Home / Technical Articles / 4 ways in which noise can enter a signal cable and its control
Few words about interference…
Noise, or interference, can be defined as undesirable electrical signals, which distort or interfere with an original (or desired) signal. Noise could be transient (temporary) or constant.
4 ways in which noise can enter a signal cable and its control (photo credit: bicsi.org)
Unpredictable transient noise is caused, for example, by lightning.
Constant noise can be due to the predictable 50 or 60 Hz AC ‘hum’ from power circuits or harmonic multiples of power frequency close to the data communications cable. This unpredictability makes the design of a data communications system quite challenging.
Electrical noise occurs or is transmitted into a signal cable system in the following four ways:
  1. Galvanic (direct electrical contact)
  2. Electrostatic coupling
  3. Electromagnetic induction (in part 2)
  4. Radio frequency interference (RFI) (in part 2)
If two signal channels within a single data cable share the same signal reference conductor (common return path), the voltage drop caused by one channel’s signal in the reference conductor can appear as a noise in the other channel and will result in interference. This is called galvanic noise.
Electrostatic noise is one, which is transmitted through various capacitances present in the system such as between wires within a cable, between power and signal cables, between wires to ground or between two windings of a transformer. These capacitances present low-impedance paths when noise voltages of high frequency are present.
Thus noise can jump across apparently non- conducting paths and create a disturbance in signal/data circuits.
Electromagnetic interference (EMI) is caused when the flux lines of a strong magnetic field produced by a power conductor cut other nearby conductors and cause induced voltages to appear across them.
When signal cables are involved in the EMI process, this causes a noise in signal circuits. This is aggravated when harmonic currents are present in the system. Higher order harmonics have much higher frequencies than the normal AC wave and result in interference particularly in communication circuits.
Radio frequency interference involves coupling of noise through radio frequency interference. We will now describe these in some detail.
1. Galvanic coupling (or common impedance coupling)
For situations where two or more electrical circuits share common conductors, there can be some coupling between different circuits with deleterious effects on the connected circuits. Essentially, this means that the signal current from one circuit proceeds back along the common conductor resulting in an error voltage along the return bus, which affects all the other signals.
The error voltage is due to the capacitance, inductance and resistance in the return wire. This situation is shown in Figure 1 below.
Figure 1 - Impedance coupling
Figure 1 – Impedance coupling
Obviously, the quickest way to reduce the effects of impedance coupling is to minimize the impedance of the return wire. The best solution is to use a balanced circuit with separate returns for each individual signal shown in Figure 2.
Figure 2 - Impedance coupling eliminated with balanced circuit
Figure 2 – Impedance coupling eliminated with balanced circuit
Go back to Index ↑
2. Electrostatic or capacitive coupling
This form of coupling is proportional to the capacitance between the noise source and the signal wires. The magnitude of the interference depends on the rate of change of the noise voltage and the capacitance between the noise circuit and the signal circuit.
In Figure 3, the noise voltage is coupled into the communication signal wires through the two capacitors C1 and C2, and a noise voltage is produced across the resistances in the circuit.
The size of the noise (or error) voltage in the signal wires is proportional to the:
  • Inverse of the distance of noise voltage from each of the signal wires
  • Length (and hence impedance) of the signal wires into which the noise is induced
  • Amplitude (or strength) of the noise voltage
  • Frequency of the noise voltage.
There are four methods for reducing the noise induced by electrostatic coupling. They are:
  1. Shielding of the signal wires
  2. Separating from the source of the noise
  3. Reducing the amplitude of the noise voltage (and possibly the frequency)
  4. Twisting of the signal wires.
Figure 3 - Electrostatic coupling
Figure 3 – Electrostatic coupling
Figure 4 indicates the situation that occurs when an electrostatic shield is installed around the signal wires.
The currents generated by the noise voltages prefer to flow down the lower-impedance path of the shield rather than the signal wires. If one of the signal wires and the shield are tied to the earth at one point, which ensures that the shield and the signal wires are at an identical potential, then reduced signal current flows between the signal wires and the shield.
Figure 4 - Shield to minimize electrostatic coupling
Figure 4 – Shield to minimize electrostatic coupling
Go back to Index ↑
Notes:
The shield must be of a low-resistance material such as aluminum or copper. For a loosely braided copper shield (85% braid coverage) the screening factor is about 100 times or 20 dB that is, C3 and C4 are about 1/100 C1 or C2. For a low-resistance multi- layered screen, this screening factor can be 35 dB or 3000 times.
Twisting of the signal wires provides a slight improvement in the induced noise voltage by ensuring that C1 and C2 are closer together in value; thus ensuring that any noise voltages induced in the signal wires tend to cancel one another out.
Provision of a shield by a cable manufacturer ensures that the capacitance between the shield and the wires is equal in value (thus eliminating any noise voltages by cancellation).
Will be continued very soon… Stay in the tune ;)
Reference: Practical Grounding, Bonding, Shielding and Surge Protection – G. Vijayaraghavan, B.Eng (Hons) Consulting Engineer, Chennai, India
13 Comments
  1. Meruert
    Oct 26, 2023
    hi everybody, help me please. What’s mean noisy level? like 0-1 or 3-4-5?
  2. [email protected]
    Apr 03, 2023
    I am looking for the topic that talks about Radio Freq. Interference RFI but could not locate it. Where is the Part 2 of this article? Thank you!
  3. xaritou
    Jan 27, 2022
    Can any body help?
    2 part(conected) internal Audio Card, first part rear of PC, second in front (as interface). This interface has an input jack(for mic) powered from phantom(12volt). Every time i engage the 12volt phantom, there is a noise coming out from speakers, even there is nothing conected. This noise is included in every record i will do. It is like the 12volt goes not only into the way for the mic (condensed) to power it on, but also into the other way (the way to the speakers, and produces this noise)
    Any help, please.
  4. Natalie
    Feb 14, 2020
    I’m searching for answers to what appears to be some sort of electrical interference. Every night between midnight and 6am we can hear what sounds like am radio in our house. It isn’t coming from neighbouring properties and can only be heard in the house. Could it be related to what’s mentioned in this article? This has been happening for 3 months now and we’re becoming desperate for a solution
  5. JEELANI
    Feb 11, 2020
    Assistance needed
  6. Venkatesan
    Oct 13, 2016
    EXCELENT theoretical expalnation about noise and shielding.
  7. Chuck Bono
    Mar 30, 2016
    Great Article. Enjoyed reading this article.
  8. Chamara DTN
    Aug 01, 2015
    Great article, thanks
  9. James Archer
    Sep 15, 2014
    When RFI, EMI, analogue currents are encountered or determined a threat to your control and communications systems, some immediately think ground rods are the answer to most of these issues as a most cost effective solution. Do not let that happen to you. Good effective management of these matters calls for the best application of up to date grounding/earthing and bonding methods. One must remember that all ferrous metals that make up structural and electrical systems can and often are nothing more than huge antenea for collecting RF and electro magnetic signals that can be even amplified through these structures and electrical pipes and cabinets etc.Driving a ground rod could inadvertently set up a loop that could be worse than the initial problem. So always ensure your plant facility has a truly effective low impedence infrastructure to facilitate a direct path to your proven and tested system earthing/grounding plane. All the best.
  10. Maurice Turgeon
    Sep 12, 2014
    Great article, especially appreciate the comment about the “earthing requirement” in fig. 4 since noise is often RF in nature and earth does form half of a diapole antenna.
    Driven rods (or earthing) is often seen as a waste of time and money in the electrical industry.
    I’m looking forward to Part II
  11. Emmanuel Britto F.
    Sep 11, 2014
    Dear,
    Further to these ways and for EHV substations we use what is called the “compensation cable”.
    Consists of a copper clad cable layed inside the trench and located in the upper side of it.
    By using this cable a capacitive voltage divider is enabled to the circuit so that the induced voltage over the control cable will be mitigated.
  12. Petrus Kruger
    Sep 08, 2014
    Hi. How great of a noise will stainless steal welding employ in a live plant? When the welding occurs for example on a tank or pipeline within the plant.
    Thanks for the informative article!
    Petrus Kruger
Leave a Reply to [email protected]
  +  forty five  =  forty six
