Structure of LV electrical power distribution
The requirements of electrical power distribution
The design of LV installations leads to basic protection devices being fitted for three types of faults:
  • Overloads
  • Short-circuits
  • Insulation faults
Safety and availability of energy
Implementation of these protection devices must allow for:
  • The statutory aspects, particularly relating to safety of people
  • Technical and economic requirements.
The chosen switchgear must:
  • Withstand and eliminate faults at optimised cost with respect to the necessary performance
  • Limit the effect of a fault to the smallest part possible of the installation in order to ensure continuity of supply.
Achievement of these objectives requires coordination of protection device performance, necessary for:
  • Managing safety and increasing durability of the installation by limiting stresses
  • Managing availability by eliminating the fault by means of the circuit-breaker immediately upstream.
The circuit-breaker coordination means are:
  1. Cascading
  2. Discrimination.
If the insulation fault is specifically dealt with by earth leakage protection devices, discrimination of the residual current devices (RCDs) must also be guaranteed.
AUTHOR: Schneider Electric experts
Title:Schneider Electric Low voltage expert guides no. 5 – Coordination of LV protection devices
Format:PDF
Pages:44
Coordination of LV Protection Devices