Home / Technical Articles / Energy and Power / MCB – Miniature Circuit Breaker Construction
Introduction to MCB
The miniature circuit breaker (MCB) plays an important role in providing overcurrent protection and a disconnect means in electrical networks. Recent advancements in circuit breaker technology has increased breaker performance and protection.
MCB - Miniature circuit breaker construction
MCB – Miniature circuit breaker construction (on photo: ABBs MCB NA C16, 16A, 10kA, 3-pole-neutral)
A breaker is a device designed to isolate a circuit during an overcurrent event without the use of a fusible element. A breaker is a resettable protective device that protects against two types of overcurrent situations:
  1. Overload and
  2. Short Circuit.
MCB Construction Details
MCB - Miniature circuit breaker construction details
MCB – Miniature circuit breaker construction details
Thermal / Magnetic trip units
Current Limiting Breakers use an electromechanical (Thermal /Magnetic) trip unit to open the breaker contacts during a overcurrent event. The thermal trip unit is temperature sensitive and the magnetic trip unit is current sensitive.
Both units act independently and mechanically with the breaker’s trip mechanism to open the breaker’s contacts.
Current Flow
MCB - Miniature circuit breaker current flow during operation
MCB – Current flow during operation (All highlighted components are energized during operation)
Overload protection
The thermal trip unit protects against a continuous overload. The thermal unit is comprised of a bimetal element located behind the circuit breaker trip bar and is part of the breaker’s current carrying path.
When there is an overload, the increased current flow heats the bimetal causing it to bend. As the bimetal bends it pulls the trip bar which opens the breaker’s contacts. The time required for the bimetal to bend and trip the breaker varies inversely with the current. Because of this, the tripping time becomes quicker as current increases in magnitude. Overload protection is applicable to any installation, conductor, or component which can be subjected to low-magnitude but longtime over-currents.
Low-magnitude, long-time over-currents can be dangerous because they reduce the life of the electrical installation, conductor, and components and if left unchecked could result in fire.
MCB - Miniature circuit breaker overload protection
MCB Overload protection
Magnetic trip units (short circuit protection)
The Magnetic trip unit protects against a short circuit. The magnetic trip unit is comprised of an electromagnet and an armature.
MCB - Miniature curcuit breaker magnetic trip units
MCB Magnetic trip units
Components of a magnetic trip unit
When there is a short circuit, a high magnitude of current passes through the coils creating a magnetic field that attracts the movable armature towards the fixed armature. The hammer trip is pushed against the movable contact and the contacts are opened.
The opening of the breakers contacts during a short circuit is complete in 0.5 milli-seconds.
MCB - Miniature curcuit breaker components of a magnetic trip unit
MCB Components of a magnetic trip unit
Arc runners / Arc chutes
The arc runner and arc chute limit and dissipate the arc energy during the interruption of an overload or short circuit event.
During an overload or short circuit event, the contacts of the breaker separate and an electrical arc is formed between the contacts through air. The arc is moved into the arch chute by “running” the arc down the interior of the breaker along the arc runner. When the arc reaches the arc chute it is broken into small segmented arcs. The segmented arcs split the overall energy level into segments less than 25V.
Each 25V segment does not have a high enough energy level to maintain an arc and all energy is naturally dissipated.
MCB - Miniature curcuit breaker Arc runners / Arc chutes
MCB Arc runners / Arc chutes
Breaker curves
Thermal Trip Unit (region one)
The first sloping region of the breaker curve is a graphical representation of the tripping characteristics of the thermal trip unit.
This portion of the curve is sloped due to the nature of the thermal trip unit. The trip unit bends to trip the breaker’s trip bar in conjunction with a rise in amperage (temperature) over time. As the current on the circuit increases, the temperature rises, the faster the thermal element will trip.
Example using the curve below:
If you had a 10A breaker and the circuit was producing 30 amps of current, the breaker would trip between 2 seconds and 1 minute. In this example you would find the circuit current on the bottom of the graph (Multiples of rated current). The first line is 10 amps (10 amp breaker x a multiple of one), the second line is 20 amps (10 amp breaker x multiple of 2), and the third line is 30 amps (10amp breaker x multiple of 3). Next you would trace the vertical 30A line up until it intersects the red portion of the breaker thermal curve.
If you follow the horizontal lines, on both sides of the red curve, to the left you will see that the breaker can trip as fast as 2 seconds and no slower than 1 minute.
Magnetic Trip Unit (region two)
This region of the breaker curve is the instantaneous trip unit. MCB – miniture circuit breaker’s instantaneous trip unit interrupts a short circuit in 2.3 to 2.5 milliseconds. Because of this the curve has no slope and is graphically represented as a vertical straight line.
Example using the curve above:
If you had a 10 amp breaker the magnetic trip element would interrupt a short circuit between 10 and 30 amps (10 amp breaker x multiple of 2 and 3) in 2.3 to 2.5 milliseconds.
Breaker Contacts (region three)
This region of the curve is the time required for the contacts of the breaker to begin to separate. The contacts will open in less than .5 milliseconds and is graphically represented by the bottom vertical portion of the curve.
MCB - Miniature curcuit breaker curves
MCB – Miniature curcuit breaker curves
Reference: ABB – Application guide | Miniature circuit breakers
6 Comments
  1. Rick
    Oct 24, 2015
    Region 2…instantaneous trip unit interrupts a short circuit in 2.3 to 2.5 milliseconds ? Is that correct ? It doesn’t correlate with the graph which shows time of about 0.02s @ 3xIn which is 20ms, not 2.3ms.
    • kohchunwee
      Feb 15, 2017
      the graph presents the standard. his description presents the speed/technology of this MCB.
  2. spj-ind
    Nov 20, 2014
    When an interruption occurs more load, then the value of the current through the bimetallic metal will increase which makes the temperature of the metal bimetallic greater. How much temperature until cb open.
  3. Muralikrishnan
    Aug 20, 2014
    Whether the MCB USE AS A MAIN SWITCH
  4. k srinivasa rao
    Apr 03, 2014
    article is good
  5. kruno
    Feb 12, 2014
    Could you elaborate what happens with bimetalic strip under shortcircuit? Does it warm’s up under very high current or the current does not last long enough (due to very fast openings of contacts) to generate enough heat to cause bending? ?