Distribution systems
In large buildings the type of distribution depends on the building type, dimension, the length of supply cables, and the loads.
Power distribution inside large buildings
The distribution system can be divided in to:
  1. The vertical supply system (rising mains)
  2. The horizontal supply (distribution at each floor level)
In most cases a high voltage supply and transformer substation is required. Normally HV switchgear and substation transformers are installed at ground floor (or basement ). However, often there are appliances with large power demand installed on the top floors (converters and motors for lifts, air-conditioning equipment and electric kitchens).
As it is desirable to bringing the high voltage supply as close as possible to the load centers, transformers are installed at the top floor, or if required, additional ones are installed on one of the intermediate floors. In such cases transformers with non-inflammable insulation and cooling are used.
The arrangement of the rising mains depends on the size and shape of the building and suitable size of shafts for installing cables and bus ducts must be provided in coordination with the building architect.
The vertical supply system are implemented in several ways, some of which are: single rising main, grouped supply, individual floor supply, ring main supply, double feed supply and others.
Single Rising Main
Single Rising Main
Single Rising Main
Applications: Where high supply security is not important.
Advantages:
  1. The different loads of individual floors are balanced out
  2. Only a small main L.V board is required
  3. Simple in construction and operation
Disadvantages: Low supply security (a fault in the rising mains effect all floors).
Title:Power distribution inside large buildings – Department of Electrical Engineering – Dr. Hussain Al-Mashat
Pages:56
  1. REZA TOUSIPANAH
    Feb 17, 2019
    Dear Sir
    there are various opinions between silicone rubber manufacturers about the suitable formulation and composition of contents and their percentage by weight in a compound for high voltage outdoor composite insulators and clients as well,they ask for different amount of silicone and silicone oil in their insulator compound, but none of the compound manufacturers accept to change their own formulation, would you please let us know the opinion of your experts in this regard and a right formulation for that.
    Your kind attention and prompt reply will be appreciated.
    Best regards: Reza Tousipanah
  2. integratedengineering
    Feb 17, 2019
    i wanted to go for premium member ship …kindly help me with link ,,,i could not d it with paypal