Power Factor Correction Calculation
Calculation of the energy savings
In order to calculate power factor correction for your installation, your should follow the steps below:
Step 1 – Calculate Actual Load (kW)
(Load) Power kW = Volts V x √3 x Current I x Power factor Pf
Step 2 – Calculate Required Power Factor Correction (kVAr)
Power Factor Correction kVAr = Power kW (TanΦi – TanΦd)
Φi = Cos-1 Initial Power Factor Pf
Φd = Cos-1 Required Power Factor Pf
Step 3 – Calculate Actual Power Factor Correction [kAVrl
Actual Power Factor Correction Pf = Cos (Tan-1 (TanΦiCorrection kVAr/Power kW ))
Typical Power Factor Correction available in multiples of 25kVAR’s, for further details please Contact Blakley Electrics Technical Department.
At the end of the spreadsheet you will get the calculation of the energy savings for above power factor correction.
  1. Initial Current (Amps)
  2. Original Load (kVA)
  3. Corrected Current (Amps)
  4. Corrected Load (kVA)
  5. Reduction in Current (Amps)
  6. Reduction in Load (kVA)
  7. Annual CO2 Savings ( kg C02)
Software:Power Factor Correction Calculation
Version:
Developer:Blakley Electrics
Price:
Power Factor Correction Calculation Spreadsheet
19 Comments
  1. احمد خضور
    Nov 07, 2023
    Goodies
  2. hamdy a osman
    Jun 03, 2023
    pls send me power factor calculation sheet
    pls send me M VOLTAGE CABLE CALCULATION SHEET
  3. Prateek Shukla
    Dec 07, 2021
    Plz send me pdf file, regard required power factor calculation..
  4. Daniel Smith
    May 04, 2021
    Great info you have shared here.
  5. Tiger
    Jan 26, 2021
    Hi, Share calculation
  6. Bakhshi
    Nov 24, 2020
    Thanks for sharing such kind useful article.
  7. Mayur Tichkule
    Feb 29, 2020
    I am an electrical engineer In Nagpur good information i got from your site.
    thanks a lot.
  8. RAJADURAI.K
    Nov 21, 2018
    Hello sir’
    im working as a electrical design engineer
    kindly please clear my doubts
    1) how to find the incomer current rating for APFCR panel ?
    2) how to find the breaker current rating for the 25kvar & 50kvar capacitor ?
    please give the answer??
    and i refer this method its right or wrong??
    Kvar= 1.73*V*I*Sin$ ($ IS INSTESD OF PHASE ANGLE PHI)
    so I= kVAR/1.73*V*SIN$
    IN A PURELY CAPACITIVE CIRCUIT $ IS 90 DEGREE
    SO TERM SIN 90 = 1
    HENCE WE CAN CALCULATE CAPACITOR CURRENT BY kVAR/1.73*V
  9. Vijayakumar
    Oct 23, 2018
    Sir, please tell me formula for improve power factor.. And which type of problems occur in industry’s when we maintain leading power factor
  10. bismarck vigo
    Oct 19, 2018
    Excelente portal, gracias por las publicaciones.
  11. Md Saleem
    Dec 26, 2017
    Hello Friends,
    I want to learm Electrical Engineering. Where i start because lot of topics in the electrical. Please guide me.
    mail id : [email protected]
  12. bvenu
    Oct 05, 2015
    sir i am working as a technician in private industry, plant is running with load about 900 kva how much capacitance we should need to connect, what kind of problems arise when we are connect capacitance more than required value kindly send the answer to my mail id
    thanking you sir.
    • Domicel
      Feb 05, 2018
      You will spend more capacitors than necessary, I presume thati It is expensive. You will loose money. And if there were a much more capacitance, you will need more KVAr again, but now capacitive.
  13. nirnal kumar
    Aug 07, 2015
    sir, give me formula for improve power factor. how can i get which capacitor will improve power fsctor
  14. eng.saif.
    May 17, 2015
    thanks a lot for sharing of important electrical information .I thinks this side is very helpful for EEE ,MEE,
  15. ghasem razeghi
    Mar 09, 2015
    I am an electrical engineer graduated from s.j.c.e mysore – india .
    thanks a lot.
  16. Revocatus Mwankemwa
    Jan 10, 2015
    The information I have got are very useful and are of great importance to the problem that I was working on.
  17. Kalim Rahman
    Nov 11, 2014
    How to find out the wire size for connecting to PFI unit?? We have an 800kva substation.
  18. Santanu Mukherjee
    Dec 21, 2013
    Thanks for sharing such nice information