Home / Download Center / Electrical Engineering Books and Technical Guides / Power substation guides / Power Plant Horror Stories – The Loss Of a Generator
Complete failure of the generator
Generators are the most expensive piece of equipment in a power system. The cost of a major generator failure to a utility or IPP (Independent Power Producer) owner is not only the cost of repair or replacement of the damaged machine, but also the substantial cost of purchasing replacement power when the unit is out of service.
Power Plant Horror Stories - The Loss Of a Generator
Power Plant Horror Stories – The Loss Of a Generator (on photo: Surveying the damage within Bold Power Station after a turbine explosion; credit: suttonbeauty.org.uk)
An alert and skillful power plant operator, at manned locations, can sometimes avoid removing a generator from service by correcting an abnormal condition.
In the vast majority of cases, however, the event will occur too rapidly for the operator to react and automatic detection and isolation is required. Operators have also been known to make errors and create abnormal conditions where tripping to avoid damage is required.
Inadvertent energization and overexcitation are examples of such events.
Several power plant events within the last two to three years substantiate the premise that generators can, and do, sustain internal short circuits and abnormal operating conditions that require tripping. The following in-service events are described:
  • Multi-phase generator faults
  • Stator ground faults
  • Accidental off-line generator energizings
  • Overexcitation
  • Loss-of-field
  • Generator breaker failure (breaker flashover)
Title:Power Plant Horror Stories – Charles J. Mozina Beckwith at Electric Co., Inc.
Pages:18
  1. Franklin Ferreira de Lima
    Apr 07, 2021
    fora Da pesquisa de um pouco da distância
  ×  eight  =  40
