Home / Technical Articles / Medium voltage circuit breaker operating sequence
Rated switching sequence according to IEC, O – t – CO – t’ – CO. (cf. opposite diagram):
O – Represents opening operation
CO – Represents closing operation followed immediately by an opening operation
Three rated operating sequences exist:
  • Slow: O – 3 min – CO – 3 min – CO
  • Fast 1: O – 0.3 s – CO – 3 min – CO
  • Fast 2: O – 0.3 s – CO – 15 s – CO
NOTE: Other sequences can be requested from manufacturer.
Close/Open cycle
Assumption: O order as soon as the circuit breaker is closed
Close/Open cycle of medium voltage circuit breaker
Automatic reclosing cycle
Assumption: C order as soon as the circuit breaker is open, (with time delay to achieve 0.3 s or 15 s or 3 min).
Automatic reclosing cycle of medium voltage circuit breaker
SOURCE: Schneider Electric – Medium Voltage Technical Guide
  1. Muhammad Usman
    Mar 27, 2018
    Hello Sir!
    Please explain Auxiliary Contacts State (OW-OD-C) what mean by (OW, OD).
    Also help how ti analysis of timing graph of High voltage Breakers.
    Thanks!
  2. Erl Von Abong
    Jun 25, 2014
    Hello Sir,
    We have this rated operating sequence O-0.3s-CO-3min-CO VCB but our available unit have this rated operating sequence O-0.3s-CO-15s-CO.
    Is it OK to use?
    Please help.
    • Kamal
      Sep 04, 2014
      I suppose,
      Requirement is O-0.3s-CO-3min-CO. And available VCB is O-0.3s-CO-15s-CO.
      15s VCB is suitable for autoreclosing application while 3 min VCB can’t.
      Although 15s VCB can be used in place of 3 min VCB with suitable delay timer in circuit of breaker.
      I hope it is the answer of your question.
      Kamal
  3. sudamadhav
    Jan 07, 2013
    The article is quite not clear, i want a detailed explanation on this and where could i find articles or features or details about VCB’s. pls help
