Home / Technical Articles / Inspection, Test and Measurement Procedures for LV and MV (up to 36kV) Switchgears
Importance of checks and maintenance
Installed in clean, well ventilated or air-conditioned locations, switchgear will require little routine maintenance. Major inspection should be scheduled for power plant shutdowns and concentrate for low voltage switchboards on identifying contact wear, correct operation of interlocks, correct overload settings and fuse sizes, signs of overheating, and undue dirt or corrosion.
Inspection, Test and Measurement Procedures for LV and MV (up to 36kV) Switchgears (on photo" Eaton Cutler Hammer Magnum DS Switchgear Inspection, and Transformer Testing)
Inspection, Test and Measurement Procedures for LV and MV (up to 36kV) Switchgears (on photo” Eaton Cutler Hammer Magnum DS Switchgear Inspection, and Transformer Testing)
For MV switchgear similar considerations apply although more extensive checks on protective devices, circuit breaker oil, vacuum bottle contact distances are required as specified by the Manufacturer.
Exceptions to the above rule are devices which operate frequently, where inspection/overhaul may need to be based on the number of operations. Also, MV isolating devices which have cleared a short circuit will require confirmation that the insulating medium and the circuit contacts are fit for continued service.
Gas Insulated Switchgear (GIS) shall be maintained in accordance with the manufacturer’s recommendations. Where extensive (intrusive) maintenance is required, the Manufacturer should be involved in the activity.
For older switchgear, a condition assessment should be performed to establish that the equipment remains in a suitable condition for further service.
Partial discharge testing and infrared scanning can be used to obtain data on the performance of the insulation system and the integrity of the switchgear busbars and cable terminations. The frequency of such tests will depend on the duty, age and condition of the switchgear.
Infrared partial discharge testing
Infrared partial discharge testing (photo credit: reliabilityweb.com)
NOTE //
The effectiveness of infra-red scanning depends on the ability to access the current-carrying components under loaded condition. Scanning through metallic enclosures has generally proved ineffective. Removal of enclosures of live equipment may not be possible without compromising electrical safety.
LV switchgear
TypeDescriptionIntervalExtent
1. INSPECTIONGeneral external condition.1 yAll
Motor starters and outgoing feeders, internal.
Incomers, internal.
4 y
Busbar compartments (1).8 y
Metering:
– Correctness main voltmeters.
– Correctness main ammeters.
4y
General internal condition of outdoor equipment (5).2 y
2. TEST AND
MEASUREMENT (3)
Incoming feeders, bus section, switches:
– Operating mechanism.
– Interlocks.
– Control equipment.
– Electrical protection/tripping (2).
4 yAll
Busbar systems:
– Torque bolts (1).
– Insulation resistance.
– Continuity (ductor).
8 y
Motor feeders:
– Draw-out system/interlocks.
– Cable connection tightness.
4 y
Thermal and earth fault protection.4 y10%
Certified Ex ‘e’ thermal protection (4).3 yAll
Restart system.4 y10%
Insulation resistance of motor + cable.4 yselected
Plain feeders:
4 yAll
Protection/tripping. (2)4 y10%
R.C.D. for fixed load (e.g. trace heating).4 yAll
NOTES:
  1. Access to modern, high integrity, insulated/segregated busbar systems may be difficult. In this case other test and measurements as indicated should give sufficient information on the actual condition.
  2. CT connected protection relays should be tested by means of secondary injection.
  3. Testing of change-over systems of emergency switchboards should coincide with the testing of the emergency generator/system.
  4. Type of protection ‘e’. Motor protection devices are selected so that the tripping time from hot when the locked rotor current of the motor is carried, is carried with the motor in the stalled condition, is less than the time tE on the motor nameplate.
  5. Internal inspection should be limited to contactor/control equipment installed out of doors in boxes, e.g. MOV control panels.
MV switchgear (up to 36 kV)
Cable boxes internal.
Circuit breakers internal.
Fused contactors internal.
4 y
Busbar compartments (1) internal.8 y
Metering:
– Correctness of main voltmeters.
– Correctness of main ammeters.
– Correctness of other measuring  systems.
4 yAll
2. TEST AND
MEASUREMENT (3)
Circuit breakers in/outgoing and fused
contactors (3):
4 yAll
Dielectric strength across open  contacts.8 y
Ductor test across closed contacts.
4 y
Certified Ex’e’ thermal protection (4).3 y
Contact distance.4 yVacuum, SF6
Dielectric test oil.4 yOil-immersed
Insulation resistance of cable (incl.  motor if applicable).4 y All
Restart system.4 y Motors
Busbar systems:
– Torque bolts (1).
– Dielectric strength.
 8 yAll
Correctness of kW, kVAr, max.
demand of measuring systems (5).
 4 y
3. RESTORATIONGreasing of operating mechanisms. 4 yAll
Oil filtering/replacement.
Component replacement.
As necessary
NOTES:
  3. After operation of the circuit breaker/contactor following a short circuit, the proper operation of switching device and its protection shall be tested.
    Motor protection devices are selected so that the tripping time from hot when carrying the locked rotor current of the motor is carried, with the motor in the stalled condition, is less than the stated time tE on the motor nameplate.
  5. Where used for tariff purposes.
Reference: Field commissioning and maintenance of electrical installations and equipment // DEP 63.10.08.11-Gen.
7 Comments
  1. A.Jokar
    May 05, 2018
    Dear Edward
    Is any established standard like IEC or IEEE for interval inspection of busbar and earthing systems.
    ASGHAR JOKAR
  2. Huynh Quoc Dan
    Mar 02, 2017
    It is a very good guidance
  3. shahnawaz shaikh
    Jul 12, 2015
    good explanation
  4. George Batlhaodi
    Jan 30, 2015
    Thanks Edvard, you explain very easy
  5. Abdul Rahman
    Jan 17, 2015
    Dear Edvard, you have a very good style of explaining a Technical subject in a simple & easy to understand language, keep it up.
  6. kanchi
    Jan 17, 2015
    this blog very use full . i share with my friends
