Need for Circuit Protection / Current and Temperature
Current flow in a conductor always generates heat. The greater the current flow, the hotter the conductor. Excess heat is damaging to electrical components and conductor insulation. For that reason, conductors have a rated continuous current carrying capacity or ampacity.
Overcurrent protection devices, such as circuit breakers, are used to protect conductors from excessive current flow. These protective devices are designed to keep the flow of current in a circuit at a safe level to prevent the circuit conductors from overheating.
Excessive current is referred to as overcurrent. The National Electrical Code® (NEC®) defines overcurrent as any current in excess of the rated current of equipm ent or the ampacity of a conductor. It may result from overload, short circuit, or ground fault (Article 1 00-Definitions).
Overloads
An overload occurs when too many devices are operated on a single circuit, or a piece of electrical equipment is made to work harder than it is designed for. For example, a motor rated for 1 0 amps may draw 20, 30, or more amps in an overload condition. In the following illustration, a package has become jammed on a conveyor, causing the motor to work harder and draw more current.
Because the motor is drawing more current, it heats up. Damage will occur to the motor in a short time if the problem is not corrected or the circuit is shut down by the overcurrent protector.
Conductor Insulation
Motors, of course, are not the only devices that require circuit protection for an overload condition. Every circuit requires some form of protection against overcurrent. Heat is one of the major causes of insulation failure of any electrical component. High levels of heat can cause the insulation to breakdown and flake off, exposing conductors.
Short Circuits
When two bare conductors touch, either phase to phase or phase to ground, a short circuit occurs. When a short circuit occurs, resistance drops to almost zero. Short circuit current can be thousands of times higher than normal operating current.
Ohm’s Law demonstrates the relationship of current, voltage, and resistance. For example, a 240 volt motor with 24 Ω of resistance would normally draw 1 0 amps of current.
Types of Overcurrent Protective Devices
Circuit protection would be unnecessary if overloads and short circuits could be eliminated. Unfortunately, overloads and short circuits do occur. To protect a circuit against these currents, a protective device must determine when a fault condition develops and automatically disconnect the electrical equipment from the voltage source. An overcurrent protection device must be able to recognize the difference between overcurrents and short circuits and respond in the proper way. Slight overcurrents can be allowed to continue for some period of time, but as the current magnitude increases, the protection device must open faster.
Short circuits must be interrupted instantaneously. Several devices are available to accomplish this.
Fuse
A fuse is a one-shot device. The heat produced by overcurrent causes the current carrying element to melt open, disconnecting the load from the source voltage.
| Title: | Basics of Circuit Breakers |
| Format: | |
| Size: | 5.1MB |
| Pages: | 88 |
Don't miss anything!
How circuit breaker trip unit works? | EEP
[...] the greater the fault current, the shorter the time it takes to interrupt the current.SOURCE: SIEMENS: Basics of Circuit Breakers Tags: circuit breaker, manual, mechanism, overload, short-circuit, trip unit, tripping Category: [...]
How Low-Voltage Air Circuit Breaker Works? | EEP
[...] A low-voltage circuit breaker is one which is suited for circuits rated at 600 volts or lower. One of the most commonly used [...]
Maintenance Of Low Voltage Circuit Breakers | EEP
[...] The deterioration of low voltage circuit breaker is normal and this process begins as soon as the circuit breaker is installed. If deterioration [...]
System protection and safety coordination definitions | EEP
[...] of the short circuit that the protective device is able to clear according to specifications. The protective device may be used in power systems for rated switching capacities up to this value.Back-up protectionIf a [...]