Distribution Automation Handbook – Power System Protection Practice // Protection of Synchronous Generators – by ABB
Synchronous generators
Most power systems tolerate the disconnection of one generating unit, one power transformer, one power line or one busbar section without running into serious problems. A fault on adjacent power system component may cause the generator protection system to operate non-selectively.
A generator has more failure modes than any other component in the power system. It is very important that the protection system detect all faults that may hurt humans and damage equipment. The generator protection system must detect the faults rapidly.
General Demands
The general demands on the protection system are based on some risk analysis, experience and tradition. Commonly, it is required that earth faults, short circuits and other severe faults must be detected by two independent protections. The fault must be cleared even if one switching device fails to operate.
The generator protection system must also provide adequate backup protection for adjacent components.
Synchronous Machines
A synchronous machine is not a simple device.
The armature, or stator, winding is arranged in three symmetrical phase belts in slots in the stator surface. The magnetic field intensity can be controlled via the DC current in the rotor, or field, winding. A synchronous machine can operate as a generator or as a motor.
Power Station Configuration
Varying power station configurations obstruct the use of a uniform and standardized generator protection system. The most important factor is the varying power station configuration.
Besides the varying power station configuration, following factors influence the design of the generator protection system:
  • Generator circuit-breaker or not
  • Earthing of the generator neutral
  • Location of the voltage transformers
  • Location of the current transformers
Title:Distribution Automation Handbook – Power System Protection Practice // Protection of Synchronous Generators – ABB
Pages:36
  1. Ramakrishna
    Nov 22, 2015
    I loke this portal. I am professional Electrical Engineer.
  2. st01
    Feb 08, 2015
    great guides big thanks
  −  5  =  four
