Home / Technical Articles / 31 Common Household Circuit Wirings You Can Use For Your Home (2)
1st part | 2nd part | 3rd part
31 Common Household Circuit Wirings You Can Use For Your Home (2nd part)
The list of the next ten household circuit wirings:
  1. Double receptacle circuit with shared neutral wire (receptacles alternate circuits)
  2. Double receptacle small-appliance circuit with GFCIs & shared neutral wire
  3. Double receptacle small appliance circuit with GFCIs & separate neutral wires
  4. 120/240V range receptacle
  5. 240V Baseboard heaters, thermostat
  6. Dedicated 120v computer circuit, isolated-ground receptacle
  7. 240V appliance receptacle
  8. Ganged single-pole switches controlling separate light fixtures
  9. Ganged switches controlling a light fixture and a vent fan
  10. Three-way switches & light fixture (fixture between switches)
11. Double receptacle circuit with shared neutral wire (receptacles alternate circuits)
This layout features two 120 V circuits wired with one three-wire cable connected to a double-pole circuit breaker. The black hot wire powers one circuit. The red wire powers the other. The white wire is a shared neutral that serves both circuits.
When wired with 12/2 and 12/3 cable and receptacles rated for 20 A, this layout can be used for the two small-appliance circuits required in a kitchen.
Remember to use a GFCI circuit breaker if you use this circuit for kitchen counter top receptacles.
This layout features two 120-volt circuits wired with one three-wire cable connected to a double-pole circuit breaker
Go back to Circuit Wirings ↑
12. Double receptacle small-appliance circuit with GFCIs & shared neutral wire
Use this layout variation of circuit wiring 10 to wire a double receptacle circuit when code requires that some of the receptacles be GFCIs. The GFCIs should be wired for single-location protection (see circuit wiring 2).
Requires three-wire and two-wire cables.
13. Double receptacle small appliance circuit with GFCIs & separate neutral wires
If the room layout or local codes do not allow for a shared neutral wire, use this layout instead. The GFCIs should be wired for single-location protection (see circuit wiring 2).
Requires two-wire cable.
14. 120/240V range receptacle
This layout is for a 40- or 50 A, 120/240 V dedicated appliance circuit wired with 8/3 or 6/3 cable, as required by code for a large kitchen range. The black and red circuit wires, connected to a double-pole circuit breaker in the circuit breaker panel, each bring 120 volts of power to the setscrew terminals on the receptacle.
The white circuit wire attached to the neutral bus bar in the circuit breaker panel is connected to the neutral setscrew terminal on the receptacle.
This layout is for a 40- or 50-amp, 120/240-volt dedicated appliance circuit wired with 8/3 or 6/3 cable
15. 240V Baseboard heaters, thermostat
This layout is typical for a series of 240 V baseboard heaters controlled by a wall thermostat. Except for the last heater in the circuit, all heaters are wired as shown below. The last heater is connected to only one cable.
The sizes of the circuit and cables are determined by finding the total wattage of all heaters.
This layout is typical for a series of 240-volt baseboard heaters controlled by a wall thermostat
16. Dedicated 120v computer circuit, isolated-ground receptacle
This 15 A isolated-ground circuit provides extra protection against surges and interference that can harm electronics. It uses 14/3 cable with the red wire serving as an extra ground ing conductor. The red wire is tagged with green tape for identification.
It is connected to the grounding screw on an isolated-ground receptacle and runs back to the grounding bus bar in the circuit breaker panel without touching any other house wiring.
This 15-amp isolated-ground circuit provides extra protection against surges and interference that can harm electronics
17. 240V appliance receptacle
This layout represents a 20 A, 240 V dedicated appliance circuit wired with 12/2 cable, as required by code for a large window air conditioner. Receptacles are available in both singleplex (shown) and duplex styles.
The black and the white circuit wires connected to a double-pole breaker each bring 120 volts of power to the receptacle (combined, they bring 240 volts).
The white wire is tagged with black tape to indicate it is hot.
This layout represents a 20-amp, 240-volt dedicated appliance circuit wired with 12/2 cable
18. Ganged single-pole switches controlling separate light fixtures
This layout lets you place two switches controlled by the same 120 V circuit in one double-gang electrical box. A single-feed cable provides power to both switches. A similar layout with two feed cables can be used to place switches from different circuits in the same box.
This layout lets you place two switches controlled by the same 120-volt circuit in one double-gang electrical box
19. Ganged switches controlling a light fixture and a vent fan
A standard switch controls the light fixture, and a time-delay switch controls the vent fan.
20. Three-way switches & light fixture (fixture between switches)
This layout for three-way switches lets you control a light fixture from two locations. Each switch has one common screw terminal and two traveler screws. Circuit wires attached to the traveler screws run between the two switches, and hot wires attached to the common screws bring current from the power source and carry it to the light fixture.
Requires parallel runs of 2-wire cable.
Reference // The Complete Guide to Electrical Wiring (Current with 2014–2017 Electrical Codes) – Black+Decker