Fundamental characteristics of circuit breakers
Fundamental characteristics of circuit breaker – Schneider Electric (Compact NSX – New breed of circuit breakers)
Circuit breaker characteristics //
The fundamental characteristics of a circuit breaker are:
  • Its rated voltage Ue
  • Its rated current In
  • Its tripping current level adjustment ranges for overload protection (Ir or Irth) and for short circuit protection (Im)
    NOTE: Current-level setting values which refer to the currentoperated thermal and “instantaneous” magnetic tripping devices for over-load and short circuit protection.
  • Its short circuit current breaking rating (Icu for industrial CBs; Icn for domestictype CBs).
Rated operational voltage (Ue)
This is the voltage at which the circuit breaker has been designed to operate, in normal (undisturbed) conditions. Other values of voltage are also assigned to the circuit breaker, corresponding to disturbed conditions.
Rated current (In)
This is the maximum value of current that a circuit breaker, fitted with a specified overcurrent tripping relay, can carry indefinitely at an ambient temperature stated by the manufacturer, without exceeding the specified temperature limits of the current carrying parts.
Example
A circuit breaker rated at In = 125A for an ambient temperature of 40 °C will be equipped with a suitably calibrated overcurrent tripping relay (set at 125 A). The same circuit breaker can be used at higher values of ambient temperature however, if suitably “derated”.
Thus, the circuit breaker in an ambient temperature of 50 °C could carry only 117 A indefinitely, or again, only 109 A at 60 °C, while complying with the specified temperature limit.
Derating a circuit breaker is achieved therefore, by reducing the trip-current setting of its overload relay, and marking the CB accordingly. The use of an electronic-type of tripping unit, designed to withstand high temperatures, allows circuit breakers (derated as described) to operate at 60 °C (or even at 70 °C) ambient.
NOTE: In for circuit breakers (in IEC 60947-2) is equal to Iu for switchgear generally, Iu being the rated uninterrupted current.
Frame-size rating
A circuit breaker which can be fitted with overcurrent tripping units of different current level-setting ranges, is assigned a rating which corresponds to the highest current level-setting tripping unit that can be fitted.
Example
A Compact NSX630N circuit breaker can be equipped with 11 electronic trip units from 150 A to 630 A. The size of the circuit breaker is 630 A. Overload relay trip-current setting (Irth or Ir)
Apart from small circuit breakers which are very easily replaced, industrial circuit breakers are equipped with removable, i.e. exchangeable, overcurrent-trip relays. Moreover, in order to adapt a circuit breaker to the requirements of the circuit it controls, and to avoid the need to install over-sized cables, the trip relays are generally adjustable. The trip-current setting Ir or Irth (both designations are in common use) is the current above which the circuit breaker will trip. It also represents the maximum current that the circuit breaker can carry without tripping.
That value must be greater than the maximum load current IB, but less than the maximum current permitted in the circuit Iz.
The thermal-trip relays are generally adjustable from 0.7 to 1.0 times In, but when electronic devices are used for this duty, the adjustment range is greater; typically 0.4 to 1 times In.
Example (see Figure 1)
Example of a NSX630N circuit-breaker
Figure 1 – Example of a NSX630N circuit breaker equipped with a Micrologic 6.3E trip unit adjusted to 0.9, to give Ir = 360 A
A NSX630N circuit breaker equipped with a 400 A Micrologic 6.3E overcurrent trip relay, set at 0.9, will have a trip-current setting:
Ir = 400 x 0.9 = 360 A
NOTE: For circuit breakers equipped with non-adjustable overcurrent-trip relays, Ir = In. Example: for C60N 20 A circuit breaker, Ir = In = 20A.
Short circuit relay trip-current setting (Im)
Short circuit tripping relays (instantaneous or slightly time-delayed) are intended to trip the circuit breaker rapidly on the occurrence of high values of fault current. Their tripping threshold Im is:
  • Either fixed by standards for domestic type CBs, e.g. IEC 60898, or,
  • Indicated by the manufacturer for industrial type CBs according to related standards, notably IEC 60947-2.
For the latter circuit breakers there exists a wide variety of tripping devices which allow a user to adapt the protective performance of the circuit breaker to the particular requirements of a load (see Figures 2, 3 and 4).
Tripping-current ranges of overload and short-circuit protective devices for LV circuit-breakers
Figure 2 – Tripping-current ranges of overload and short circuit protective devices for LV circuit breakers
(1) 50 In in IEC 60898, which is considered to be unrealistically high by most European manufacturers (Schneider Electric = 10 to 14 In).
(2) For industrial use, IEC standards do not specify values. The above values are given only as being those in common use.
Performance curve of a circuit-breaker (thermal-magnetic, electronic)
Figure 3 (left) – Performance curve of a circuit breaker thermal-magnetic protective scheme; Figure 4 (right) – Performance curve of a circuit breaker electronic protective scheme
• Ir: Overload (thermal or long-delay) relay trip-current setting
• Im: Short circuit (magnetic or short-delay) relay trip-current setting
• Ii: Short circuit instantaneous relay trip-current setting.
• Icu: Breaking capacity
Isolating feature
A circuit breaker is suitable for isolating a circuit if it fulfills all the conditions prescribed for a disconnector (at its rated voltage) in the relevant standard. In such a case it is referred to as a circuit breaker-disconnector and marked on its front face with the symbol
All Acti 9, Compact NSX and Masterpact LV switchgear of Schneider Electric ranges are in this category.
Rated short circuit breaking capacity (Icu or Icn)
The short circuit current-breaking rating of a CB is the highest (prospective) value of current that the CB is capable of breaking without being damaged. The value of current quoted in the standards is the rms value of the AC component of the fault current, i.e. the DC transient component (which is always present in the worst possible case of short circuit) is assumed to be zero for calculating the standardized value.
This rated value (Icu) for industrial CBs and (Icn) for domestic-type CBs is normally given in kA rms. Icu (rated ultimate s.c. breaking capacity) and Ics (rated service s.c. breaking capacity) are defined in IEC 60947-2 together with a table relating Ics with Icu for different categories of utilization A (instantaneous tripping) and B (time-delayed tripping).
Tests for proving the rated s.c. breaking capacities of CBs are governed by standards, and include:
  • Operating sequences, comprising a succession of operations, i.e. closing and opening on short circuit
  • Current and voltage phase displacement. When the current is in phase with the supply voltage (cos ϕ for the circuit = 1), interruption of the current is easier than that at any other power factor. Breaking a current at low lagging values of cos ϕ is considerably more difficult to achieve; a zero power factor circuit being (theoretically) the most onerous case.
In practice, all power-system short circuit fault currents are (more or less) at lagging power factors, and standards are based on values commonly considered to be representative of the majority of power systems. In general, the greater the level of fault current (at a given voltage), the lower the power factor of the fault-current loop, for example, close to generators or large transformers.
Figure 5 below extracted from IEC 60947-2 relates standardized values of cos ϕ to industrial circuit breakers according to their rated Icu.
Following an open – time delay – close/open sequence to test the Icu capacity of a CB, further tests are made to ensure that:
  • The dielectric withstand capability
  • The disconnection (isolation) performance and
  • The correct operation of the overload protection have not been impaired by the test.
Icu related to power factor (cos ϕ) of fault-current circuit (IEC 60947-2)
Figure 5 – Icu related to power factor (cos ϕ) of fault-current circuit (IEC 60947-2)
There are other characteristics of a circuit-breaker that are not mentioned in this article: rated insulation voltage, rated impulse-withstand voltage, rated short-time withstand current, rated making capacity, rated service short-circuit breaking capacity and fault-current limitation
Resource: Schneider Electric – Electrical Installation Guide 2010
9 Comments
  1. Heramb Mayadeo
    Oct 08, 2020
    Hello Edvard,
    When we set the thermal overload setting of the LVCB how the tolerance zone of the CB is taken into account? A CB set at Ir=360A will not trip at 365A. It will have some tolerance zone. How do I make sure that it will trip above 360 A but not below that in presence of the tolerance zone?
  2. Ricardo França
    Jul 15, 2014
    One does not need to worry about the frequency of Ue? As when using AC drivers for controlling motors, the voltage frequency applied can be something like 400Hz. In this case, the characteristic of operation remain the same?
  3. xavier
    Jun 25, 2014
    Very useful
  4. cso
    Dec 11, 2012
    Hello Edvard,
    Can you help me understand a characteristic of LVCB’s in the range of 600 amp frames with trip units consisting adjustable ground fault settings. It seems there are breakers with either a residual ground scheme, or a source-ground-return type scheme. I’m wondering if there are advantages to choosing one scheme over the other, or does their application depend on the location of the breaker with respect to a grounded transformer. I notice feeder breakers typically use breakers with ground schemes of the residual type.
    Thank you,
    CS
  5. Dorin Pestereanu
    Jun 07, 2012
    Very useful for all electrical engineer , I liked that , Edvard …, Of course all EEP it’s very important and very
    useful ; I love EEP portal !!!!
    My best regards ,
    Dorin Pestereanu
    senior electrical engineer
      Thank you very much Dorin! Very nice of you!
  6. roshan46
    Jun 07, 2012
  7. V.T.APPUSWAMY
    Jun 06, 2012
    Good. Useful for new engineers, technicians and for experienced practising engineers. Nice. Uesful. I enjoyed reading it. Regards V.T.APPUSWAMY
      Thank you very much! Glad you find it usefull!