Home / Technical Articles / PLC application for reduced voltage-start motor control
Reduced-voltage-start motor control circuit
Figure 1 shown below illustrates the control circuit and wiring diagram of a 65% tapped, autotransformer, reduced-voltage-start motor control circuit. This reduced voltage start minimizes the inrush current at the start of the motor (locked rotor current) to 42% of that at full speed.
PLC application for reduced voltage-start motor control (photo credit: dmaeuropa.com)
In this example, the timer must be set to 5.3 seconds. Also, the instantaneous contacts from the timer in lines 2 and 3 must be trapped.
(a) Hardwired relay circuit and (b) wiring diagram of a reduced-voltage-start motor
Figure 1 – (a) Hardwired relay circuit and (b) wiring diagram of a reduced-voltage-start motor
Hardwired circuit (real I/O)
Figure 2 illustrates the hardwired circuit with the real inputs and outputs circled. The devices that are not circled are implemented inside the PLC through the programming of internal instructions.
Real inputs and outputs to the PLC
Figure 2 – Real inputs and outputs to the PLC
Tables 1, 2, and 3 show the I/O assignment, internal assignment, and register assignment, respectively.
Figure 3 illustrates the PLC implementation of the reduced-voltage start circuit. The first line of the PLC program traps the timer with internal output 1000. Contacts from this internal replace the instantaneous timer contacts specified in the hardwired control circuit. This PLC circuit implementation does not provide low-voltage protection, since the interlocking does not use the physical inputs of M1, S1, and S2.
Table 1 – I/O address assignment
I/O Address
Module TypeRackGroupTerminalDescription
 Input000 Stop PB (NC)
001 Stop PB (NO)
 Output030 Motor Starter M1
031 S1
032 S2
Table 2 – Internal address assignment
DeviceInternalDecription
 —1000 Trap Timer Circuit
 Timer1001 Timer
Table 3 – Register assignment
RegisterDecription
 4000 Preset register value 53, time base 0.1 sec. for 5.3 sec. (timer output is 1001)
 4001 Accumulated register for timer output 1001
PLC implementation of the circuit in Figure 1
Figure 3 – PLC implementation of the circuit in Figure 1
If low-voltage protection is required, then the starter’s auxiliary contacts or the overload contacts can be programmed.
If the auxiliary contacts or the overloads are used as inputs, they must be programmed as normally open (closed when the overloads are closed and the motor is running) and placed in series with contact 1000 in line 3 of the PLC program. If the overloads open, the circuit will lose continuity and M1 will turn OFF.
Resource: Introduction-to-PLC-Programming – www.globalautomation.info
  1. Vince T
    Dec 20, 2014
    TR1 is a timer relay.
  2. biswajit dey
    Dec 08, 2014
    You’ve mentioned that,at the time of PLC programming, one should consider OL as NO contact. I think it should be “examine if open” (XIO) or NC contact. If not,how could you start the motor without energising the OL !
  3. paul deelen
    Jun 04, 2014
    The picture is a horror, it is real bad practice and the comments are given in plcs.net for long time.
    the timer should be set to the needed time to have the motor running at normal speed.
    this can be from 2 to 30 seconds.
    hardware circuit is correct
    i/o address assignment line 2 should be start button
    in program the O/L should be detected, when resetted the motor will have full power as M1 is still active thus the coil M1 (please use different names internal and external) will be activated.
    greetings [email protected]
Leave a Reply to paul deelen
  ×  two  =  14
