Power Factor Correction
Formulas
If an inductive load with an active power demand P has an uncorrected power factor of cosf1 lagging, and is required to have a corrected power factor of cosf2 lagging, the uncorrected and corrected reactive power demands, Q1 and Q2, are:
Q1 = P tanf1
Q2 = P tanf2
where tanfn = (1 / cos2fn – 1)½
The leading (capacitive) reactive power demand QC which must be connected across the load is:
QC = Q1 – Q2 = P (tanf1 – tanf2)
The uncorrected and corrected apparent power demands, S1 and S2, are related by:
S1cosf1 = P = S2cosf2
Comparing corrected and uncorrected load currents and apparent power demands:
I2 / I1 = S2 / S1 = cosf1 / cosf2
If the load is required to have a corrected power factor of unity, Q2 is zero and:
QC = Q1 = P tanf1
I2 / I1 = S2 / S1 = cosf1 = P / S1
Shunt Capacitors
For star-connected shunt capacitors each of capacitance Cstar on a three phase system of line voltage Vline and frequency f, the leading reactive power demand QCstar and the leading reactive line current Iline are:
QCstar = Vline2 / XCstar = 2pfCstarVline2
Iline = QCstar / Ö3Vline = Vline / Ö3XCstar
Cstar = QCstar / 2pfVline2
For delta-connected shunt capacitors each of capacitance Cdelta on a three phase system of line voltage Vline and frequency f, the leading reactive power demand QCdelta and the leading reactive line current Iline are:
QCdelta = 3Vline2 / XCdelta = 6pfCdeltaVline2
Iline = QCdelta / Ö3Vline = Ö3Vline / XCdelta
Cdelta = QCdelta / 6pfVline2
Note that for the same leading reactive power QC:
XCdelta = 3XCstar
Cdelta = Cstar / 3
Series Capacitors
For series line capacitors each of capacitance Cseries carrying line current Iline on a three phase system of frequency f, the voltage drop Vdrop across each line capacitor and the total leading reactive power demand QCseries of the set of three line capacitors are:
Vdrop = IlineXCseries = Iline / 2pfCseries
QCseries = 3Vdrop2 / XCseries = 3VdropIline = 3Iline2XCseries = 3Iline2 / 2pfCseries
Cseries = 3Iline2 / 2pfQCseries
Note that the apparent power rating Srating of the set of three series line capacitors is based on the line voltage Vline and not the voltage drop Vdrop:
Srating = Ö3VlineIline
NOTATION
The symbol font is used for some notation and formulae. If the Greek symbols for alpha beta delta do not appear here [ a b d ] the symbol font needs to be installed for correct display of notation and formulae.
B
C
E
f
G
h
I
j
L
P
Q
susceptance
capacitance
voltage source
frequency
conductance
h-operator
current
j-operator
inductance
active power
reactive power
[siemens, S]
[farads, F]
[volts, V]
[hertz, Hz]
[siemens, S]
[1Ð120°]
[amps, A]
[1Ð90°]
[henrys, H]
[watts, W]
[VAreactive, VArs]
Q
R
S
t
V
W
X
Y
Z
f
w
quality factor
resistance
apparent power
time
voltage drop
energy
reactance
admittance
impedance
phase angle
angular frequency
[number]
[ohms, W]
[volt-amps, VA]
[seconds, s]
[volts, V]
[joules, J]
[ohms, W]
[siemens, S]
[ohms, W]
[degrees, °]
[rad/sec]
Don't miss anything!
Powered by MailChimp
  1. ahmad
    Jan 31, 2011
    we have a 420 kva transformer and the load is about 380kva help me to find the best capasitor bank
    for this specification
    thank
Leave a reply!
Engineering Trainings
Top EEP’s Technical Writers
Technical Categories
Power Watts Calculator
Calculation of Power with DC current The power P in watts (W) is equal to the current I in amps...
Temperature Rise
Formulas The resistance of copper and aluminium windings increases with temperature, and the relationship is quite linear over the normal...
Vacuum switching
Physical phenomena This “Cahier Technique” constitutes a general presentation of basic notions relative to the functioning and use of vacuum...
Close