General description of site test procedure
Site test procedure covers all necessary electrical testing for the 110 kV cable and accessories to be carried out during and after installation of the cable system. This procedure is in line with the requirements of the contract suitable for 110 kV, XLPE cables and accessories and the tests are in accordance with TCSP-104.08, IEC 229, IEC 540 and IEC 840.
Test On 110kV Power Cable After Installation – Part 1 (on photo: Kyoritsu 4102A digital earth resistance tester)
110 kV, 115 kV and 132 kV XLPE Cables
(Standard Reference is IEC 60840 and relevant SEC Transmission Specifications 11-TMSS-02, Rev. 0 and TCS-P-104.02, TCS-P-104.03, TCS-P-104.06 and TCS-P-104.08)
1. Mechanical Check and visual Inspection
ITEMDescriptionRemark
1Inspection for physical damage or defects
2Check tightness of all bolted connections (torque wrench method)
3Check for proper cable bolted connections
4Check cable bends to ensure that bending radius is equal to or greater than the minimum bending radius specified
5Check for proper cable support, clamping, trays arrangements
6Link box tightness check
7Verify that shields are terminated as specified (through link box or directly grounded)
8Verify the exact route length as per approved drawings from terminations to terminations
9Check that all grounding points are securely connected to ground grid as specified
10Check that phases are identified and color coded
11Single core cable connected between power transformer and switchgear shall be single point earthed as switchgear side and at floating side SVL (sheath voltage limiter) should be installed
12Check single point or both ends, via voltage limiter as per approved design
13Inspection of label inside link boxes and water proofing
14Check cable entry path trench as ducts are properly sealed
15Check irregularities of outer jacket formed by non-uniform shield wire distribution
16Check/inspect the transposition of cable phases
17Check the cable outer jacket for any physical damage during and after installation
18Check for the cross connection of cable metallic sheath in cross bonding system
19Check the rubber seal in cable clamps to avoid any damage to cable outer jacket
20Check the insulating shrouds are installed at the base of the cable terminations
21For accessories (sealing terminations, instrument panels and link boxes) check the following:
a. Name plates installed and data is correct
b. Danger signs
c. Bolt tightness check and paint work conditions
2. Electrical Test
(Standards Reference is IEC 60840, and relevant SEC Transmission specifications 11-TMSS-02, TCS-P-104.08).
1Check Phasing for Conductor and sheath bonding
2Sheath DC high voltage test (10 kV DC for 1 min.) and 5 kV DC insulation test before and after high voltage/24 hour soaking test
3Conductor resistance, capacitance and inductance measurement test
4Conductor insulation resistance test
5Cross-bonding verification testThe sheath current should be <3% the current due to induction neighboring circuits should be considered and limit should be 3%+current due to external circuits
6Zero and positive sequence impedance measurement
7SVL (Sheath/Surge voltage Limiter) test by 2.5 kV DC insulation tester
8Measure the ground resistance at all link box positions as per SEC standards TES-P-104.08)
9Contact resistance test on link boxes (less than 20 μΩ)
10Metallic sheath continuity test
11Cable profile test- during jointing
12In case of Double Circuit (110 kV and above), check the separate grounding pit
13AC High voltage test for all new cables, but if old portion are involved then soaking for 24 hours at rated voltage
1. Phase indication test
After complete installation, the cables are to be identified with respect to their phases and are to be reconfirmed whether they are correctly marked or not.
Phase Identification Test diagram
Equipment / Instruments Used
Battery operated KYORITSU, High Voltage Insulation Resistance Tester, and MODEL-3125
Kyoritsu 4105A - Digital Earth resistance tester
Kyoritsu 4105A – Digital Earth resistance tester
Instructions
  1. The screens of all cables at one end are to be shorted and grounded.
  2. The conductor of the cable under test is to be connected to the negative pole of the meter.
  3. The positive pole of the meter is to be grounded.
  4. Through a switch ground the other end of this conductor of the cable under test and measure the resistance.
  5. If the resistance becomes zero, the phase identification is ok and checks whether the correct color coding is applied or not.
  6. To cross check, open the switch, the meter shall read high resistance (Tending to infinity).
  7. Similarly repeat the test for other phases and verify the correctness of color coding.
2. DC Conductor Resistance Measurement
The DC resistance of conductors of the cables, to be measured at ambient temperature before conducting any other test, and the values are to be computed for 20ºC.
Schematic layout for measurement of DC resistance for long cable
Reference
  • IEC 60228 – Conductors of insulated cables
Equipment / Instruments used
  1. Any wheatson bridge, micro Ohm-Meter.
  2. Any industrial type thermometer to measure the ambient temperature.
Instructions
  1. The conductors are short circuited at the far end by minimum 95 mm2 cable.
  2. The other ends of the cable are connected to the bridge according to equipment instructions.
  3. Note down the measured value.
  4. The resistance of conductor at 20ºC/km is obtained by substituting the measured value in the formula.
Formula for Temperature Correction:
For Copper R20 = R/L (1 + 0.00393*(T-20)) Ω/KM
Where,
  • R20 – Conductor resistance at 20ºC *(ohm/km
  • R – Measured resistance of one phase (ohm)
  • L – Exact length (km)
  • 0.00393 – Temperature coefficient at 20ºC for copper (K)
  • T – Temperature of conductor when measured in ºC
3. Capacitance Test
The capacitance shall be measured between conductor and metallic screen. According to IEC, the measured value shall not sxceed the normal value specified by the manufacturer by more than 8%.
Schematic layout for capacitance measurement
Reference
  • IEC 60840 – Applies to cable voltage ratings between 30 kV and 150 kV. It includes a regular type test sequence for cables and a separate sequence for the cable accessories.
Any RLC bridge capable of measuring capacitance up to 0.01 micro-farad (μF)
Omicron - for zero positive sequence test and capacitance measurements
Omicron – for zero positive sequence test and capacitance measurements
Instructions
  • Connections are made as per below schematic.
  • Connect the instrument cable between conductors and metallic screen and take the measurements.
  • The capacitance is measured between each individual conductor and sheath. A capacitance bridge is used for this measurement.
  • The value obtained can be converted to μF/km
Formula for Capacitance:
C = Cm/L (μF/km)
  • C – Capacitance in μF/k
  • Cm – Measured Capacitance in μF
  • L – Length of Cable in km.
To be continued soon…
Zafar Iqbal - Author at EEP-Electrical Engineering Portal
Zafar Iqbal
Electrical engineer with more then 5 year experience in Electrical Transmission and Distribution Field. Highly specialized for design, installation and testing of HV/MV T&D lines and Power Substations.
Profile: Zafar Iqbal
29 Comments
  1. Dyaa matar
    Aug 25, 2021
    Which mode should be selected for capacitance and dissipation factor test
  2. augustine ennin
    Jul 30, 2021
    pls is the standard also for overhead lines
  3. Mohamed Mahdi
    Oct 22, 2018
    Dear Eng. Zafar
    I really thank you for providing us with these information of HV cables site tests and we have learnt from them well.
    we are waiting to learn more from you in the field of electrical power transmission
    thank you
  4. shaik sulthan
    Apr 02, 2018
    Dear Eng.Zafar,
    You are really doing a good job by providing necessary information regarding field testing of power cable.I would like to suggest, please mention the specific standard of each testing, clear connection drawing of testing and achievable values of testing.it would be even better if you please provide this information.
    Anyhow, the overall article was so good and keep up the good work.
    Best of luck for the rest of your life.
  5. Hadi Salih
    Jan 14, 2018
    Dear Sirs,
    what differ between shield and screen in medium voltage armored cable where I need to do test between continuity test between shield and screen.
    Thank you,
    Hadi
  6. Ahmed Zubair
    Jul 16, 2015
    Nice work ! keep it up .. Why there is earth tester in the picture instead of HV insulation tester ? (3124 ….)
  7. a k jawahire
    Mar 18, 2015
    Why earthing one end only for single core cable
    • Nadhim
      Apr 25, 2015
      That is to avoid making the cable screen (Grounding) a part of the Grounding system of the Network (or Substation), if not then a huge earth fault will be induced in it and may damage the cable (because it is not made for this purpose).
  8. SATHYA
    Mar 10, 2015
    Dear sir, we need a instrument which can identify the presence of under ground power lines as we are in the task of digging on road sides for construction without disturbing the utilities. Kindly give your suggestions
  9. EMAMOMO Justin O.
    Feb 24, 2015
    I am indeed grateful on how this EEP have educated me on electrical repairs,maintenance and installation. Thanks.
    I dearly need a hard copies of this EEP as concerns all treated topics.
    Warm regards,
    Emamomo Justin ( Nigerian)
  10. syed zuber ahmed
    Feb 02, 2015
    zafar saab good article for testing
  11. JALEES DIVKER
    Jan 22, 2015
    Zafer sahab good article, BUT not good to copy and paste SEC standard
    • zafar
      Jan 22, 2015
      thank you jalees sahab, please go through the whole article. its not copy-paste. i take the references of SEC standards and i mentioned this in it.
  12. Derin Adeyi
    Jan 11, 2015
    Thanks for the article, I used it as a guide to develop my write up about cable testing. But notheless, I would require you to give me some standards for cable testing in a tabular format, equipment used and the expectations (result).
  13. Farid Mominzadah
    Jan 09, 2015
    How test instsllrd ACSR CONDUCTOR?
  14. Zia Uddin Ahmed
    Jan 06, 2015
    I am working in Power house in operation + maintenance it is very interesting and informative .You are doing good for others and new comer.
  15. Suhas Buddhisagar
    Jan 05, 2015
    R/s :
    Yes , I am a Electrical Engineer , I often read and download various articles , I did graducation in 78 , now retired , a layman in this field , feel you are doing a great service , happy new year , god bless you.
    • zafar
      Jan 06, 2015
      thank you for you appreciation sir, and happy new year to you too
  16. Abdullah Khan
    Dec 24, 2014
    I’ve a question regarding DC Conductor Resistance.
    I did this test many times for 1200 sqr.mm cable of 132kV and 115kV network in Saudi Arabia.
    But the connection was different.
    I shorted R-Y, R-B to calculated DC Resistance of R-Phase. Similarly, B-Y, B-R and Y-R, Y-B for Blue and Yellow Phases respectively.
    Now here you have shorted all 3-phases together. This does alter the test results ???
    • zafar
      Jan 06, 2015
      dear Abdullah, yes you are right we generally measure DC resistance at the time we measure the insulation resistance, both need shorting like you said. but if you are going to measure only DC resistance, you can do by this way. it does not alter the results and it is less time taking, no need to short again and again from other side.
  17. topp hero
    Dec 24, 2014
    Good content for me. I follow this web to reference on my job. Thanks a lot.
  18. Vishnu
    Dec 24, 2014
    Thank u for this information,
    If you don’t mind, why dont you provide videos for individual test. It will be more helpfull for us. Please give us some video references.
    • zafar
      Jan 06, 2015
      Working on it.
  19. mark.mccloy
    Dec 23, 2014
    Will you be covering diagnostics and associated baseline measurements and trending recommendations?
    • zafar
      Jan 06, 2015
      no sir, it is not covering diagnostics and recommendations but limitations of results are provided, based on the result you can diagnose.
  20. arif
    Dec 23, 2014
    pls upload video tutorial bcoz there iis not much tutorial about electrical engineering…
    and i am interested to learn about it.
  21. WALDYR SILVA
    Dec 22, 2014
    Please send me all info about testing measurement !!
  22. Motlatjo Kgare
    Dec 22, 2014
    This is very usefull and informative.
    • zafar
      Jan 06, 2015
      thank you