Understanding motor’s nameplate

Motor nameplate is normally located on all produced electric motors. Understanding motor nameplate details can be hard sometimes, but is essential. In most countries it is a requirement for manufacturers to display all information on the motor’s nameplate, but often this is not the case.

19 Essential Information Found On Motor’s Nameplate
19 Essential Information Found On Motor’s Nameplate (on photo: Baldor Reliancer motor; credit: rickmcneely.com)

However, when a motor has been in operation for a long time, it is often not possible to determine its operating information because nameplates of motors are often lost or painted over.

  1. Rated Voltage
  2. Rated Frequency
  3. Phase
  4. Rated Current
  5. Type
  6. Power factor
  7. kW or Horsepower
  8. Full-load speed
  9. Efficiency
  10. Duty
  11. Insulation class
  12. Maximum ambient temperature
  13. Altitude
  14. Enclosure
  15. Frame
  16. Bearings
  17. NEMA: Letter code
  18. NEMA: Design letter
  19. NEMA: Service factor

Motor name plate details

1. Rated Voltage

This data tells you at which voltage the motor is made to operate. Nameplate-defined parameters for the motor such as power factor, efficiency, torque and current are at rated voltage and frequency. When the motor is used at other voltages than the voltage indicated on the nameplate, its performance will be affected.

Figure 1 – Voltage on motor nameplate

Voltage on motor nameplate
Figure 1 – Voltage on motor nameplate

1.1 Multiple Rated Voltage

Motors usually come with enough terminals to provide alternate connections. This indicates that they can function at a minimum of two different voltages. The primary categories of alternative terminal connections are:

1.1.1 Series-Parallel Motor Connection

The winding of each phase is partitioned into two equal segments. Please keep in mind that this kind of connection is always possible because the number of poles is always a multiple of two.

  1. Connecting the two halves in series will result in each half receiving a voltage equal to half of the motor’s rated phase voltage.
  2. By connecting the two halves (of phase winding) in parallel, the motor can receive a voltage equivalent to one half of the prior voltage, without changing the voltage applied to each coil. Consult the examples illustrated in Figures 2 and 3.

Figure 2 – Series-parallel connection Y

Series-parallel connection Y
Figure 2 – Series-parallel connection Y

This connection requires nine motor terminals. The most typical dual voltage system is 220/440 V, which means that the motor is connected in parallel when supplied with 220 V and in series when supplied with 440 V.

Figures 2 and 3 illustrate typical terminal numbering, as well as connection schematics for this type of motor, which can be star or delta linked. The same schematics apply to any other two voltages, as long as one is double the other, for as 230/460 V.

Figure 3 – Series-parallel connection Δ

Series-parallel connection Δ
Figure 3 – Series-parallel connection Δ
1.1.2 Star-Delta Motor Connection

Two ends of each phase winding are connected to terminals. By connecting the three phases in delta, each phase receives the total line voltage, which is typically 220 volts (see Figure 4). Connecting the three-phases in star allows the motor to be supplied by line voltage of 220 × √3 = 380 V.

The winding voltage remains at 220 volts per phase.

Figure 4 – Star-delta connection Y – Δ

Star-delta connection Y - Δ
Figure 4 – Star-delta connection Y – Δ

This connection requires six terminals on the motor and is suitable for any dual voltage, provided that the second voltage is equal to the first voltage multiplied by √3.

Example: 220/380 V – 380/660 V – 440/760 V

In the example 440/760 V, the stated higher voltage indicates that the motor can be powered by a star-delta switch.

1.1.3 Triple-Rated Voltage

The two previous alternate connection arrangements can be achieved in a single motor by dividing the windings of each phase into two halves, allowing for series-parallel connections. All terminals must be accessible in order to connect the three phases in a star or delta configuration.

This means that there can be four options for rated voltage.

  1. Prallel-delta connection;
  2. Star-parallel connection, being the rated voltage equal to √3 × the first one;
  3. Series-delta connection, i. e. the rated voltage being twice the value of the first one;
  4. Series-star connection, the rated voltage is equal to √3 × the third one. However as this voltage would be higher the 690 V, it is only indicated as reference for star-delta connection.

Example: 220/380/440(760) V

Note: 760 V (only for starting)

This form of connection requires twelve terminals, and Figure 5 depicts the standard terminal numbering as well as the connection diagram for the three rated voltages.

Figure 5 – Connection diagram for the three rated voltages

Connection diagram for the three rated voltages
Figure 5 – Connection diagram for the three rated voltages

2. Rated Frequency

Usually for motors, the input frequency is 50 or 60 Hz. If more than one frequency is marked on the nameplate, then other parameters that will differ at different input frequencies have to be indicated on the nameplate as well.

Figure 6 – Frequency on motor nameplate

Frequency on motor nameplate
Figure 6 – Frequency on motor nameplate

Three-phase motors designed for 50 Hz operation can be connected to a 60 Hz network. Connecting a 50 Hz motor with the same voltage to a 60 Hz network will result in the following motor performance:

  • Same output;
  • Same rated current;
  • Starting current decreases 17%;
  • Starting torque decreases 17%;
  • Breakdown torque decreases 17%;
  • Rated speed increases 20%.

Note: Please consider the required outputs for motors that drive machines with variable torque and speed.


3. Phase

This parameter represents the number of AC power lines that supply the motor. Single-phase and three-phase are considered as the standard.

Figure 7 – Phase on nameplate

Phase on nameplate
Figure 7 – Phase on nameplate

A three-phase system is formed by associating three single-phase voltage system, U1, U2 and U3 which so the phase displacement between any two of them is 120º, which means, the “delays” of U2 relating to U1 , U3 relating to U2, relating to U3, are equal to 120º (considering a complete cycle = 360º).

The system is balanced if the three voltages have the same effective value, U1 = U2 = U3, as shown in Figure 8.

Figure 8 – Balanced three-phase system

Balanced three-phase system
Figure 8 – Balanced three-phase system

4. Rated Current

Current indicated on the nameplate corresponds to the rated power output together with voltage and frequency. Current may deviate from the nameplate amperes if the phases are unbalanced or if the voltage turns out to be lower than indicated.

Figure 9 – Rated current on nameplate

Current on nameplate
Figure 9 – Rated current on nameplate

5. Motor Type

Some manufacturers use type to define the motor as single-phase or poly-phase, single-phase or multi-speed or by type of construction. Nevertheless, there are no industry standards for type. Grundfos uses the following type designation: MG90SA2-24FF165-C2.

Figure 10 – Motor type designation

Motor type designation
Figure 10 – Motor type designation

6. Power factor

Power factor is indicated on the nameplate as either “PF” or “P .F” or cos φ . Power factor is an expression of the ratio of active power (W) to apparent power (VA) expressed as a percentage. Numerically expressed, power factor is equal to cosine of the angle of lag of the input current with respect to its voltage.

The motor’s nameplate provides you with the power factor for the motor at full-load.

Figure 11 – Power factor also known as cosFI

Power factor also known as cosFI
Figure 11 – Power factor also known as cosFI

A motor consumes not only active power, which is converted into mechanical power and heat (losses), but also reactive power required for magnetization, which does not produce work.

In Figure 12, vector P denotes active power, while vector Q indicates reactive power; their sum yields the apparent power S.

[/highlight2]Figure 12[/highlight2] – The Power factor is determined measuring the input power, the voltage and the rated load

The Power factor is determined measuring the input power, the voltage and the rated load
Figure 1.3 – The Power factor is determined measuring the input power, the voltage and the rated load

The electric motor is crucial in the world’s industry, accounting for almost 65% of energy usage. Consequently, it is imperative to utilize motors with outputs and characteristics well suited to their function, as the power factor varies with motor load.


Go back to Index ↑


Mechanical Input:

7. kW or horsepower

kW or horsepower (HP) is an expression of the motor’s mechanical output rating – that is it’s ability to deliver the torque needed for the load at rated speed.


8. Full-load speed

Full-load speed is the speed at which rated full-load torque is delivered at rated power output. Normally, the full-load speed is given in RPM. This speed is sometimes called slip-speed or actual rotor speed.

Figure 12 – Motor efficiency label; Full-load speed; Efficiency in percent and kW or horsepower

Motor efficiency label; Full-load speed; Efficiency in percent and kW or horsepower
Figure 12 – Motor efficiency label; Full-load speed; Efficiency in percent and kW or horsepower

Go back to Index ↑


Performance:

9. Efficiency

Efficiency is the motor’s output power divided by its input power multiplied by 100. Efficiency is expressed as a percentage. Efficiency is guaranteed by the manufacturer to be within a certain tolerance band, which varies depending on the design standard, eg IEC or NEMA.

Therefore, pay attention to guaranteed minimum efficiencies, when you evaluate the motor’s performance.


10. Duty

This parameter defines the length of time during which the motor can carry its nameplate rating safely. In many cases, the motor can do it continuously, which is indicated by an S1 or “Cont” on the nameplate. If nothing is indicated on the nameplate, the motor is designed for duty cycle S1.

Figure 13 – Motor duty on the nameplate

Motor duty
Figure 13 – Motor duty on the nameplate

Note: Motors designated for continuous duty must be protected against overloads by either an integrated device or an independent device, typically equipped with a thermal relay adjusted to a rated or setting current that is equal to or less than the value of the rated motor power supply current (In) and the Service Factor (SF).

How to know if you set the correct current on a motor thermal overload relay

Go back to Index ↑


Reliability

11. Insulation class

Insulation class (INSUL CLASS) is an expression of the standard classification of the thermal tolerance of the motor winding. Insulation class is a letter designation such as “B” or “F”, depending on the winding’s ability to survive a given operating temperature for a given life. The farther in the alphabet, the better the performance.

For instance, a class “F” insulation has a longer nominal life at a given operating temperature than a class “B”.

Figure 14 – Insulation class. CI.F(B) = class F with temperature rise B

Insulation class. CI.F(B) = class F with temperature rise B
Figure 14 – Insulation class. CI.F(B) = class F with temperature rise B

12. Maximum ambient temperature

The maximum ambient temperature at which a motor can operate is sometimes indicated on the nameplate. If not the maximum is 40°C for EFF2 motors and normally 60°C for EFF1 motors. The motor can run and still be within the tolerance of the insulation class at the maximum rated temperature.

Figure 15 – The power output reduction curve shows the performance reduction with increased ambient temperature or increased installation height above sea

The power output reduction curve
Figure 15 – The power output reduction curve shows the performance reduction with increased ambient temperature or increased installation height above sea

The operational temperature threshold of the motor is depending upon the type of insulating material used. In order to conform to the standards, insulation materials and systems, each comprising a combination of several components, are categorized into INSULATION CLASSES. Each is characterized by a specific temperature threshold, namely the maximum temperature that the insulation material or system can withstand continuously without compromising its ability to last.

The insulation classes for electrical machines and their corresponding temperature limitations, as per IEC 60034-1, are as follows:

  • Class A ( 105 ºC )
  • Class E ( 120 ºC )
  • Class B ( 130 ºC )
  • Class F ( 155 ºC )
  • Class H ( 180 ºC )

13. Altitude

This indication shows the maximum height above sea level at which the motor will remain within its design temperature rise, meeting all other nameplate data.

If the altitude is not indicated on the nameplate, the maximum height above sea is 1000 metres.

Go back to Index ↑


Construction

14. Enclosure

Enclosure classifies a motor as to its degree of protection from its environment and its method of cooling. Enclosure is shown as IP or ENCL on the nameplate.

Figure 16 – Motor frame, enclosure, bearing and grease information on nameplate

Motor frame, enclosure ,bearing and grease information on nameplate
Figure 16 – Motor frame, enclosure, bearing and grease information on nameplate

Enclosures for electrical equipment must provide a certain level of protection based on their installation features and maintenance accessibility. Consequently, equipment situated in an area exposed to water jets must have a housing that can withstand the impact of the jets at specified pressure and angle of incidence, without allowing water infiltration.


15. Frame

The frame size data on the nameplate is an important piece of information. It determines mounting dimensions such as the foot hole mounting pattern and the shaft height. The frame size is often a part of the type designation which can be difficult to interpret because special shaft or mounting configurations are used.

Figure 17 – The frame size data on the nameplate

The frame size data on the nameplate
Figure 17 – The frame size data on the nameplate

16. Bearings

Bearings are the component in an AC motor that requires the most maintenance. The information is usually given for both the drive-end (DE) bearing and the bearing opposite the drive-end, non drive- end (NDE).


NEMA

Besides the above mentioned information, NEMA nameplates have some supplementary information. The most important ones are:

  1. Letter code,
  2. Design letter and
  3. Service factor.

17. Letter code

A letter code defines the locked rotor current kVA on a per horsepower basis. The letter code consists of letters from A to V. The farther away from the letter code A, the higher the inrush current per horsepower.

NEMA code letterLocked rotor kVA/HPNEMA code letterLocked rotor kVA/HP 
A0 – 3.15L9.0 – 10.0
B3.15 – 3.55M10.0 – 11.2
C3.55 – 4.0N11.2 – 12.5
D4.0 – 4.5ONOT USED
E4.5 – 5.0P12.5 – 14.0
F5.0 – 5.6QNOT USED
G5.6 – 6.3R14.0 – 16.0
H6.3 – 7.1S16.0 – 18.0
INOT USEDT18.0 – 20.0
J7.1 – 8.0U20.0 – 22.4
K8.0 – 9.0V22.4 AND UP

18. Design letter

Design letter covers the characteristics of torque and current of the motor. Design letter (A, B, C or D) defines the different categories. Most motors are design A or B motors.

A design A motor torque characteristic is similar to the characteristic of a design B motor; but there is no limit in starting inrush current. With a design B motor, the motor manufacturer has to limit the inrush current on his products to make sure that users can apply their motor starting devices.

So, when replacing a motor in an application, it is important to check the design letter, because some manufacturers assign their products with letters that are not considered industry standard which may lead to starting problems.


19. Service factor

A motor designed to operate at its nameplate power rating has a service factor of 1.0. This means that the motor can operate at 100% of its rated power. Some applications require a motor that can exceed the rated power. In these cases, a motor with a service factor of 1.15 can be applied to the rated power. A 1.15 service factor motor can be operated at 15% higher than the motor’s nameplate power.

It’s good to know, that any motor that operates continuously at a service factor that exceeds 1 will have reduced life expectancy compared to operating it at its rated power.

Service factor (SF) is the factor that, when applied to rated output, represents the allowable load that can be applied to motor continuously, under specified operating conditions.

Note that this refers to continuous overload conditions, i.e., a power reserve that gives the motor a better capacity to withstand adverse operating conditions. Service factor should not be confused with momentary overload capacity during few minutes. A service factor = 1.0 means that the motor has not been designed for continuous operation above its rated output.

However, this does not change its capacity to withstand instantaneous overloads.

Suggested Course – Motor Control Schematics Course For True Engineers

Motor Control Schematics Course For True Engineers


Go back to Index ↑

References:

  • Motor book by Grundfos
  • Specification of Electric Motors by WEG

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

37 Comments


  1. Clovis
    Mar 16, 2023

    From the point of view I see this site to helpful were motors are concerned.


  2. Douglas Mackinnon
    Aug 12, 2022

    Edvard, Novice question here In regard to 3 phase motors: Is a measured RLA of around 27 amps on each line too high for a motor whose data tag list 30 amps?
    Does a technician need to take a reading or average of 3 then multiply by 1.73 and compare this to the data tag? Or should no phase be operating above 30 amps + service factor?


  3. Sean
    Mar 09, 2022

    I have an old mill and the nameplate has some info I’m not familiar with. In order it reads : H.P._ R.P.M._ FR. 254 VOLTS_ AMPS_ PH._ CYC 60. The info with number values are the two I’m unsure of. My best guess is that FR. is frequency and CYC is duty cycle? But I really don’t know :/


    • chris
      Mar 13, 2022

      Hi Sean, the FR likely refers to the frame dimensions (25/4 = 6.25″ base to shaft) and CYC probably refers to the frequency or cycles per second which will be 60Hz in North America.


    • Art
      Sep 17, 2022

      Frame and frequency


  4. Giannis
    Jun 08, 2021

    Does the voltage refer to line-to-line or line-to-neutral values?


  5. Joe King
    Mar 28, 2021

    Is the motor nameplate rated current the current in one phase leg or the sum of all three phase legs (current in one phase * 1.73)?


  6. Aniket
    Sep 12, 2020

    How to know motor is suitable for VFD operation from motor nameplate. Here in given nameplatethere is no info is mentioned about VFD operation.


  7. Callixte Kayigire
    Mar 14, 2020

    How to know the quantity grease to fill in the bearing by reading the motor nameplate


  8. Callixte Kayigire
    Mar 14, 2020

    1.What is the function of duty cycle on motor nameplate?
    2. How to know the time to regrease a motor by reading it’s nameplate?


  9. Gabriel
    Aug 26, 2019

    Good evening Sir. I have a question?How can a single phase motor can be made self starting


    • Ankit
      Feb 24, 2020

      Single phase induction motor cant be self starting because in this motor when current induce in rotor(due to emf) then rotor experience a force but it can’t not decide direction to rotate (because rotor are inner part and both upper side like stator have a same magnetic field).in that case rotor create a hum sound when we give some torque on a particular direction then the rotor rotate start that direction by an auxiliary supply when rotor start rotate then auxiliary supply automatically disconnect and motor run properly


  10. CESAR LIZCANO LOZOYA
    Jul 03, 2019

    GOOD MORNING I NEED CROSSREFERENCE

    120RU02H80X26 BALDOR RELLIANCE
    110BT02J00X26 BALDOR RELLIANCE


  11. Robery
    May 29, 2019

    How would you determine FLA with this info?


  12. Benny
    May 07, 2019

    Is it safe or even allowed to apply higher voltage than the voltage indicated on the equipment name plate? Ex. Applying 480 volt to a 208 stamped nameplate?


    • Edvard
      May 07, 2019

      Why would you do this? You could burn the windings…


      • Carl
        Dec 04, 2020

        Hi
        Love your site…
        There is a case its to do with the VF ratio
        So you connect the motor in delta …but run on the star rated voltage. Then adjust the drives VF ratio to suit.
        Its to do with delivering more torque above the nominal speed of the motor.
        …I’ve seen this and done it. …but you are now working outside of the manufactures guidelines.
        Not a commonly known trick and I’ve only seen it done twice….
        Your dealing with an inverter so you can set max current trip etc etc..if you think it will cook the motor


  13. Irfan
    Jan 22, 2019

    can we determine motor shaft size from name plate?


  14. Douglas F. Knight
    Dec 13, 2018

    I would like to praise you, and your associates! Your site provides a plethora of information. And your formatting of the subject matter; that you have made available for the public to use. Is easy to use and logically layed out.


    • Edvard
      Dec 13, 2018

      Thank you Douglas!


    • Vince segura
      May 31, 2020

      Ditto on thank you.. for providing info to public.
      I am an inventor/ innovator and often repurpose or convert or modify existing frames and designs. I respectfully request data base complication for alternate uses like universal motors which can run on DC or AC and permanent magnet motors and any unusual desigs and possible alterhet configurations etc new tech new designs and thots on them it would be a most helpful data base etc helping those if us without the resources or your type of exp and education.. in the interests of improving the world. Big companing nefa cotos etc always try to squelch any innovations that may reduce thier power control or profits/income. If I had a genie bottle wish it would be to reverse that and give them a conscious.. imagine the advancements possible if the money they put into stopping or hamstringing progress was instead spent helping .. so you could do alot with just data and pricing access to new ideas and theories. For instance RF induced hi volt low amp tech.. Tesla based won’t make big corps happy but is better technology. And I’m working in using back emf pulses to increase windmill generation of electricity .. I’m hoping up to 350% for the same size frame and rotor. Current/present designs suck ass. Old views.. well that’s my 3¢.. idea: you could do this as a tax right off giving back to community.. thsnx have a great day. I could use r&d funding too🙃 can’t hurt to ask Right!?


  15. Mohamed Elsayed
    Nov 11, 2018

    very good


  16. ahmed jalil
    Feb 10, 2018

    Thanks for the informationa


  17. Amin Nikdoust
    Nov 22, 2017

    Thank you for clear and complete information.it was so useful and help me to inspect the Siemens motors and also prepare a professional report.


  18. ronmar
    Jan 17, 2017

    Hi, My comment regarding the voltage is that how can we identify if this is applicable for wye delta controls.


  19. Ady
    Jun 19, 2016

    Hi …. Can you tell me what the letters CY stand for on a GE Motor 1/4hp AC 230v single phase motor. It has CY in red and then the number 50 stamped in black ? Thank you, Ady


  20. Steven Katopwa
    Apr 01, 2016

    Thank you Edvard for this information and I wish to learn more from you.


  21. Manuranga
    Jan 30, 2016

    Great knowledge sharing. Thanks..Good luck for future.


  22. prudhvi
    Sep 14, 2015

    Its great information about a motor thanx for ur data. I am waiting for your app in windows phone pls consider this request….
    Thanks edward


  23. sACHIn GJ
    Sep 03, 2015

    Really Amazing Informations sir …
    Very helpful …


  24. Rob Motuzas
    Aug 31, 2015

    The information contained on your site is excellent and I am very happy with the articles provided.


  25. mohammed
    Aug 29, 2015

    Very important information thanks can provide us test type can carry on motor LV and HV voltage


  26. sagar
    Aug 29, 2015

    Thanks to provide such a useful info.hopping for continuous do your best


  27. sirelkhatim
    Aug 29, 2015

    Dear sir,
    Thanks for this invaluable information which is very important for engineers dealing with electric motors.
    In item number 5 I think you mean single speed please correct if I am right.
    Also I think the model and serial numbers for a certain manufacturer is important and is shown on the nameplate also what about motor cooling and information about the cooling fan.


    • Edvard
      Aug 29, 2015

      You are welcome Sirelkhatim! Number 5 is actually internal type mark of manufacturer. Each motor manufacturer has its own labeling which is telling a lot of things about motor.

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
This whitepaper by OMICRON explores the fundamental shift in substation automation testing from hardware-dependent setups to virtualized, software-defined verification.