Home / Technical Articles / Inspection and Test Procedures for Metal-Enclosed Busways
Content
  1. Visual and Mechanical Inspection
  2. Electrical Tests
  3. Test Values
    1. Test Values – Visual and Mechanical
    2. Test Values – Electrical
  4. Tables:
    1. TABLE 100.12 – US Standard Fasteners Bolt-Torque Values for Electrical Connections
    2. TABLE 100.1 – Insulation Resistance Test Values Electrical Apparatus and Systems
    3. TABLE 100.17 – Dielectric Withstand Test Voltages for Metal-Enclosed Bus
1. Compare equipment nameplate datawith drawings and specifications.
2. Inspect physical and mechanical condition of busway system
3. Inspect anchorage, alignment, and grounding.
4. Verify correct connection in accordance with single-line diagram.
5. Inspect bolted electrical connections for high resistance using one or more of the following methods:
  • Use of a low-resistance ohmmeter in accordance with Section 2 (Electrical Tests).
  • Verify tightness of accessible bolted electrical connections and bus joints by calibrated torque-wrench method in accordance with manufacturer’s published data or Table 100.12 below.
  • Perform thermographic survey
    (NOTE: Remove all necessary covers prior to thermographic inspection. Use appropriate caution, safety devices, and personal protective equipment.)
6. Confirm physical orientation in accordance with manufacturer’s labels to insure adequate cooling.
7. Examine outdoor busway for removal of “weep-hole” plugs, if applicable, and the correct installation of joint shield.
Go to Content ↑
2. Electrical Tests
1. Perform resistance measurements through bolted connections and busjoints with a low-resistance ohmmeter, if applicable, in accordance with Section 1 (Visual and Mechanical Inspection).
2. Measure insulation resistance of each busway, phase-to-phase and phase-to-ground for one minute, in accordance with Table 100.1 below.
3. Perform a dielectric withstand voltage test on each busway, phase-to-ground with phases not under test grounded, in accordance with manufacturer’s published data. In the absence of manufacturer’s published data, use Table 100.17.
Where no dc test value is shown in Table 100.17, ac value shall be used. The test voltage shall be applied for one minute.
4. Perform a contact-resistance test on each connection point of uninsulated busway. On insulated busway, measure resistance of assembled busway sections and compare values with adjacent phases.
5. Perform phasing test on each busway tie section energized by separate sources. Tests must be performed from their permanent sources.
6. Verify operation of busway space heaters.
Go to Content ↑
3. Test Values
3.1 Test Values – Visual and Mechanical
1. Compare bolted connection resistance values to values of similar connections. Investigate values which deviate from those of similar bolted connections by more than 50 percent of the lowest value. (7.4.1.5.1)
2. Bolt-torque levels should be in accordance withmanufacturer’s published data. In the absence of manufacturer’s published data, use Table 100.12. (7.4.1.5.2)
3. Results of the thermographic survey shall be in accordance with Section 9. (7.4.1.5.3)
Go to Content ↑
3.2 Test Values – Electrical
2. Insulation-resistance test voltages and resistance values shall be in accordance with manufacturer’s published. In the absence of manufacturer’spublished data, use Table 100.1.
Minimum resistance values are for a nominal 1000-foot busway run. Use the following formula to convert the measured resistance value to the 1000-foot nominal value:
Busway run - minimum resistance formula
Converted values of insulation resistance less than those in Table 100.1 or manufacturer’s minimum should be investigated. Dielectric withstand voltage tests shall not proceed until insulation-resistance levels are raised above minimum values.
3. If no evidence of distress or insulation failure is observed by the end of the total time of voltage application during the dielectric withstand test, the test specimen is considered to have passed the test.
4. Microhm or dc millivolt drop values shall not exceed the high levels of the normal range as indicated in the manufacturer’s published data.
If manufacturer’s published data is not available, investigate values which deviate from those of similar bus connections and sections by more than 50 percent of the lowest value.
5. Phasing test results shall indicate the phase relationships are in accordance with system design.
6. Heaters shall be operational.
Go to Content ↑
TABLE 100.12
US Standard Fasteners – Bolt-Torque Values for Electrical Connections
Table 100.12.1 - Heat-Treated Steel - Cadmium or Zinc Plated
Table 100.12.1 – Heat-Treated Steel – Cadmium or Zinc Plated
Table 100.12.2 - Silicon Bronze Fasteners
Table 100.12.2 – Silicon Bronze Fasteners
Table 100.12.3 - Aluminum Alloy Fasteners
Table 100.12.3 – Aluminum Alloy Fasteners
Table 100.12.4 - Stainless Steel Fasteners
Table 100.12.4 – Stainless Steel Fasteners
a. Consult manufacturer for equipment supplied with metric fasteners.
b. This table is based on bronze alloy bolts having a minimum tensile strength of 70,000 pounds per square inch.
c. This table is based on aluminum alloy bolts having a minimum tensile strength of 55,000 pounds per square inch.
d. This table is to be used for the following hardware types:
  • Bolts, cap screws, nuts, flat washers, locknuts (18–8 alloy)
  • Belleville washers (302 alloy).
Go to Content ↑
TABLE 100.1
Table 100.1 – Insulation Resistance Test Values for Electrical Apparatus and Systems
Go to Content ↑
TABLE 100.17
Table 100.17 – Dielectric Withstand Test Voltages for Metal-Enclosed Bus
Go to Content ↑
Resource: Acceptance Testing Specifications for Electrical Power Distribution Equipment and Systems – NETA 2003
  1. Romeo Pornea
    Aug 12, 2021
    What is the minimum acceptable insulation resistance for aluminum busduct rated to operate at 440Volts. Please indicate the code reference standard.
    Regards,
    Romeo
  2. Wisam sadik
    Feb 03, 2021
    What is the steps for inspection “ dielectric with stand voltage “ for busway of 1600A ?
    Answer me please ..
  3. Jose
    May 10, 2019
    Hi, this is a very interesting article. Congratulations!
    I have a question: what is the acceptable insulation resistance of a 2500Amp copper busway 173 feet long?
    This riser is made of two busways in parallel, rated 2500 amps
    Thanks!
    Jose
  4. Amro
    Mar 01, 2018
    what is effect of rising of temperature within the busway at the 150% over loading continuously during 2 hr
32  ⁄  four  =
