Estimated Study Time: 6 minutes
Introduction
In HT electrical distribution, the system can be earthed or unearthed. The selection of unearthed or earthed cable depends on distribution system. If such system is earthed, then we have to use cable which is manufactured for earthed system. (which the specifies the manufacturer). If the system is unearthed then we need to use cable which is manufactured for unearthed system.
The unearthed system requires high insulation level compared to earthed system.
For earthed and unearthed XLPE cables, the IS 7098 part2 1985 does not give any difference in specification. The insulation level for cable for unearthed system has to be more.
Earthed System
Earlier the generators and transformers were of small capacities and hence the fault current was less. The star point was solidly grounded. This is called earthed system.
Where in unearthed system, (if system neutral is not grounded) phase to ground voltage can be equal to phase to phase voltage. In such case the insulation level of conductor to armor should be equal to insulation level of conductor to conductor.
In an earthed cable, the three phase of cable are earthed to a ground. Each of the phases of system is grounded to earth.
Example: 1.9/3.3 KV, 3.8/6.6 KV system
Unearthed System
Today generators of 500MVA capacities are used and therefore the fault level has increased. In case of an earth fault, heavy current flows into the fault and this lead to damage of generators and transformers. To reduce the fault current, the star point is connected to earth through a resistance. If an earth fault occurs on one phase, the voltage of the faulty phase with respect to earth appears across the resistance.
Therefore, the voltage of the other two healthy phases with respect to earth rises by 1.7 times.
In an unearth system, the phases are not grounded to earth .As a result of which there are chances of getting shock by personnel who are operating it.
Example: 6.6/6.6 KV, 3.3/3.3 KV system.
Unearthed cable has more insulation strength as compared to earthed cable. When fault occur phase to ground voltage is √3 time the normal phase to ground voltage. So if we used earthed cable in unearthed System, It may be chances of insulation puncture.
So unearthed cable are used. Such type of cable is used in 6.6 KV systems where resistance type earthing is used.
Nomenclature
In simple logic the 11 KV earthed cable is suitable for use in 6.6 KV unearthed system. The process of manufacture of cable is same.
The size of cable will depend on current rating and voltage level.
- Voltage Grade (Uo/U) where Uo is Phase to Earth Voltage & U is Phase to Phase Voltage.
- Earthed system has insulation grade of KV / 1.75 x KV.
- For Earthed System (Uo/U): 1.9/3.3 kV, 3.8/6.6 kV, 6.35/11 kV, 12.7/22 kV and 19/33 kV.
- Unearthed system has insulation grade of KV / KV.
- For Unearthed System (Uo/U): 3.3/3.3 kV and 11/11 kV.
- 3 phase 3 wire system has normally Unearthed grade cables and 3 phase 4 wire systems can be used earthed grade cables, insulation used is less, and cost is less.
Thumb Rule
As a thumb rule we can say that 6.6KV unearthed cable is equal to 11k earthed cable i.e 6.6/6.6kv Unearthed cable can be used for 6.6/11kv earthed system.
Because each core of cable have the insulation level to withstand 6.6kv so between core to core insulation level will be 6.6kV+6.6kV = 11kV
For transmission of HT, earthed cable will be more economical due to low cost where as unearthed cables are not economical but insulation will be good.
In such cases, unearthed cables may be used so that the core insulation will have enough strength but current rating is de-rated to the value of earthed cables.
But it is always better to mention the type of system earthing in the cable specification when ordering the cables so that the cable manufacturer will take care of insulation strength and de rating.
if the system is earthed system,use of earth cable is desirable & vice-versa.
Can anybody tell is it righ as I heard the bounding metal (Cu.) tape for unearthed HV cable is thicker than its earthed counterpart
In furnace transformer, (DYn11), the secondary star point is not earthed.
Which one suitable cable for primary side. (ie) earthed or unearthed cable?
That will depend on the primary side voltage (whether it is grounded system or ungrounded system)
Use unearthed cable for 11KV system.
Hi I use 11kv AB cable Route Length 8km.
But many problems cables failed falut creat of up side note conductor side
Why
You may have used 11 kV (E) cable for an 11 kV (UE) system. The insulation level for 11 kV (E) cable is lower. You are advised to check the upstream system if it is an UE system which means that the upstream transformer neutral is grounded through a resistance. You should use a 11 kV (UE) cable.
Please explain the ground to nutral voltage is restricted in less than two voltage ..In ESD safe work table.. please explain all things.
sir, let me know which type of cable we can use for 11 kv supply from discom (PGVCL sub station). 11 KV earth cable or 11 KV unearth cable. please inform me.
Use of earth cable
You should use 11 kV (UE) cable. All the Discom receiving stations have their transformers grounded through a resistance. They are not solidly grounded like LV systems. Therefore you must use a 11 kV (UE) cable.
Dear Sir,
I need to know that 11KV Cable can be used for 6.6KV System for Operation.
I also want to know the advantages & disadvantages of usages of 11KV cable for 6.6KV Voltage operation.
HOW we can identify the given cable is earthed or unearthed without checking nomenclature mentioned on the cable top.
Hi team,
If NGR using 11kV DG’s normal we use UE cables. Suppose we are not used UE cable from DG 11kV panel to its feeding transformer (2.5mva ,11kV/433V ) . One major L-G fault happened during the 11kV DG time what would the effect of fault in DG etc
The 11 kv Cables can sustain for a higher phase to ground voltage. which is evaluated during the load cycle of the cable accessories and the test voltage is 2.5 Uo and time is 60 cycles of 8 hours. Here the point of discussion is unearth cable will have a ph to earth voltage 1.73 Uo during a fault situation. So I think the 11 KV cable will sustain for this application.
Hello team.,
Can we use 1.1kV/650V cable for 800Vac unearthed system rated at Inverter O/P terminal.
Thanks & Regards
Srikanth
dear peter,
can we use 11kv/11kv UE cable to 11kv/22kv Earthed system? are they same?
Yes u can use 11kv ( UE ) / 22 KV ( E ).
Hi Guys,
Can any one explain can we use 11KV cable instead of 3.3KV cable, if not what is the reasons?
NB
Nice and updated information .
A good platform of Electrical engineering.
In 33 kv unearthed system 3CX240SQ.MM Unearthed cable we can use the Earthed straight through kits and earthed end kits .if we use what will be the result.
Can any one tell me the logic/ reasons, why do we make use of the cable 1.1kV grade /insulation for low voltage system ( house wiring wires 220 440 V AC) or reasons for using 1.1 kV insulation cable in 11kV transmission lines and as well as in internal wiring system?
What if the system is effectively earthed grounded through NGR to Limit the earth fault current upto 50A (33/3.3KV, Delta star) Should I use 1.9/3.3KV or 3.3/3.3KV Grade Power cable
3.3/3.3KV Grade Power cable(means UE cable) shall be used (at secondary i.e. 3.3 kv side i.e star side) as the system is with NGR (means neutral is grounded with resistor).
What about 33KV/ 3.3 KV system earthed with NGR to limit the fault current upto 50A (max). Should I use 1.9KV/3.3KV or 3.3KV/3.3 KV
why so much stress on your face??? relax and smile!!
why?
Thank’s for those type of information !!!
We use 11 KV cable to connect our Distribution transformer which has its primary or HV winding in Delta connection and Secondary or LV winding in Star connection. Since Delta connection has no earth, we always need 11 KV Unearthed (UE) cable.
So we should always ask for 11 KV UE cable.
Dear Friend
Please, your comment is not true. You have mixed upstream and downstream networks.
If you are talking about earthing of 11 KV network, which have supplied your transformer, you should follow secondary winding of upstream transformer( HV to 11KV), which usually it is resistance grounded and increases required insulation level by 1.73 times.
Bye and have a nice time.
hooshang karimi Ahvaz – Iran
This article about earthed and unearthed cables is very basic and with poor technical content.
I am not agree with “As a thumb rule we can say that 6.6KV unearthed cable is equal to 11k earthed cable i.e 6.6/6.6kv Unearthed cable can be used for 6.6/11kv earthed system.”
Reason: For 6.6/11kV Earthed cable, the system nominal voltage is 11kV. If we use 6.6/6.6kV Unearthed cable for 6.6/11kV Earthed system with 11kV nominal voltage, the phase to earth voltage remain 6.6kV for Earthed system(Agreed), but phase to phase voltage remain 11kV for Earthed system and this 6.6/6.6kV Unearthed cable can not meet the 11kV nominal system phase to phase voltage insulation.
How to calculate feeder htvr through metlab or etap
It is good and interesting web. Informative topics are covered
Mr. Peter
you must check set time for overload in your breaker
may be the setting is wrong.
thanks.
How’s 6.6kV+6.6kV = 11kV? As far as I know 6.6+6.6=13.2
It means it is suitable for 11KV insulation requirement (since 13.2KV>11KV). Standard cable insulation ratings are as 1.1KV, 3.3KV, 11KV, 33KV…)
I can not agree this statement ie., 6.6/6.6kv Unearthed cable can be used for 6.6/11kv earthed system.
but we can use 6.6/11kv cable for 6.6/6.6kv system.
I have a question and it goes thus:
A motor Filter Fan’s RPM on motor data plate is 3545 RPM, Relay overload set is 2.9A. During solo run, motor runs at 1.6A (starting current) at 3615 RPM. The LV motor tripped at 4.9A with enclosure door closed during load run. What are the possible causes of the motor trip? What can be done to avoid such trippings? (What are your recommendations?)
(the motor specification are: Voltage = 460 V, Power = 1.5kW (2HP), No. of Phase = 3,Frequency = 60Hz,No. of poles = 2)
Your prompt response will highly be apprexciated.
Kind Regards,
Peter.
Hi Peter, the starting current of 3 ph induction motor has nothing to do with the load. (Load affect the run up time and thermal withstand)
The starting current for induction motors can as high as 7-8x the rated full load current. By your description of 1.5kW 460 3ph motors, I would think 4.9A sounds like a reasonable starting current. (not taking PF/eff into account, the rated full load current is at least 1.89A)
Dear Mr Peter,
if the motor trip at load run, means we have to check the load first. is it suitable for your motor or not, you can ask the mechanical engineer for that. well, for the motor itself, you can do normal check such as its impedance, megger, bearing etc.
I too experienced similar problem, in my case motor – fan belt coupled, we loosen the belt and it worked for us