Home / Technical Articles / Medium Voltage / 4 medium voltage switching equipment for primary substation installations
Medium voltage switching equipment
This technical article covers the medium voltage switching equipment intended mainly for primary substation installations. The target is to give some basic knowledge and difference between 4 main piece of MV switching equipment, especially in the view of distribution automation concept.
4 medium voltage switching equipment for primary substation installations (on photo: Vacuum MV circuit breaker mechanism)
Both indoor and outdoor installation alternatives are presented.
The indoor installation refers to the switching equipment used in metal-enclosed medium voltage switchgears. Main focus with the discussions is on the air-insulated solutions.
The following switching equipment will be covered:
  1. Circuit Breakers
  2. Contactors
  3. Switch Disconnectors
  4. Disconnectors
1. Circuit Breakers
A circuit breaker must be capable to make and break all the load and fault currents that it might be subjected to at the specific installation. Key factors with circuit breakers’ performance are:
  1. Opening (break) and closing (make) time,
  2. Rated continuous current-carrying capability,
  3. Rated dynamic short circuit withstand capability,
  4. Rated thermal short circuit withstand capability,
  5. Maximum operation voltage and
  6. Rated operation sequence.
Earlier, the small-oil circuit breakers were common on medium voltage indoor installations and air-blast or oil breakers in outdoor installations. Today, these technologies have been replaced with SF6 gas and vacuum technologies. SF6 gas is dominating with outdoor installations, whereas with indoor installations both vacuum and SF6 gas technologies are utilized.
Two main constructional types with circuit breakers are the live tank breakers and the dead tank breakers.
With live tank breakers, the outer surface of the breaking chamber is not earthed and is under primary voltage influence, thus “live.” With dead tank breakers, the outer surface of the breaking chamber is earthed, thus “dead.”
Dead tank breakers are generally only available for outdoor installations from 33 kV upwards.
On the left a ABB 66 kV live tank breaker and on the right a 66 kV dead tank breaker with bushing current transformers
Figure 1 – On the left a ABB 66 kV live tank breaker and on the right a 66 kV dead tank breaker with bushing current transformers
The circuit breakers for outdoor mounting are generally fixed ones, whereas the breakers intended for indoor use, as a part of metal-enclosed switchgears, are generally mounted on a truck, although exceptions exist.
The actuating system, operation mechanism, is the unit within the circuit breaker that supplies the power and movement for the primary contacts to close or open. Depending on the arc-extinguishing principle the breaker utilizes, the needed power is different.
Indoor-mounted 24 kV vacuum-type circuit breaker on a truck, type VD4
Figure 2 – Indoor-mounted 24 kV vacuum-type circuit breaker on a truck, type VD4
With modern design SF6 and vacuum breakers, the power need is relatively low. There are a number of different actuating systems available.
The choice between systems depends on the application, the breaker type and reliability as well as maintenance interval requirements. What is common for all the actuator systems is the demand for a fast response to control commands and the capability to store enough energy for the breaker to complete the specified operation sequence without recharging the energy storage.
The following actuator types are commonly available:
  1. Charged spring operation mechanism (spring)
  2. Pneumatic (compressed air)
  3. Hydraulic (compressed air)
  4. Hydraulic spring (Metallic spring bellows)
  5. Magnetic (capacitor)
Means of storing the energy with different actuator types is shown in the brackets. The control of the actuator within a circuit breaker is carried out by utilizing electrical commands, either locally or remotely. The electrical signal activates the shunt trip or closing coils that in turn will activate the actuator, either closing or opening the breaker.
Normally, also a mechanical control of the actuator to open the breaker is provided locally at the breaker, that is, the emergency trip. The traditional shunt coils can be replaced with an electronic circuit for actuator control. The important breakers, like the main power transformer feeders, at the higher distribution voltage levels are often equipped with duplicated tripping coils or corresponding electronic circuits.
For outdoor installations with a voltage level of 66 kV and up, the modern technology provides a possibility to combine the functionality of circuit breaker, disconnector and earthing switch into one physical component called disconnecting breaker (see this video).
The circuit breaker construction has been modified to fulfill the disconnector requirements in the open position. The earthing switch is separately mounted on the same disconnecting breaker unit and interlocked with the main contacts position.
66 kV Disconnecting circuit breaker with earthing switch
Figure 3 – 66 kV Disconnecting circuit breaker with earthing switch
Protection and control
The fast and reliable operation of the circuit breaker is of paramount importance for the complete distribution system. Therefore the operation of the breaker is closely monitored by the protection and control system, that is, the IEDs and the upper-level systems.
The modern IEDs are typically monitoring the following issues:
  1. Trip circuit continuity (both in open and closed positions)
  2. Breaker travel time (IED for fixed limits and upper-level systems for trends)
  3. Breaker stress (I2t, in the view of maintenance intervals)
  4. Breaker’s response to trip commands (breaker failure protection)
  5. Gas pressure or density in case of SF6 type of breakers
  6. Actuator’s energy storage charging current, like motor current with charged spring operation mechanism
Switching reactive loads, like shunt capacitors and unloaded power transformers, can be sometimes a source for undesired overvoltages or overcurrents.
To overcome this problem, a device for synchronized switching can be introduced. This device will coordinate the breaker’s control commands to perform the operation at the most advantageous time of the sinusoidal voltage waveform.
With three-phase breakers, one of the phases is monitored by the device and the other phases have a 120-degree mechanical delay in their operation, thus the breaker has to be specifically tuned for this kind of operation.
2. Contactors
Medium-voltage contactors are used instead of circuit breakers typically in industrial indoor metal-enclosed switchgear applications up to 12 kV where the switching frequency is very high, like certain motor feeders for pumps and fans.
The contactor is either the vacuum type or the SF6-insulated one.
Since the contactor cannot handle (break) the high fault currents associated with faults like short circuits, it is normally equipped with series HRC fuses. If the primary device, like motor, requires overload protection, the feeder in question can be equipped with a suitable protection IED.
In such cases, the IED protection functions’ settings will be coordinated with the contactor’s breaking capability and the protective fuse characteristics.
Different versions of medium voltage vacuum-type contactors
Figure 4 – Different versions of medium voltage vacuum-type contactors
Go back to contents ↑
The switch disconnectors, also called load disconnectors, are used either as fixed or truck- mounted switching devices in metal-enclosed indoor switchgears. The switch disconnector has a rated breaking capacity up to its rated nominal current, that is, the maximum load current, and it provides visual separation point fulfilling the requirements for isolation distance.
The making capacity normally corresponds to the short circuit rating of the switch. The switch disconnectors can be either air-insulated or gas-insulated ones. The unit can be further expanded with series HRC fuses and with line-side earthing disconnector.
An air-insulated indoor switch disconnector with fuses for fixed mounting
Figure 5 – IEC air-insulated switch disconnectors are suitable for cable sectionalizer, transformer, motor and capacitor bank switching, in secondary distribution substations for supplying lines, transformers and ring networks, can be combined with DIN standard fuses for transformer protection
The operation mechanism is typically of the charged spring type, where the energy needed for closing or opening operation is manually charged into the spring. The closing or opening sequence is initiated using local mechanical control. The unit can be equipped with electrical trip shunt coil, enabling a remote opening control of the main switch.
4. Disconnectors
Disconnectors are mechanical switching devices which provide an isolating distance and a visual separation gap in the open position. They are capable to open or close a circuit if both the negligible current is switched and there is no significant difference in the voltage between the terminals of the poles.
Currents of negligible quantity have values ≤ 0.5 A. Examples are capacitive charging currents for bushing, busbars and connections, very short lengths of cable and currents of voltage transformers. Disconnectors can carry rated currents under operating conditions continuously and under abnormal conditions, such as short circuit, based on their rated short circuit withstanding capability.
Since the disconnectors are not designed to break or make current, they have to be interlocked with primary switching equipment, like circuit breakers, that are capable of making or breaking current. The interlocking can be realized with electrical or mechanical interlocking, or a combination of both.
Earlier, a common practice was to employ overall substation-wide mechanical interlocking schemes, like a system called “castle-key” interlocking. Today, a common practice is to use overall electrical interlocking schemes, supported by mechanical interlocking between the switching equipment mounted on the same physical construction.
Medium-voltage indoor knife contact disconnector
Figure 6 – Medium-voltage indoor knife contact disconnector
The classic design is the knife contact (single-break) disconnector, as shown in the following figure. Other designs intended mainly for outdoor use exist, like double break, single-center break and pantograph. In medium-voltage indoor switchgear installations, the need for separate disconnectors has become less common with the increasing use of withdrawable circuit breakers and switch disconnectors.
With gas insulated switchgears (GIS) and outdoor installations, the disconnector is still a very common component.
Disconnectors can be actuated manually and, in remotely operated installations, by motor or compressed-air drives.
Earthing switches are used for earthing and short-circuiting de-energized station components. Earthing switches can at their rated short circuit withstand currents under abnormal conditions, such as a short circuit, but they are not required to carry continuous load currents.
The earthing switch can be also equipped with spring-charged closing device, making it capable of making fault currents, like in a case where the earthing switch is closed against an energized feeder.
In general, earthing switches are combined with the adjacent disconnectors or switch disconnectors to form one unit. However, earthing switches can also be installed separately.
On the left a center single-break outdoor 66 kV disconnector with earthing switch and on the right a double-break outdoor 66 kV disconnector with earthing switch.
Figure 7 – On the left a center single-break outdoor 66 kV disconnector with earthing switch and on the right a double-break outdoor 66 kV disconnector with earthing switch.
  1. Rotating base
  2. Frame
  3. Post insulation
  4. Rotating head
  5. Contact arm
  6. High voltage terminal
  7. Mechanism
  8. Earthing switch
Reference // Distribution Automation Handbook by ABB
  1. David Renshaw
    May 23, 2017
    Edvard, t:hanks for an interesting article. The text might br improved at one point: one line of the section on earthing switches reads “Earthing switches can at their rated short circuit current…” It might be better to say “Earthing switches can survive their rated short circuit current…” (In practice, if an earthing switch has to do this, it’s probably an operator error & we shouldn’t be surprised if the switch needs replacing afterwards.)