Distribution of electrical energy
The lighting and electrical design of elementary school is divided into following parts: electrical design, lighting design, fire alarm design, and telecom design. The school’s electrical system will consist of three-phase 480/277V power and three-phase 208/120V power. The incoming utility feed is assumed to be three-phase 4,160 Volt.
Lighting and electrical systems design guide - An example of elementary school building
Lighting and electrical systems design guide – An example of elementary school building
This incoming feed enters the building from the Park Avenue street side of the building running parallel with the natural gas, water, and telecommunications utilities.
The service terminates in the building’s main electrical room which is centrally located in the basement level. At the unit substation which consists of a main service breaker-disconnect, a 750 kVA delta-wye transformer, secondary breaker, and secondary switchgear distribution section, the main service is stepped down from a three-phase 4,160V delta to a 480/277V wye configuration.
From here the system splits into the building’s three main power branches – life safety, emergency, and normal. The life safety branch will carry all loads deemed necessary for the protection of human life. The emergency branch will carry all loads that are necessary for safe and reliable operation of the school as an emergency natural disaster shelter.
Supplying standby power for the life safety and emergency branches will come from four Capstone 65kW natural gas microturbines, which will be discussed later in this document (Please see the attached electrical riser diagram for a more detailed organization of the electrical system).
Riser diagrams
Riser diagrams
The preliminary sizing for all equipment was based on a tabulation that can be found on page 25 of the supporting documents and also details of this equipment can be seen on pages 29-30.
Equipment Layout
As mentioned before, the unit substation will be located in the building’s main electrical room in the basement level.
Also, this room will house the main distribution panels for each of the three power branches – life safety, emergency, and normal. The automatic transfer switches for the life safety and emergency branches will be located here as well.
Main Electrical Room Layout
Finally, each branch will be provided with a 480/277V lighting panel, transformer, and 208/120V double-tub receptacle panel in the main electrical room.
Title:Lighting And Electrical Systems Guide – ASCE Charles Pankow Foundation Architectural Engineering Student Competition
Pages:45
Lighting And Electrical Systems Design Guide - An Example of Elementary School Building
Lighting And Electrical Systems Design Guide – An Example of Elementary School Building
28 Comments
  1. Raymond Elias
    Apr 13, 2023
    I’m interested
  2. Victor Plunkana Phiri
    Jan 28, 2021
    Please call
  3. Ijimakinwa Stephen
    Sep 24, 2020
    Maybe we can work together.
    I want to learn more about electrical
    • A Hareendralal
      Nov 26, 2020
      What is the maximum capacity of motors that can be operated at various voltage levels: eg. Single phase (230V), Three phase (440V), 3.3 kV, 6.6 kV, 11kV.
  4. Zeeshan Bacha
    Jan 29, 2020
    Hi, I need Cable size and ckt breaker rating in pdf file plz
    [email protected]
    It’s my mail
  5. Engr Zakerya
    Jan 29, 2020
    Dear Sir can you please share the cable sizing and circuit breaker rating Design in Excel sheet for low voltage, medium and high voltage system. my Email address: [email protected]
  6. Hemendra Jani
    Jan 28, 2020
    GR8
  7. Eduardo García
    Jan 28, 2020
    ENERGY-W is the design and proven efficiency of power generation obtained from ocean and river currents (Tamesis)No power limits, 10 times cheaper than traditional ones.Contact + 5491144232218
  8. Houssein
    Jan 25, 2020
    Could you please share the Short Circuit Calculation excel sheet, cable sizing excel sheet and load calculation sheet to my email address.
    [email protected]
  9. Fawad
    Jan 09, 2020
    sir i need cable sizing and circuit breaker rating design excel sheet for low voltage and medium voltage system. so please send me in my email address as below.
    ([email protected])
  10. Usman
    May 27, 2019
    Dear Edward
    Could you please share the Short Circuit Calculation excel sheet, cable sizing excel sheet and load calculation sheet to my email address. I will be thankful to you.
    [email protected]
    • Moses Lusaaka
      Jun 04, 2019
      Can I also get the excel sheet of the mentioned information on e-mail at [email protected]
  11. Mike Scirocco
    Feb 04, 2019
    Very nicely done, thank you for making this available. May I ask why no solar cells were included in the proposal?
  12. Bilal
    Dec 28, 2016
    Dear Edvard can you please send me the cable sizing calculation at [email protected]
  13. Mohamad
    Jun 23, 2016
    link to download the guide for the school is not working. please advise
  14. URG
    Mar 12, 2016
    Hi … is it possible if we can get separate section for design, maintenance, operations, installation etc in technical articles or sitemap to easily navigate in relevant field. Moreover, is there any chat room or blog etc available to discuss any query ?
  15. Abderramane GHARIANI
    Jul 10, 2015
    thanks for all your contribution, more we share more we grow our skill leveln, I appreciate your just feeling about the problems encountered by engineers, go ahead
  16. Amine
    Jul 09, 2015
    I don’t know when I click the blue button I don’t see the page of donwload I see another page.
      Take a look at the bottom, there is a link for download – ‘Right Here’.
  17. Amine
    Jul 09, 2015
    I can not download this guide can someone sent to me at [email protected]
    thank you
      Why can’t download?
      • Ramsheed
        Feb 10, 2016
        Could you please sent to [email protected]
        • Sani Suleiman Sani Kura
          Jun 11, 2020
          I want learn how to design an electrical system. I need your assistance please.
  18. Danish Hayat Latifi
    Mar 30, 2015
    Dear Edward
    Could you plz share the cable sizing excel sheet nd load calculation sheet as i want to know — if i am taking 3 runs of cable from one end to other end , then , why do fault level calculation for 1 run – fault current should also be done considering 3 runs …. In load calculation do we have to consider diversity factor for different panels nd then diversity factor for main panel .
    This is how i do …
    Your clarification plzz
  19. Aamir Baig
    Jan 03, 2015
    I am facing difficulty to download this file, can anyone plz send me at [email protected]
      Guide sent! Enjoy!
      • Michael
        Oct 31, 2017
        Edvard,
        Thanks for your contribution. I can’t open this guide , Can you please send the elementary school design guide as a PDF. I also try open your articles in past and wasn’t able to, please advise if there is another way to access it.
        Thanks,
        Michael T
        • Srikanth
          Nov 02, 2019
          Dear Edvard,
          Thanks for more your concepts,
          Please share the cable design Excel sheet
  +  fourteen  =  eighteen