Home / Technical Articles / An Overview Of Grounding System (Grounded)
An Overview Of Grounded Grounding System
An Overview Of Grounded Grounding System (on photo: Grounded solar panel by J.E.M. Solar; jemsolar.com)
Continued from technical article: An Overview Of Grounding System (Ungrounded)
Topics covered
  1. Solidly grounded system
  2. Resistance grounded system
  3. Reason for resistance grounding
  4. System earthing at EHV level
Figure 3 – Solidly grounded system
Let us assume that R phase (Phase-3 in figure-3) is shorted to ground than:
  • If = Current through shorted path (Fault current)
  • In = Current through neutral to earth connection
  • Icy = Capacitive current returning via the network Phase-2 (Y phase)-earth capacitances
  • IcB = Capacitive current returning via the network Phase-1 (B phase)-earth capacitances
We can write:
If = In + IcY + IcB + Ir // Equation-08
Where Ir = Current returning via network insulation resistance which is always negligible
In case of LV, system voltage available between phase and earth is 415/1.732 = 240V. Resistance of earth plate, grounding connections etc… is of the order of 1.5 Ohms so the earth current is limited to approximately 240/1.5 =160 Amperes. This is not very high magnitude hence any intentional impedance is not required in neutral to earth connection.
As per equation -08 for If one can see that if IcY and IcB is negligible than If = In which is the case in LV system. At 415V level capacitive ground currents are not significant hence we can write:
If = In for solidly earthed LV system // Equation-09
Go back to Index ↑
Figure 4 – Resistance grounded system
In case of MV system (3.3kV onwards to 33kV) voltage between phase and earth is high. Also capacitive charging current is not large enough to compensate the same, so earth fault current is likely to be excessive.
Hence resistance is connected between neutral to ground connection. Current through neutral is limited to 100-400 Amperes.
Restricting the earth fault current / current through neutral
Although all the component of power system at MV level are rated at full MV system fault level, for instance:
Than what is getting protected by restricting the earth fault current/current through neutral?
The neutral of transformer or generator are grounded through impedance, the principal element of which is resistance. This method is used when the earth fault current would be too large if not restricted (e.g.) MV Generators. Here, a resistor is connected intentionally between the neutral and earth. This is to limit the earth fault current.
Go back to Index ↑
The reasons to limit the earth fault current
The reasons to limit the earth fault current are:
1. In rotating electrical machines like motors and generators, if the earth fault current is high, as in the case of solid earthing, the core damage would be high. To limit the damage to the core, machine manufacturers allow only a limited ground fault current.
This is given in the form of a core damage curve.
2. A typical value would be 25A-100A for 1 second. This value is used as a guide in selecting NGR and setting stator earth fault relays in generator protection.
3. Winding damage in rotating electrical machines is not of serious concern (Though windings are rated for full fault level). The repairs to winding damages can be done by the local re-winder. But, in case of core damage, repairs cannot be carried out at site. The machine has to be sent back to the manufacturer’s works for repairs thus resultingin prolonged periods of loss of production.
Since rotating electrical machines are not present in voltage levels from 22kV onwards, these systems are usually solidly grounded.
4. X0/X1 ratio of the system also decides type of neutral earthing. If the corresponding X0/X1 ratio falls under that predefined range. It is a choice between to weather to deal with higher voltage or higher current while under short circuit. Effectively earthed lowers the over voltage limit of the healthy phases while another phase is short circuited to earth. But the ground fault current is very high.
That means system will need a high capacity breaker but insulation system has to be moderate BIL rating.
But as the neutral to earth impedance increases ground fault current reduces but doing so the over voltage factor will rise even up to 1.73 times! So requires a breaker with low current capacity but a HIGH BIL for all insulation system.
Let us assume that R phase (Phase-1 in figure-4) is shorted to ground than:
  • IcB = Capacitive current returning via the network Phase-3 (B phase)-earth capacitances
Repeating equation-8 we can write:
Neglecting Ir and substituting the following:
In = -V1/Rn (Negative sign indicates that capacitive charging & discharging current are in phase opposition to current through neutral)
IcY + IcB = Total capacitive charging and discharging current of healthy phase = j3CwV1 from equation-07
Phasor diagram representation will be:
Phasor Diagram
Figure 5 – Phasor Diagram
So finally after substitution of In and IcY + IcB expression for ground fault current in MV system would be:
If = -V1/Rn + j3CwV1 // Equation -10
Magnitude of ground fault current will be:
|If| = |V1|√(I/Rn)2+ 9C2w2
Go back to Index ↑
In case of HV system (above 33kV) Capacitive ground current is large enough to neutralize the earth fault currents hence no resistance is required in neutral to earth connection.
Solid grounding is universally adopted for following reasons:
1. As we already understood that it is a choice between weather to deal with higher voltage or higher current while under short circuit. At EHV level if we opt for higher voltage than due to higher costof insulation at EHV selection of higher voltage will not be a viable idea.
It is better to opt for higher current by selecting solid grounding.
2. Rotating machines are not present at EHV system so there is no use of limiting the ground fault current as we do in MV system. Even if rotating machines are present because of higher voltage capacitive ground current is also large enough to neutralize the earth fault current.
Go back to Index ↑
References:
  1. Industrial electrical network design guide By Schneider electric
  2. Switchgear protection & power system By Sunil S Rao, Khanna publications
  3. EARTHING: Your questions answered By Geoff Cronshaw
  4. IEEE Recommended Practice for Electric Power Distribution for Industrial Plants
Asif Eqbal
Bachelor of Engineering in Electrical & Electronics engineering, from Manipal University, (Karnataka), India in 2006. Presently involved in the design of EHV outdoor substation and coal fired thermal power plants for more than seven years. Motto of joining EEP as a contributor is to share my little engineering experience and help the budding engineers in bridging the conspicuous gap between academics and Industrial practice. “If you have knowledge, let others light their candles with it, so that people who are genuinely interested in helping one another develop new capacities for action; it is about creating timeless learning processes".
7 Comments
  1. AKHIL S M
    Jul 10, 2020
    Why are we seeing line to ground fault of KA range in 11kv/415v transformer secondary side
  2. BRIJAL MEHTA
    Jul 02, 2019
    Can you explain other possible reasons for using solid grounding in EHV System??
  3. 3nath
    Aug 11, 2016
    Excellent article boss…..
  4. Rajen Kamdar
    Oct 16, 2015
    Article was good.
  5. Sumadeep
    Jul 01, 2014
    Nice
  6. Suresdh babu
    May 21, 2014
    Good article! We know that rotating machines are generally used, up to operating voltage of 11KV/6.6KV, even generators are also used for this voltage. Hence beyond 11KV system generally (and very generally!) solidly earthed system is adopted to make it more economical.
  7. Qaisar
    Mar 27, 2014
Leave a Reply to 3nath
sixty nine  +    =  seventy four
