Principle of discrimination

Protection functions form a consistent system depending on the overall structure of the power distribution system and the neutral earthing arrangement. They should therefore be viewed as a system based on the principle of discrimination, which consists of isolating the faulty part of the power system and only that part as quickly as possible, leaving all the fault-free parts of the power system energized.

Isolating the Fault With Time-based Discrimination
Isolating the Fault With Time-based Discrimination (photo credit: atlaselectricinc.com)

Various means can be used to implement discrimination in power system protection:

  1. Time-based discrimination,
  2. Current-based discrimination,
  3. Discrimination by data exchange, referred to as logic discrimination,
  4. Discrimination by the use of directional protection functions,
  5. Discrimination by the use of differential protection functions,
  6. Combined discrimination to ensure better overall performance (technical, economic), or back-up.

Principle of Time-based discrimination

Time-based discrimination consists of assigning different time delays to the overcurrent protection units distributed through the power system.

The closer the protection relay is to the source, the longer the time delay.


Operating mode

The fault shown in the diagram opposite (fig. 1) is detected by all the protection units (at A, B, C, and D). The contacts of delayed protection unit D close faster than those of protection unit C, which themselves close faster than those of protection unit B…

Once circuit breaker D tripped and the fault current has been cleared, protection units A, B and C, which are no longer required, return to the stand-by position. The difference in operation time DT between two successive protection units is the discrimination interval.

Figure 1 - Time-based discrimination principle
Figure 1 – Time-based discrimination principle

It takes into account (fig. 2):

  • Breaking time Tc of the downstream circuit breaker, which includes the breaker response time and the arcing time,
  • Time delay tolerances dT,
  • Upstream protection unit overshoot time: tr,
  • A safety margin m.
Breakdown of a discrimination interval
Figure 2 – Breakdown of a discrimination interval
ΔT should therefore satisfy the relation:

ΔT ≥ Tc + tr + 2dT + m

Considering present switchgear and relay performances, ΔT is assigned a value of 0.3 s.

Example Tc = 95 ms, dT = 25 ms, tr = 55 ms; for a 300 ms discrimination interval, the safety margin is 100 ms.


Advantages of Time-based Discrimination

This discrimination system has two advantages:

  1. It provides its own back-up; for example if protection unit D fails, protection unit C is activated ΔT later,
  2. It is simple.


Drawbacks

However, when there are a large number of cascading relays, since the protection unit located the furthest upstream has the longest time delay, the fault clearing time becomes prohibitive and incompatible with equipment short-circuit current withstand and external operating necessities (e.g. constraint imposed by utility).

Application

This principle is used in radial power systems. (fig. 4). The time delays set for time-based discrimination are activated when the current exceeds the relay settings. The settings must be consistent.

Radial power system with time-based discrimination
Figure 4 – Radial power system with time-based discrimination

There are two cases, according to the type of time delay used:

Definite time relays (fig. 5)

The conditions to be fulfilled are: IsA > IsB > IsC et TA > TB > TC.

The discrimination interval ΔT is conventionally in the range of 0.3 seconds.

Time-based discrimination with definite time relays
Figure 5 – Time-based discrimination with definite time relays

IDMT relays (fig. 6)

If the thresholds are set to the rated current In, overload protection is ensured at the same time as short-circuit protection and setting consistency is guaranteed.

Time-based discrimination with IDMT relays
Figure 6 – Time-based discrimination with IDMT relays

InA > InB > InC
IsA = InA, lsB = InB, and IsC = InC

The time delays are set to obtain the discrimination interval DT for the maximum current seen by the downstream protection relay. The same family of curves is used to avoid overlapping in a portion of the domain.

Resource: Protection Guide 2003 – Schneider  Electric

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.