Home / Download Center / Electrical Software and MS Excel Spreadsheets (Calculations of cables, voltage drop etc.) / Earthing mat design for a power substation (MS Excel Spreadsheet)
What does this spreadsheet do?
Program is designed as per ANSI/IEEE 80 Code, it calculates step potential of switchyard, touch potential of switchyard, total length of earthing mat conductor, size of earthing mat conductor and total number of earthing rods.
Input fields As per ANSI/IEEE Std 80-1986 code
  • Length of Area Occupied by Earthing Grid
  • Width of Area Occupied by Earthing Grid
  • Fault level at Incoming Bus
  • Incoming Voltage
  • Outgoing Voltage
  • Soil Resistivity
  • Resistance of Main Earthing Mat
  • Resistance of surface Material (Crushed Rock )
  • Thickness of Surface Material (Crushed Rock)
  • Depth of Earthing Grid Conductor
  • Diameter of Earthing Grid Conductor
  • Reference Depth of Grid
  • Spacing between Parallel Conductor of Grid
Software:Earthing Mat Design For Substation
Version:22.12.2012 New
Developer:Jignesh Parmar
Price:Free
30 Comments
  1. Omar Gatous
    Jul 09, 2023
    I am thinking and looking for something to learn about how to design primary and secondary earthing systems for any project.
    I am electrical engineer
  2. Nasir Mehmood
    Dec 27, 2022
    We are making 6700KVA hydel power station. Along 11KV/66KV Switch Yard. Is it necessary for both? Or just for switchyard area.
    • Daniel Kubelwa
      May 09, 2023
      how is the TFX is being link by used a direct or resistor or inductance?
  3. isaac serwadda
    Jun 14, 2022
    Great knowledge sharing
  4. Mohammed Haris Qurashi
    Apr 07, 2022
    Can anyone tell me soil treatment procedure for Single Grounding with reference to Standard…
  5. Anil
    Oct 11, 2021
    Please tell me what is the basis of selection of Ambient Temperature-35 Degree.
  6. Haytham Alloush
    Sep 18, 2021
    Are the step & touch voltages calculated for HV substations ? or they should be calculated for LV projects as street lighting poles or LV water pumps projects too ?
  7. Corpuz
    Sep 09, 2021
    It is better if you would show us how these are derived
  8. BENEDICT UKPEBOR
    Sep 09, 2021
    This portal is very informative. What are the requirement for premium membership?
  9. Koustav Saha
    Dec 26, 2018
    What is the tolarable value of GPR/EPR for earthing grid calculation?
  10. Amardeep Sah
    Sep 14, 2018
    Sir,
    Can u send me the details required to design an earth mat for 33/11 KV PSS
  11. hesham
    Jun 26, 2018
    thanks alot
  12. Khaled Ellithy
    Jan 25, 2018
    Excellent;
    Ellithy
    Professor in Power systems
  13. Mamata Patil
    Sep 25, 2016
    I want to give a seminar on grid Earthing..Can u give me detail info about it?
  14. NIDHI
    Jan 08, 2016
    Sir,
    In the design procedure for earthing it is said that as we doubles the length of the rod the resistance will be reduced by 40% and when we increase the size of the electrode the resistance decreases by 10%. i am getting this . with reference to what equation the above mentioned conclusions is reached
  15. Murugesan.C
    Jul 08, 2015
    I am not able to see the detailed drawing about construction of earth mat. A drawing shall be presented indicating driving/penetrating number of MS rod in ground and connecting all of them by a earthing flat/strip. Illustration of such drawing may help the young engineers to learn and execute.
  16. Nadun
    Jun 26, 2015
    Could u please explain me how to do the earth mat design for 220/132/33 kV Outdoor GSS which have 5 steps (135m, 138m, 141m, 144m, 147m).
    Can’t do the Earth mat design separately for each step and finally connect each steps together. OR is it must to do the design for all the steps together?
    Since their is huge civil work in step 144m and 147m it may take some time, so we can start lower 3 level works if we can lay the earth mat.
    Thank you!
  17. RAJEEV SINGH
    Dec 03, 2014
    I want to design the Earthmat of Solar Park of 10MW consisting of 10 Nos. step up transformers spreading over huge land area, which is evacuating the power at 11kV level. Please suggest:
    i) whether the each earth mat is to be connected.
    ii) for DC earthing separate mat is provided?
    iii) spacing between conductors and material??
  18. radixit
    Aug 14, 2014
    I want to design the earth mat of a 33/11 kv substationat kanpur for which i want to know the fault current the resistivity we have found 22 ohm met and IEEE80 formule is not available,there fore I WANT YOUR HELP
  19. ramesh
    Jun 30, 2014
    Among the inputs data, i don’t understand what you mean by the following, which is both required in your program:
    i) Reference Depth of Grid and Depth of Earthing Grid Conductor
    ii) Diameter of Earthing Grid Conductor or size of earthmat flat
    iii) Number of adjacent earthing mat conductors
    iv) How evaluate the values Ks, Df
    Kindly explain what you mean by these terminologies, and where to get such inputs.
  20. Robinson
    May 15, 2014
    (i) Number of adjacent earthing mat conductors
    (ii) Margin factor in earthing mat against corrosion and rusting.
  21. esaivani
    Feb 12, 2014
    sir,
    explain the brief note for earth mat calculation
  22. Eric.Bernays
    Sep 07, 2013
    Is there a version for use in the UK?
  23. mcalderac
    Jul 17, 2013
    thanks for this page. ***** five stars !!!!
  24. dieng
    Jun 20, 2013
    Great Job man! Thanks a lot!
  25. Roshan Mathew Verghese
    Nov 01, 2012
    Hi edvard,
    could you put up an article for measuring the Earth Resistance, Step & Touch potentials, using a Injection transformer ?
  26. akira
    Oct 25, 2012
    Dear Sir
    Thank you for this subject , i need to know how to determine required no. of earthing rods?
  27. RAGHAVENDRA KUMAR
    Aug 28, 2012
    Can u send me the details required to design an earth mat for 132/33KV Substation which the area consist of 12400 Sqm and 13620 SqM?
  28. keLvinz0r
    May 31, 2012
    GREAAAAT JOB!
    I’M YOUR FAN!
  29. Pandiyan
    Dec 29, 2011
    Sir,
    Can u send me the details required to design an earth mat for 230/110KV GIS Substation which the area consist of 60by 75 mtrs?