Home / Technical Articles / An example of calculating the technical losses of T&D lines
Introduction to Losses
There are two types of losses in transmission and distribution line.
  1. Technical Losses and
  2. Commercial Losses.
It’s necessary to calculate technical and commercial losses. Normally technical losses and commercial losses are calculated separately.
Transmission (technical) losses are directly effected on electrical tariff, but commercial losses are not implemented to all consumers.
Technical losses of the distribution line mostly depend upon electrical load, type and size of conductor, length of line etc.
Let’s try to calculate technical losses of one of following 11 KV distribution line ;)
Example – 11 kV Distribution Line
11 KV distribution line have following parameters:
  • Main length of 11 KV line is 6.18 km.
  • Total number of distribution transformer on feeder:
    25 KVA = 3 No.
    63 KVA = 3 No.
    100 KVA = 1 No.
  • 25 KVA transformer:
    – Iron losses = 100 W
    – Copper losses = 720 W
    – Average LT line loss = 63W
  • 63KVA transformer:
    – Iron losses = 200 W
    – Copper losses = 1300 W
    – Average LT line loss = 260W
  • 100 KVA transformer:
    – Iron losses = 290 W
    – Copper losses = 1850 W
    – LT line loss = 1380W
  • Maximum amp is 12 Amps.
  • Unit sent out during to feeder is 490335 Kwh
  • Unit sold out during from feeder is 353592 Kwh
  • Normative load diversity factor for urban feeder is 1.5 and for rural feeder is 2.0
Calculation
Total connected load = No’s of connected transformers
Total connected load = (25×3) + (63×3) + (100×1) = 364 KVA
Peak load = 1.732 x Line voltage x Max. amp
Peak load = 264 / 1.732 x 11 x 12 = 228
Diversity factor (DF) = Connected load (in KVA) / Peak load
Diversity factor (DF) = 364 /228 = 1.15
Load factor (LF) =
Unit sent out (in Kwh) / 1.732 x Line voltage x Max. amp. x P.F. x 8760
Load factor (LF) = 490335 / 1.732 x 11 x 12 x 0.8 × 8760 = 0.3060
Loss load factor (LLF) = (0.8 x LF x LF)+ (0.2 x LF)
Loss load factor (LLF) = (0.8 x 0.3060 x 0.3060) + (0.2 x 0.306) = 0.1361
Calculation of iron losses
Total annual iron loss in KWh =
Iron losses in Watts x Nos of TC on the feeder x 8760 / 1000
Total annual iron loss (25 KVA TC) =
100 x 3 x 8760 / 1000 = 2628 KWh
Total annual iron loss (63 KVA TC) =
200 x 3 x 8760 / 1000 = 5256 KkWh
Total annual iron loss (100 KVA TC) =
290 x 3 x 8760 / 1000 = 2540 KWh
Total annual iron loss =
2628 + 5256 + 2540 = 10424 KWh
Calculation of copper losses
Total annual copper loss in KWh =
Cu Loss in Watts x Nos of TC on the feeder LFX LF X8760 / 1000
Total annual copper loss (25 KVA TC) =
720 x 3 x 0.3 × 0.3 × 8760 / 1000 = 1771 KWh
Total annual copper loss (63 KVA TC) =
1300 x 3 x 0.3 × 0.3 × 8760 / 1000 = 3199 KWh
Total annual copper loss (100 KVA TC) =
1850 x 1 x 0.3 × 0.3 × 8760 / 1000 = 1458 KWh
Total annual copper loss =
1771 + 3199 + 1458 = 6490 KWh
HT line losses (Kwh) =
0.105 x (conn. load x 2) x Length x Resistance x LLF / (LDF x DF x DF x 2)
HT line losses = 1.05 x (265 × 2) x 6.18 x 0.54 x 0.1361 /1.5 x 1.15 x 1.15 x 2 = 831 KWh
Peak power losses =
(3 x Total LT line losses) / (PPL x DF x DF x 1000)
Peak power losses = 3 x (3 × 63 + 3 × 260 + 1 × 1380) /1.15 x 1.15 x 1000 = 3.0
LT Line losses (KWh) = (PPL) x (LLF) x 8760
LT Line losses = 3 x 0.1361 x 8760 = 3315 KWh
Total technical losses =
(HT Line losses + LT Line losses + Annual Cu losses + Annual iron losses)
Total technical losses = (831+ 3315 + 10424 + 6490) = 21061 KWh
% Technical loss = (Total losses) / (Unit sent out annually) x 100
% Technical loss = (21061 / 490335) x 100 = 4.30%
% Technical Loss = 4.30%
Jignesh Parmar
43 Comments
  1. shozab
    Jun 11, 2018
    Dear Mr. Jignesh,
    It is nice meeting you, i have gone thru your blogs and find certain excel calculation sheet, actually i m looking for the excel tool for Insulation Coordination as per IEC, IEEE, IS.
    Also Line loss calculation using UG cable at HV (33kV and 11kV)
    You are requested to kindly post the blog on it electrical section or reply to me with returning email. It will be helpful. Alsot kindly let me the buying charges of these.
  2. Adefisoye Oladimeji
    May 23, 2018
    Thank you for your guide on calculating technical loss, however please I need clarification on 0.2 value used in loss load factor calculation and 0.105 used in calculating HT line losses(Kwh). Thank you
  3. Rajesh kumar
    Mar 05, 2018
    Respected sir please provide the information of 8760
    • Vatan Kuncolienkar
      Oct 20, 2019
      8760= Number of hours in a year viz.24×365
  4. batuhan alkan
    Dec 18, 2017
    Ht line losses, peak powe losses and lt line losses calculation has to much calculation mistake can you explain how are you finding 831- 3.0 – 3315
  5. Dhrumit
    Jun 13, 2017
    In Uganda my company get form Umeme 33kv. After line loss I get 28 -29 kg And my transformer set on step 5 last stape but I am not geting 415 volt. So what should I do. Please give me solution if you have.
  6. Ramprabha
    May 22, 2017
    Thank you sir for giving this information. Plz clear. In load factor it’s mentioned 8760. How, what constant.
  7. RAJESH JAIN
    Jan 11, 2017
    Two Distribution transformers of 630 KVA are installed in a residential group housing society. In summer they have 60% loading and in winter they have only 30-35% loading.I want to know in winter if all load will run at one Transformer and one transformer take in idle position , how much losses we can save. LT cables will be same ,only one Transformer will be in idle position for winter period.
  8. sathish
    Dec 03, 2016
    hi friends any buddy have IEC and other standard codes and definition
  9. WILIBALDO TORO
    Oct 17, 2016
    Dear Sir, do you have this article corrected? the question is because I have the same doubts with respect the ecuations and his results.
    thanks in advance
  10. Jeffery B. Ballah
    Jun 06, 2016
    Dear Sir. Thanks for your opportunity provided me to read EEP materials on line. I’m praying that one day I can get a job that will enable me subscribe as a member so that I may be able to download and read these materials daily to improve my skills as a student reading Electrical Engineering in a war ravish country Liberia where there is no research lab and internets But thanks to EEP I’m fighting hard to be myself in this my chosen career.
    Best regards.
  11. Saif ur Rehman
    Apr 08, 2016
    Dear sir
    I want to know that, how to include line losses in grid extension feasibility study please reply
  12. Hafidz
    Apr 03, 2016
    Sir, what refrence for Book of this formula ? is there from iec,ieee,or etc?
  13. vicku
    Aug 18, 2015
    1st of all tell me about max’m Ampere i.e u have taken max’m amp as 12amps , I don’t understand that that max’m ampere is of Line Conductor or Transformer..
    how max’m Ampere Will be Calculated if NOT GIVEN.
    If someone Know the Answer Than Kindly Reply me… at [email protected]
  14. Aliyu Mustapha Rufau
    Aug 14, 2015
    Thanks for the calculations
  15. Temitope
    Aug 10, 2015
    Sir, your materials seem helpful. In your calculation of HT line losses where did the constants 0.105 from and it later transformed to 1.05. please am not too clear on this. what is the name of the constant? or is the constant meant feeder. and if its for 33kv feeder, how what will be the constant
  ⁄  1  =  eight