Save 15% on Pro Membership Plan with discount code: NTX67 (limited time offer). Study specialized LV/MV/HV technical articles and papers.
Home / Technical Articles / 4 essential qualities of electrical protection
Fundamental Protection Requirements
In generating stations, all electrical circuits and machines are subject to faults. A fault is generally caused by the breakdown of insulation between a conductor and ground or between conductors due to a variety of reasons.
4 essential qualities of electrical protection (photo credit: rbswitchgeargroup.com)
The result is a flow of excess current through a relatively low resistance resulting in severe damage unless cleared quickly. Let’s see the four main building blocks that are used to meet fundamental requirements of electrical protection:
1. Speed
When electrical faults or short circuits occur, the damage produced is largely dependent upon the time the fault persists. Therefore, it is desirable that electrical faults be interrupted as quickly as possible.
Since 1965, great strides have been made in this area. High-speed fault detecting relays can now operate in as little time as 10 milliseconds and output relaying in 2 milliseconds. The use of protection zones minimizes the requirement for time-delayed relaying.
2. Reliability
The protective system must function whenever it is called upon to operate, since the consequences of non-operation can be very severe. This is accomplished by duplicate A and B protections and duplicate power supplies.
Examples of protection relays - Micom, Ref and Siprotec
Examples of protection relays – Micom, Ref and Siprotec
3. Security
Protections must isolate only the faulted equipment, with no over-tripping of unaffected equipment. This is accomplished by the use of over-lapping protection zones.
4. Sensitivity
The protection must be able to distinguish between healthy and fault conditions, i.e., to detect, operate and initiate tripping before a fault reaches a dangerous condition.
On the other hand, the protection must not be too sensitive and operate unnecessarily.
Some loads take large inrush starting currents, which must be accommodated to prevent unnecessary tripping while still tripping for fault conditions. The ability of relaying to fulfil the sensitivity requirement is improved through the use of protection zones.
Introduction to Protection and Control (WEBINAR)
This ABB’s webinar will define power system protective relaying and its purpose. A general overview of key concepts, protective relay classifications, operating principals, operating reliability and relaying philosophy will be presented.
Also provided is a brief review of terminology, ANSI C37.2 device function numbers and IEC 61850 logical nodes (device function models).
Reference: Science and Reactor Fundamentals – Electrical CNSC Technical Training Group
  1. BALACHANDAR
    Oct 30, 2018
    This portal is very useful for all category electrical engineers. What I mean even beginners and who are now working in the power system network.
  2. Donald stven
    Dec 29, 2014
    I wonder why you didn’t mention about ADS ( Automatic disconnection of supply ). This protection includes both basic and fault. Where basic protection is provided through insulation, barriers, enclosures etc; the fault protection is provided by protective earthing, protective equipotential bonding and automatic disconnection in case of any fault. Apart from all these you need a regular maintenance of electrical systems to protect your house from any electrical hazards.
  3. Deepak Chand
    Nov 06, 2014
    Good one
  4. jeramil
    Nov 05, 2014
    dear sir,
    i would like to ask some documents with regards to designing electrical installations for industrial purposes especially standards from ieee…
    i hope you would consider my request.
    thanks and cheers.
    jeramil
Leave a Reply to BALACHANDAR
60  ⁄    =  twelve
The Electrical Digital Twin Webinar
