Power flow in radial network
Symmetrical load
In three phase system the load for each phase should be the same. We call symmetrical load when the load of each phase is equal.
In symmetrical circuit each phase has same configuration, so in drawing we can represent only one phase and omit 2 other phases. The diagram that shows only one line is called single line diagram.
The load of different types has different representations. In the power system the best presentation is power load S = (P, Q).
The point to where the load is connected is called node. Ordinary this is may be a feeder, a derivation of MV network, a transformer post. The tension at this point we call node voltage.
Electrical scheme, single diagram
Suppose the loads are symmetrical. So for phase A the scheme is the same as for phase B or phase C. To show one phase is sufficient.
At the beginning node of a branch:
- Node voltage by U1,
- Active power flow from the beginning by P’ and
- Reactive power flow by Q’
At the end node of a branch:
- Node voltage by U2,
- Active power flow to the end node by P” and
- Reactive power flow by Q”
Voltage drop has 2 components, a longitudinal and a transversal component.
- DU2 = (P” r + Q”x)/U2 (longitudinal)
- dU2 = (P” x – Q” r)/U2 (transversal)
- DU1 = (P’ r + Q’ x)/U1
- dU1 = (P’ x – Q’ x)/U1
In general when the power factor is about 0.8 the transversal component of voltage drop is small compare to the longitudinal one. dU2 can be drop out in calculation.
Node voltage:
U1 = √((U2 + DU2)2 + dU22)
U2 =√((U1-DU1)2 + dU12)
In normal case, when power factor is greater than 0.8:
U1 ≈ U2 + DU2
U2 ≈ U1 – DU1
Voltage loss:
DU = U1 – U2
Power loss:
DP = ( P”2 + Q”2) r/U22 DQ = (P”2 + Q”2) x/U22
DP = ( P’2 + Q’2) r/U12 DQ = (P’2 + Q’2) x/U12
Principles of calculation (an example)
Beginning | Ending | Branch | Comment |
A | B | AB | |
B | C | BC | |
C | D | CD | |
D | E | DE | E is last node |
B | F | BF | F is last node |
D | G | DG | |
G | H | GH | H is last node |
To find out the path from the first node to last node:
- Write down branch of last node, ex: DE
- Get the previous node to the node D: C so we have CDE
- Repeat this process until the first node
BCDE
ABCDE
For the last node F: ABF
For the last node H: ABCDGH
Compute a radial network (approximately):
- Find the path to each last node
- Compute the power flow for each branch
- From the first to the last node compute all node voltage, voltage drop in each branch and power loss.
Example of radial network calculation
1. The path is {0, 1, 2}
2. From node 2 the power flows are:
P12 = P2 + 0 = P2 = 1 MW
Q12 = Q2 + 0 = Q2 = 0.6 MVar
From node 1 the power flows are:
P01 = P1 + P12 = 0.8 + 1 = 1.8 MW
Q01 = Q1 + Q12 = 0.3 + 0.6 = 0.9 MVar
3. Compute voltage drop and power loss:
From node 0 to 1 (branch { 0, 1})
DU1(01) = (P01.r01 + Q01.x01)/U0 = (1.8 x 1+0.9 x 1)/22 = 0.123 kV
U1 = U0 – DU1 = 21.877 kV
From node 1 to node 2 (branch {1, 2})
DU1(12) = (P12.r12+Q12.x12)/U1 = (1 x 1.5 + 0.6 x 1)/21.877 = 0.096 kV
U2 = U1 – DU1(12) = 21.877 – 0.096 = 21.781 kV
Reference // Handbook for installation of medium voltage lines by Mr. Ky Chanthan, Mr. Theng Marith
Thank You very much for sharing such valuable information
You’re welcome Shandukani.
Thanks for sharing such a wonderful issue. It is likely to be forgoten with time.
Glad you find it usefull!
Hi Mr. Edvart
I need a design program for 20kV overhead transmission lines. May you help me?
Best Regards
Alfred
i can give the design of 20 kv line , provided you need to give info about location and load Etc.