Home / Technical Articles / Protection / 8 typical transformer protection schemes with correctly selected relays
Protection schemes and relays selection
This article shows application hints for typical transformer protection schemes where SIPROTEC 4 relays are used.
Let’s see the most typical transformer applications and their protection schemes:
  1. Small transformer infeed
  2. Large or important transformer infeed
  3. Dual infeed with single transformer
  4. Parallel incoming transformer feeders
  5. Parallel incoming transformer feeders with bus tie
  6. Three-winding transformer
  7. Autotransformer
  8. Large autotransformer bank
Earth faults on the secondary side are detected by current relay 51N. However, it has to be time-graded against downstream feeder protection relays.
The restricted earth-fault relay 87N can optionally be applied to achieve fast clearance of earth faults in the transformer secondary winding. Relay 7VH60 is of the high-impedance type and requires class × CTs with equal transformation ratios.
Primary circuit-breaker and relay may be replaced by fuses.
Small transformer infeed protection scheme
Figure 1 – Small transformer infeed protection scheme
Go back to contents ↑
Relay 7UT612 provides numerical ratio and vector group adaptation. Matching transformers as used with traditional relays are therefore no longer applicable.
Notes //
  1. If an independent high-impedance-type earth-fault function is required, the 7VH60 earth-fault relay can be used instead of the 87N inside the 7UT612. However, class × CT cores would also be necessary in this case (see small transformer protection).
  2. 51 and 51N may be provided in a separate 7SJ60 if required.
Large or important transformer infeed protection scheme
Figure 2 – Large or important transformer infeed protection scheme
Line CTs are to be connected to separate stabilizing inputs of the differential relay 87T in order to ensure stability in the event of line through-fault currents. Relay 7UT613 provides numerical ratio and vector group adaptation.
Matching transformers, as used with traditional relays, are therefore no longer applicable!
Dual infeed with single transformer protection scheme
Figure 3 – Dual infeed with single transformer protection scheme
The directional functions 67 and 67N do not apply for cases where the transformers are equipped with the transformer differential relays 87T.
Parallel incoming transformer feeders protection scheme
Figure 4 – Parallel incoming transformer feeders protection scheme
Overcurrent relay 51, 51N each connected as a partial differential scheme. This provides simple and fast busbar protection and saves one time-grading step.
Parallel incoming transformer feeders with bus tie protection scheme
Figure 5 – Parallel incoming transformer feeders with bus tie protection scheme
The zero-sequence current must be blocked before entering the differential relay with a delta winding in the CT connection on the transformer side with earthed star-point. This is to avoid false operation during external earth faults (numerical relays provide this function by calculation).
About 30 % sensitivity, however, is then lost in the event of internal faults. Optionally, the zero-sequence current can be regained by introducing the winding neutral current in the differential relay (87T). Relay type 7UT613 provides two current inputs for this purpose. By using this feature, the earth-fault sensitivity can be upgraded again to its original value.
Restricted earth-fault protection (87T) is optional. It provides backup protection for earth faults and increased earth-fault sensitivity (about 10 % IN, compared to about 20 to 30 % IN of the transformer differential relay). Separate class × CT- cores with equal transmission ratio are also required for this protection.
High impedance and overcurrent in one 7SJ61.
Three-winding transformer protection scheme
Figure 6 – Three-winding transformer protection scheme
General notes //
In this example, the transformer feeds two different distribution systems with cogeneration. Restraining differential relay inputs are therefore provided at each transformer side.
If both distribution systems only consume load and no through-feed is possible from one MV system to the other, parallel connection of the CTs of the two MV transformer windings is admissible, which allows the use of a two-winding differential relay (7UT612).
7. Autotransformer
87N high-impedance protection requires special class × current transformer cores with equal transformation ratios.
The 7SJ60 relay can alternatively be connected in series with the 7UT613 relay to save this CT core.
General note //
Two different protection schemes are provided: 87T is chosen as the low-impedance three-winding version (7UT613). 87N is a 1-phase high-impedance relay (7VH60) connected as restricted earth-fault protection.
In this example, it is assumed that the phase ends of the transformer winding are not accessible on the neutral side, that is, there exists a CT only in the neutral earthing connection.
Autotransformer protection scheme
Figure 7 – Autotransformer protection scheme
The transformer bank is connected in a breaker-and-a-half arrangement. Duplicated differential protection is proposed:
  • Main 1: Low-impedance differential protection 87TL (7UT613) connected to the transformer bushing CTs.
  • Main 2: High-impedance differential overall protection 87TL (7VH60). Separate class × cores and equal CT ratios are required for this type of protection.
Backup protection is provided by distance protection relay (7SA52 and 7SA6), each “looking” with an instantaneous first zone about 80 % into the transformer and with a time-delayed zone beyond the transformer. The tertiary winding is assumed to feed a small station supply system with isolated neutral.
Large autotransformer bank protection scheme
Figure 8 – Large autotransformer bank protection scheme
Reference // Protection, Substation Automation, Power Quality and Measurement by Siemens