that must be evaluated alongside the attributes of other protective devices within the system.
The insulation of their mountings must also adhere to the Basic Insulation Level (BIL) and synchronize with the system insulation.
Distribution Substation and Feeder Protection Course
Reference: Power Transmission and Distribution – Anthony J. Pansini
17 Comments
  1. JUSTO VIDAL
    Jan 21, 2025
    THANKS VERY INTERESING
  2. Lebo
    May 05, 2021
    Greetings
    Please assist I have a 275kV line voltage and would like to know the BIL of it
    Thanks in advance for your response it means a lot
  3. taigon
    Aug 04, 2020
    Please suggest the clearance LT to HT winding and inter layer insulation of HT coil for resin casted potential transformer.
    PT BIL is 95 kV,
    we can’t achieve impulse test with 95 k, please help
  4. Seshadrik
    Mar 25, 2020
    It’s very good information for up coming young engg
    We need more and more latest upcoming
    Development update
  5. Antoine KAYIJUKA
    Jun 12, 2019
    What is the length of 110kV insulators considering BIL 650KV and Nominal creepage distance 3679mm? and how to calculate.
  6. Zosimo Bacalla
    Jul 24, 2018
    What is the correction factor in terms of insulation for a potential transformer rated at 15.5kV Insulation with 110kV BIL full wave. Being installed at the height of 3000meters.
  7. Al-Amin
    Mar 31, 2018
    nice Article.
    Bil rating will vary from operating voltage level to level ?
  8. Florian Misoc
    Jan 19, 2018
    Great article!
  9. Brian Trager
    Jan 16, 2017
    Good job Edvard. Your contribution to the industry is appreciated.
  10. MOHAMMAD MONIRUZZAMAN
    Sep 05, 2016
    What is “BIL” Test ?
    How to do “BIL” Test ?
    • Iryani
      Nov 03, 2016
      BIL refer to lightning impulse test. can refer to IEC 60060-1
      • Nilesh
        Jun 30, 2018
        Waht Is BIL of below Rated Surge Arrester.
        1)4.5kV
        2)7.2kV
        3)12kV
        4)18kV
        5)24kV
        6)33kV
        How its calculate Please explain.
  11. Vu
    Mar 11, 2016
    Is insulation Levels presented in table 1 Phase-Neutral Voltage?
  12. vinod nagrecha
    Dec 11, 2015
    How would Basic Insulation Level vary as altitude where equipment is to be installed rises ?
  13. Electrical Engineer
    May 26, 2015
    good topic
  14. Jan Ledochowski
    Mar 27, 2014
    There is a mistake below title Hot Swap Controllers PDF:
    ….one-half that value in 40 microseconds (thousandths of a second).
    should be: millionth of a second.
  15. UDAYKUMAR
    Feb 09, 2014
    Dear Sir/Madam,
    can you tell me abt earth falut details…