Home / Download Center / Electrical Engineering Books and Technical Guides / Power substation guides / Guidelines to properly designed substation grounding system
Soil Resistivity Measurements
Before the design of the grounding system begins, soil resistivity measurements need to be taken at the substation. Stations with uniform resistivity throughout the entire area are rarely found. Thus, measurements should be made at multiple locations within the site.
Guidelines to properly designed substation grounding system (photo credit: canacopegdl.com)
Usually there are several layers, and each has a different resistivity.
If there are large variations, more readings should be taken at these locations. Lateral changes may occur as well, but in general the changes are gradual and negligible.
There are a number of measuring techniques. With two-point methods, rough measurements of the resistivity of undisturbed earth can be made. Three-point method or variation of depth method measured ground-resistance test several times.
Each time the burial depth of the test electrode is increased by a certain amount. But this method is not recommended if large volume of soil needs to be investigated.
Four-pin methods are the most accurate method of measuring the average resistivity of large values.
Wenner’s Four-Pin Method
The Wenner’s four-pin method is the most common. This method is also called the Equally-Spaced Four-Pin method.
In this technique, four probes are driven into the ground in a straight line to a depth b, at equal distances a apart. The voltage between the two inner probes is measured and is divided by the current of the two outer probes.
This gives a value of the mutual resistance R. The Wenner’s four-pin method is shown in Figure 1 below.
Figure 1: Wenner’s Four-Pin Method
The resistivity measurement records should include temperature data and information on the soil moisture conditions at the time that the measurements were done.
Also record all data available on any buried conductors already known or suspected. Buried conductors in contact with the soil can invalidate readings if they are close enough by altering the test current flow pattern.
The Wenner four-pin method is popular for a number of reasons. This method obtains soil resistivity data for deeper layers without having to drive the test pins to those layers. Also, no heavy equipment is needed.
The results are not greatly affected by the resistance of the test pins or the holes created by driving the test pins into the soil. A shortcoming of the Wenner method is that the magnitude of the potential between the two inner electrodes rapidly decreases when their spacing is increased to large values.
And often times commercial instruments cannot measure such low potential values.
Title:Guidelines to properly designed substation grounding system – Inna Baleva (A Project Presented to the faculty of the Department of Electrical and Electronic Engineering California State University, Sacramento)
Pages:74
  1. zvyazok.com
    Jan 27, 2021
    Wow, this article is pleasant, my younger sister is analyzing these kinds of things, therefore I am going to inform her.
  2. Vinod Maurya
    Jul 05, 2020
    When testing of transformers With impulse voltage generator according with IEC60076-3 Rule ,How to calculate the switching Impulse time from obtained graph in oscilloscope ,like T1,Td,T2(100us,200us,500us)
  3. Alaa elghanam
    Mar 29, 2020
    I am senior electrical engineers