Search

Premium Membership ♕

Join EEP PREMIUM today to unlock specialized LV/MV/HV technical articles & expert guides. Apply coupon CTS15 to get 15% off the PRO plan.

Home / Technical Articles / Analysis of 11kV Generator Protection Panel Drawings (PDF)

Estimated Study Time: 30 minutes

Generator Protection Drawings

This article provides a comprehensive technical analysis of an 11kV generator protection relay panel +R1 designed to protect a 70MW, 3000RPM synchronous generator operating at a 0.8 power factor. The protection architecture is built upon a redundant, dual-channel philosophy utilizing Group 1 and Group 2 logic to ensure fail-safe operation and continuous availability.

Analysis of 11kV Generator Protection Panel Drawings (PDF)
Analysis of 11kV Generator Protection Panel Drawings (PDF)

At the core of the system are two primary multi-function numerical protection relays (Main 1 and Main 2), designated in the schematics as GPRM and GPRR, which execute a comprehensive suite of ANSI/IEEE standard protection functions.

The protection scheme encompasses critical electrical and mechanical protects, including overall and stator differential protection (87G), 95% and 100% stator earth fault (64G1/64G2), and rotor earth fault (64R) facilitated by a dedicated low-frequency injection unit. The numerical relays also process complex impedance and power metrics to provide loss of excitation (40G), reverse and low forward power (32G/37G), negative phase sequence (46G), overfluxing (24G), and pole slipping (78G) protections.

Additionally, the panel integrates standard voltage and frequency protects (27G, 59G, 81G), dead machine protection (50G), and local breaker back-up/breaker failure protection (50LBB).

To execute protective actions based on the numerical relays’ logic, the panel utilizes dedicated high-speed electromechanical lockout relays segregated by specific fault zones and operational impacts. These trip executions are categorized into Unit Lockout 86A, Turbine Lockout 86B, and Generator Lockout 86C relays, all duplicated across both the Main 1 and Main 2 protection groups.

This analysis deconstructs the generator protection panel’s schematic architecture, advancing from the AC/DC distribution and instrument transformer (CT/PT) circuits through the opto-isolated control inputs, and culminating in a rigorous examination of the lockout relay wiring, interlocks, and tripping matrices governing the generator circuit breaker (GCB), field circuit breaker (FCB), and turbine stop valves.

We all know that the protection panel acts as the “brain” of the generator’s electrical safety system. It continuously monitors the generator’s voltage, current, frequency, and thermal states.

When an abnormal condition (fault) occurs, the relays within this panel detect the anomaly, process the logic, and issue high-speed trip commands to isolate the generator from the grid and shut down the prime mover (turbine).

Here is the download link for the complete PDF document with drawings (56 pages). Open it up, so you can follow the discussion.
Schematics (PDF, 1.5 MB)

Ok, let’s get started!

Table of Contents:

  1. Physical Layout and Equipment Breakdown:
    1. GPRM: Main-1 Protection Relay
    2. GPRR: Main-2 Protection Relay
    3. 64R: Rotor E/F Injection Unit
    4. Lockout Relays: 86A1, 86A2, 86B1, 86B2, 86C1, 86C2
    5. Trip Coil Supervision Relays: 195, 295
    6. Voltage Balancing Relays: 60.11G, 60.22G, etc.
  2. Power System Architecture: The Single Line Diagram (SLD):
    1. Generator and Primary Connections
    2. Current Transformer (CT) Configuration
    3. Voltage (Potential) Transformer (VT or PT) Configuration
  3. Protective Functions and Trip Logic Architecture:
    1. ANSI Protection Codes Utilized
    2. Mapping Protections to Lockout Relays
  4. Auxiliary AC/DC and Measurement Distribution:
    1. AC and DC Distribution
    2. VT Distribution and Voltage Balance
  5. Master Lockout and Tripping Logic:
    1. Unit Lockout Relay – 86A1
    2. Turbine Lockout Relay – 86B1
    3. Generator Lockout Relay – 86C1
    4. Redundant Lockout Relays
    5. GCB Closing & Trip Coil-1 Circuit
    6. GCB Trip Coil-2 Circuit
    7. Generator Field CB and AVR Tripping
    8. Turbine CB Trip and Auto Trip
  6. GPRM/GPRR Input/Output and Annunciation Interfaces:
    1. Opto-Isolated Inputs
    2. Contact Multiplication
    3. Annunciation Contact Distribution
    4. Relay LED Configuration
  7. Conclusion and Summary Notes
  8. Attachment (PDF) 🔗 Download Study ‘HV Shunt Reactors: Dry-Type vs. Oil-Immersed’

1. Physical Layout and Equipment Breakdown

The physical layout and component inventory of the panel are detailed across Sheets 001 through 006. Understanding the hardware is prerequisite to understanding the schematic logic.

The front view of the relay panel, shown on Sheet 001 (Row C, Column 2), displays a standard 19-inch rack-style or flush-mounted layout with the main protection relays situated at eye level for easy operator access, and test blocks/trip relays located below.

The Bill of Materials (BOM) provides specific part numbers and functions. Let us examine the primary front-view equipment listed on Sheet 002:


1.1 GPRM (Main-1 Protection Relay)

Described on Sheet 002, Row E, Column 2-8. This is a Schneider Electric MiCOM P343. It operates on a 110-250V DC auxiliary supply. It accepts nominal 1A/5A CT inputs and 100-120V AC VT inputs.

Crucially, it features 16 Opto (Digital) Inputs and 32 Output contacts, along with 10 RTD inputs and 4 CLIO (Current Loop Input/Output) ports for analog interfacing. This numerical relay acts as the primary defense line.

Figure 1 – Relay panel general arrangement

Relay panel general arrangement
Figure 1 – Relay panel general arrangement

Go back to Content Table ↑


1.2 GPRR (Main-2 Protection Relay)

Described immediately below GPRM on the BOM. It is an identical MiCOM P343 relay. Utilizing two identical relays (rather than two different brands) suggests a completely redundant, parallel protection scheme where either relay can independently trip the unit.

Go back to Content Table ↑


1.3 64R (Rotor E/F Injection Unit)

Found on Sheet 002, Row B, Col 2. Since the generator rotor operates on ungrounded DC, traditional earth fault protection cannot be used. This unit injects a low-frequency AC or DC bias voltage into the rotor circuit.

If an earth fault occurs, the injected circuit completes through the fault, allowing the relay to measure the leakage current and initiate a trip.

Related Study – Trip Signal and Trip Circuit Analysis of the 132kV Line-1 (=E01) Schematics (PDF included)

Trip Signal and Trip Circuit Analysis of the 132kV Line-1 (=E01) Schematics (PDF included)

Go back to Content Table ↑


1.4 Lockout Relays (86A1, 86A2, 86B1, 86B2, 86C1, 86C2)

Listed from Sheet 002, Row C downwards. These are Easun TR241 High-Speed Trip Relays. They are high-burden relays, meaning they draw significant current momentarily to operate, making them immune to false operations from DC system ground faults or capacitive discharges.

They have 16 Make (Normally Open) and 4 Break (Normally Closed) contacts.

The “86” designation is the ANSI standard code for a Master Lockout Relay. Once tripped, they mechanically or electrically latch and must be explicitly reset before the generator can be restarted.

Go back to Content Table ↑


1.5 Trip Coil Supervision Relays (195, 295)

Easun XR351 relays. These relays constantly monitor the continuity of the Generator Circuit Breaker (GCB) trip coils. If a trip wire breaks or the coil burns out while the generator is running, the protection panel would normally be blind to this failure until it unsuccessfully tried to trip.

The XR351 prevents this by raising an alarm immediately upon continuity loss.

Go back to Content Table ↑


1.6 Voltage Balancing Relays (60.11G, 60.22G, etc.)

Alstom MVAPM32 relays. These compare the voltages between two sets of Potential Transformers (PTs). If a fuse blows on one PT, the voltage drops, creating an unbalance. The relay detects this and blocks distance or under-voltage protection elements to prevent a spurious trip.

Figure 2 – Equipment listing

Equipment listing
Figure 2 – Equipment listing

Go back to Content Table ↑


2. Power System Architecture: The Single Line Diagram (SLD)

The electrical topology of the power plant is illustrated on the Single Line Diagram (SLD) across Sheets 002 and 003. This section is vital as it shows where the physical measurements (current and voltage) are taken from the primary HV equipment to feed the secondary LV relays inside the +R1 panel.


2.1 Generator and Primary Connections

On Sheet 003, Row A, Column 1, the SLD legend defines the Generator (G) as a 70MW, 11kV, 3000 RPM (indicating a 2-pole, 50Hz machine), 0.8 Power Factor synchronous generator. The generator is connected to an Isolated Phase Bus Duct (IPB) which carries the 11kV current to the Generator Circuit Breaker (GCB) shown on Sheet 002, Row C, Col 2.

From the GCB, power flows through an Isolator to the Unit Switchgear and ultimately to the 11kV/220kV Generator Transformer (GT) and into the 220kV Main Bus.

A Unit Auxiliary Transformer (UAT) is tapped directly off the 11kV bus between the generator and the GCB. The UAT is rated at 8MVA (11kV/6.9kV) and provides parasitic power to the plant’s auxiliary systems (pumps, fans) while the generator is running.

Figure 3 – The single-line diagram

The single-line diagram
Figure 3 – The single-line diagram

Go back to Content Table ↑


2.2 Current Transformer (CT) Configuration

The accuracy and reliability of the protection relays depend entirely on the CTs. Sheet 003, Row D, Col 1-8 provides the CT schedule. There are several sets of CTs, all featuring a 5000/1A ratio, indicating the generator’s full load current is in the thousands of amperes.

  • CT 1,2,3 (Phase Side IPB): PS (Protection Special) Class CTs used for Generator Protection. They feed the main and backup relays.
  • CT 7,8,9,10,11,12 (Neutral Side IPB): These are installed on the star-point (neutral) side of the generator windings. By comparing the current at the neutral side (CT 7,8,9) with the phase side (CT 1,2,3), the GPRM/GPRR relays perform high-speed Differential Protection (ANSI 87G). If current enters the phase but does not exit the neutral, it indicates an internal stator short circuit.
  • CT 13-18 (AVR): Dedicated to the Automatic Voltage Regulator.
  • CT 19,20,21 (Metering): 0.2 accuracy class CTs dedicated to highly accurate revenue/panel metering (TVM – Trivector Meter).
  • CT 27,28,29: PS Class CTs designated for Overall Differential Protection, which protects the entire zone encompassing the generator and the step-up transformer.

Figure 4 – Current transformers

Current transformers
Figure 4 – Current transformers

Go back to Content Table ↑


2.3 Potential Transformer (PT) Configuration

Voltage signals are derived from PTs listed on Sheet 003, Row C. The primary voltage is 11kV, stepped down to 110V (phase-to-phase) for the relays. The ratio is given as 11kV/√3 / 110V/√3, providing phase-to-neutral voltages to the panel.

  • PT 1,2,3 (Core-1): 3P accuracy class, 30VA burden. Connected in Star/Star. Dedicated purely to protection circuits.
  • PT 1,2,3 (Core-2): 0.2 accuracy class, 60VA burden. Dedicated to metering and synchronization.
  • PT 4,5,6 & 7,8,9: Additional PTs used for redundant protection, AVR Channel 1, AVR Channel 2, and performance testing.

Useful Observation: The strict physical separation of Core 1 (Protection) and Core 2 (Metering) is a critical design mandate. Protection cores are designed to not saturate during fault currents, whereas metering cores are designed to saturate early to protect sensitive delicate meters from high voltage surges.

Figure 5 – Voltage (potential) transformers

Voltage (potential) transformers
Figure 5 – Voltage (potential) transformers

Go back to Content Table ↑


3. Protective Functions and Trip Logic Architecture

The protective philosophy of the panel is mapped out in the Trip Logic Diagrams on Sheet 004 (Group-1) and Sheet 005 (Group-2). These sheets act as Boolean logic flowcharts, illustrating how various ANSI protection functions map to specific Lockout Relays.

The segregation into Group 1 and Group 2 ensures that a failure in one lockout relay or tripping path will not disable the entire protection scheme.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Time Limited! – Save 15% on PRO Membership Plan with coupon CTS15

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
This whitepaper by OMICRON explores the fundamental shift in substation automation testing from hardware-dependent setups to virtualized, software-defined verification.