Current transformers for HV protection
Abstract
Current transformers or CTs take up a lot of space in HV cubicles. Thorough knowledge of how they work makes it
possible to:
  • reduce their dimensions and thus their cost,
  • use standard CTs in a larger number of configurations.
The purpose of this study is to learn more about CT operation in association with protection relays and to lay down a few rules for sizing them properly. After a brief theoretical review of CT operation and current protection devices, the behaviour of the CTprotection relay combination is studied in two particularly important cases
in HV:
  • overcurrent relay supplied by a heavily saturated CT,
  • protection relay connected to two CTs in parallel in duplex cubicles.
This study is completed by experimental results.
Theoretical Review
Current transformers consist of a magnetic circuit in toroid form. The primary is made up of n1 turns or simply a single conductor crossing the toroid (n1 = 1). The secondary is wound in n2 regular turns around this toroid (see fig. 1 and 2).
Ampere’s theorem states that the sum of the ampere-turns is equal to the circulation of the magnetic field vector.
AUTHOR: Schneider Electric expert | Michel ORLHAC
Title:Current transformers for HV protection
Pages:20
Download:Please login first
Don't miss anything!
Powered by MailChimp
  1. Mustafa assal
    Dec 19, 2011
Leave a reply!
Engineering Trainings
Top EEP’s Technical Writers
Technical Categories
Diagnosing Transformer Winding Insulation (video)
This video tutorial shows the progression of power factor or dissipation factor over frequency. Furthermore, measuring transformer winding insulation, including...
How solar collectors works?
Solar energy (solar radiation) is collected by the solar collector’s absorber plates. Selective coatings are often applied to the absorber...
Using AC and DC together in electrical system?
There are a number of issues to using AC and DC together in the same electrical system. Briefly, they are: circuit...
Close