Basic tripping settings of CB
There are (at least) six basic adjustable tripping settings (functions) you really should understand in order to fully understand how circuit breaker actually works. All these adjustable functions actually shape the time-current curve of a circuit breaker and allows proper tripping according to the network parameters and also the proper coordination between upstream and downstream devices.
6 Adjustable Tripping Settings of a Circuit Breaker You MUST Know
Note that modern circuit breakers (MCCB, ACB) mostly have an electronic tripping unit which is much more advanced comparing to these explained here, but the basics are the same, very same.
So, let’s start with explanation!
  1. Continuous Amps (Ir)
  2. Long-Time Delay
  3. Short-Time Pickup
  4. Short-Time Delay
  5. Instantaneous Pickup
  6. Ground Fault Pickup
Circuit breaker adjustable tripping functions
The below time-current curve reflects one possible setup for a 1200 ampere circuit breaker with a nominal (maximum continuous ampere) rating of 1000 amps. This time-current curve will be the basis for discussing adjustable tripping settings of the circuit breakers.
Time-current curve of a circuit breaker
Continuous Amps (Ir) varies the level of current the circuit breaker will carry without tripping. Ir is a percentage of the circuit breaker’s nominal rating (In). Continuous amps can be adjusted from 20 to 100 percent of the circuit breaker’s nominal rating.
For example, a 1000 amp breaker can be changed from 1000 amps to 800 amps by adjusting the breaker continuous amps setting to 80%.
Continuous current [Amps]
Go back to CB tripping settings ↑
2. Long-Time Delay
Long-time delay causes the breaker to wait a certain amount of time to allow temporary inrush currents, such as those encountered when starting a motor, to pass without tripping.
The adjustment is from 2.2 to 27 seconds at six times the continuous amps (Ir) setting.
As shown below, the long-time delay effects the position of an I2T slope. This means that lower levels of current will allow the breaker to remain online for longer periods of time.
Long time delay tripping settings
Short-time pickup is used for selective tripping. The short-time pickup function determines the amount of current the breaker will carry for a short period of time, allowing downstream protective devices to clear short-circuits without tripping the upstream device.
Short-time pickup is adjustable from 1.5 to 10 times the trip unit ampere setting (Ir).
For example, a 1000 ampere frame can be adjusted to trip anywhere from 1500 to 10,000 amps. The switch also has an “OFF” position to eliminate short-time pickup and short-time delay.
Short-time pickup used for selective tripping
4. Short-Time Delay
Short-time delay, used in conjunction with short-time pickup, controls the time involved in postponing a short-time pickup trip.
There are two modes: fixed time, or I2T ramp. Fixed time is adjustable from .05 to .5 seconds. The I2T ramp mode is adjustable from .18 seconds to .45 seconds, providing a short inverse time ramp.
This allows better coordination with downstream thermal-magnetic circuit breakers and fuses. A fixed instantaneous trip point of 10,000 amps trips the breaker automatically and overrides any pre-programmed instructions.
Instantaneous pickup is used to trip the circuit breaker with no intentional delay at any current between 2 and 40 times the breaker’s continuous ampere setting (Ir).
In this example instantaneous pickup has been set to 10 times the continuous amp setting, or 10,000 amps (10 x 1000) with a continuous amp setting of 1000 amps. In this case a higher setting would still trip at 10,000 amps due to a fixed instantaneous override of 10,000 amps which automatically trips the breaker regardless of the instantaneous pickup setting.
If the continuous amp setting had been 300 amps, setting the instantaneous pickup at 10 would make the instantaneous setting equal to 3000 amps, well below the fixed instantaneous override.
Instantaneous pickup - Used to trip the circuit breaker with no intentional delay at any current between 2 and 40 times the breaker’s continuous ampere setting (Ir)
Instantaneous pickup – Used to trip the circuit breaker with no intentional delay at any current between 2 and 40 times the breaker’s continuous ampere setting (Ir)
Ground fault pickup controls the amount of ground fault current that will cause the breaker to interrupt the circuit. The adjustment can be set from 20 to 70% of the maximum breaker rating. In compliance with NEC® 230-95 (A), no trip point setting exceeds 1200 amps.
The ground fault pickup is divided into three sections; .1s, .2s, and .4s. This feature adds a time delay of .1, .2, or .4 seconds to the breaker’s trip when a ground fault occurs.
Circuit breaker coordination
The ground fault pickup time delay feature is useful for circuit breaker coordination. In the following scheme, upstream breaker “A” has been set to .2s and downstream breakers “B” and “C” have been set to .1s.
A ground fault occurring in the circuit supplied by “B” will trip the “B” breaker without disturbing “A” or “C”.
Reference // STEP 2000 – Molded Case Circuit Breakers (MCCB) by SIEMENS
53 Comments
  1. Giovanni
    Jun 04, 2023
    Good explanation, clear and succinct
  2. Al Suther
    May 31, 2023
    Isn’t it generally not permissible to change the settings of a breaker since these were set based on a commissioning coordination study.
  3. Joseph Wilberforce Ansah
    Mar 28, 2023
    Electricity Section,
    University of Cape Coast
    Ghana West Africa.
  4. Rolando Blanco Guevarra
    Mar 16, 2023
    It is very useful.and served as reference about the tie breaker tripping .thanks ,really apreciate it.more power to the author
  5. WAREZ ALI
    Jun 23, 2022
    NEED TO LEARN AND DOING BUSINESS
  6. Vincent Byrne
    Feb 27, 2022
    Just starting to get into ACB is there any other advice or information your could give or point me towards
  7. tim
    Feb 09, 2022
    Great article
  8. Kalum Prasanna
    Dec 31, 2021
    Continuos current can be adjusted between 200A to 1000 A isn,t it ? Example says its 800A is that correct ?
  9. Mike
    Oct 05, 2021
    I did’nt understand why there’s setting of 6*IR in short term overload release.
  10. Mohammed Ewais
    Aug 01, 2021
    Great
  11. DILIP KUMAR DAS
    Jul 31, 2021
    Useful information for ACB / MCCB settings.
    Thanks a Lot !
  12. Indika
    Mar 09, 2021
    Great 👍👍👍🙏🙏🙏
  13. Silviu Darie
    Jan 30, 2021
    Great presentation. Congratulations
  14. juan de la cruz ravelo
    Sep 26, 2020
    Esta información es muy completa y me ayuda a tener un conocimiento de cómo ajustar los parámetros correctamente.
  15. Engr. Juliano Osngal
    Jul 21, 2020
    Thanks the topic is 200%excellent
  16. Daniel tecleab
    Feb 16, 2020
    the information provided is very helpful for practical based and theory based lessons and has been presented in precise manner, it is what i was looking for and i will expect more edvard
  17. Saleh Farman
    Dec 17, 2019
    Dear Sir,
    Does the Direct Acting Series Trip is only build on ACB or both ACB & MCCB?
  18. eng. ghassan
    Oct 23, 2019
    thank a lot for all thing you always provide.
    best regards
    Ghassan
  19. Michael
    Oct 03, 2019
    Just a quick question – what exactly does The adjustment is from 2.2 to 27 seconds “at six times the continuous amps (Ir) setting” mean, i.e. what does the @ 6,000A mean exactly?
    • Jamil Ahmed Khan
      May 31, 2020
      Yes. At 6000A or some minor+/- CB will trip at pre set time.
  20. Shridhar
    Sep 05, 2019
    Thanks very helpful information.
  21. roberto soto
    Aug 20, 2019
    This information is very complete and helps me to have a knowledge of how to adjust parameters correctly.
  22. Lay Lwin
    Jul 19, 2019
    The information is given is very useful for us. Thank you. Please also post similar technical information detail. Truly appreciate your time spending to share knowledge.
  23. Hari kusnomo
    Jul 08, 2019
    Thanks for this technical information
  24. Abdul khaliq
    Jun 06, 2019
    Very useful information, no doubt.
  25. mohamad ramezani
    Jan 15, 2019
    very thanks for detail of this document . very useful
  26. Vishal
    Jan 03, 2019
    Please explain long time delay setting calculation.
  27. SEEN BAYAS AHAMED
    Nov 28, 2018
    Trip characteristics is adjustable in mcb or not
  28. ali taheri
    Nov 17, 2018
    Thank you Edvard
  29. Thiagarajan
    Oct 20, 2018
    Hi Sir ,
    I have problem to start 3.3kv motor . The motor start trip 21 secs due Thermal Pickup
    Starting Current 1640Amps , The protection relay we use GE multilin 869 . As per Mechanical documnet the Motor Alignment everything looks ok . Please advice …..
    • Jimuel
      Jul 28, 2020
      What exactly did you mean here? Based from what I understand, the motor started to trip after 21 seconds it has started to run?
  30. Vivek
    Oct 06, 2018
    Sir
    I want to know about LBB tripping settings for 33kv VCB and 220kv SF6 breaker.
  31. NITIN BHAGWAN MHASKE
    Oct 03, 2018
    Very helpful article.Thank You for sharing
  32. OM SINGH
    Sep 30, 2018
    Hi Edvard,
    Thanks for theses technical information of CB. Theses are very helpful for me.
  33. Rustam Gasimov
    Sep 29, 2018
    Thank you for detailed information.
  34. Khuram shahzad
    Aug 10, 2018
    sir ,
    hope you are fine,
    please share difference between lr and lm sitting in mg barker.
  35. Habib
    Aug 07, 2018
    Hi Edvard,
    Thanks for giving information,
    1- what was the difference between Making Capacity and Breaking Capacity?
    2- Can we design our systems according to Making Capacity?
    3- If Maximum Instantaneous Trip set level 15% of rated Breaker than what happened when Short circuit occurred greater than INS trip Set level.
    4- In 3Pole MCCB/ACB without additional C.T Breaker tripped on earth fault what was the reasons?
    5- What is the difference between REF and UREF ground fault?
  36. Ishaq Qamar
    Jul 13, 2018
    Great information.
    I am very thankful to you if you send me the all breaker trip setting level as per different ampare load for data center to fallow the IEC .
  37. CURT
    Jun 23, 2018
    How do the terms, “Ir” and “In” relate to one another in an adjustable breaker? I tested an electronic insulated case breaker the other day and the current setting was adjustable from .5 to 1 and labeled ‘XIn” The instantaneous range was adjustable from 3 to 6 and was labeled “XIr” Is one adjustment based on rating plug and the other based on frame size of the breaker?
  38. Dave Wehage
    Mar 28, 2018
    Good info.
  39. Amir
    Mar 07, 2018
    Thank you so much. I was wondering if you let me know IEC/IEEE standards for short time pick up.
  40. Shahrooz
    Dec 12, 2017
    That was great. helped me a lot.
  41. ramachandra laxman
    Nov 10, 2017
    Very helpful. Good job.
  42. NITIN
    Dec 17, 2016
    LSIG BREAKER RELEASE
  43. Raj
    Nov 22, 2016
    This site is very helpful to electrical engineers like me …thankyou
  44. KARTHICK
    Nov 14, 2016
    Thanks sir……very useful material…….
  45. Gustabo Calderon
    Nov 13, 2016
    Thank you so much Edvard, very good job.
  46. asan masraf
    Jul 05, 2016
    I follow the of articles but if is possible to make these articles available in soft copy.
      Hi Asan, see the button ‘Get PDF’ on your left? That your answer :) To create PDF out of any technical article.
      • Chetan
        Nov 23, 2019
        Great Article
  47. Muneeb Islam
    Jun 22, 2016
    Thank you Edvard, I have been looking for this info for long. I shall inquire about this in detail soon.
    What is the standard testing current injection limits for 400A and 800A MCCB?
    Muneeb Islam
  48. عكرود نبيل
    Jun 15, 2016
    I like your Job, Very very interesting and very helpfull.
    keep better, go on!!
  49. Frank Schraner
    Jun 10, 2016
    Great article, when you don’t do it every day you forget some of this. Having the curve right next to the explanation helps even more THANK YOU! I’m going to print this and keep it with my field work tools.
Leave a Reply to eng. ghassan
thirty seven  −    =  twenty eight