Home / Technical Articles / Animal deterrents and security in substation
Six-foot black snake the culprit in power outage
The vast majority of electrical utility substations designed to transform transmission voltages to distribution class voltages employ an open-air design.
The configurations may vary, but usually consist of equipment that utilizes polymer or porcelain insulators or bushings to create electrically insulated creepage and dry arc distances between the potential voltage carried by the bus or conductor and the grounded portions of the equipment or structure.
Although these insulators or bushings provide the proper insulation distance for normal operation voltages (AC, DC, and BIL), they do not provide sufficient distances to eliminate bridging of many animals from potential to ground.
This animal bridging situation usually exists at the low side or distribution voltage portion of the substation (12 through 36 kV), but depending on the size and type of the animal, can also affect higher voltage equipment. Utilities have reported that animal-caused outages have become a major problem affecting the reliability and continuity of the electrical system and are actively taking steps to prevent it.
The effects of animal bridging ranges from nuisance trips of the electrical system which may be a momentary occurrence, to faults that may interrupt power for long periods of time. Aside from the inconvenience and reliability aspects of animal-induced outages, there can be damage to the substation equipment ranging from porcelain bushings and insulators that may cost as little as $20.00, to complete destruction of large transformers running into the millions of dollars. There can also be an environmental risk involved with catastrophic failure such as oil spillage from equipment that has ruptured due to electrical faults.
Damage from outages is not limited to the equipment owned by the electrical utility. Many heavy industrial plants such as pulp and paper, petrochemical, and car manufacturers employ processes that are sensitive to interruptions and may result in significant time and money to reestablish production. The proliferation of computers, programmable logic controllers (PLCs), and other electrically sensitive devices in the workplace is also a reliability concern.
In addition to the concern for protecting assets such as substation equipment, improving the reliability of the system, eliminating environmental risks, and ensuring customer satisfaction and loyalty, the conservation of endangered and protected animal species is an issue. It is important to be educated and informed about the species and types of animals that are protected in each individual area or location.
To evaluate the problem and its possible solutions, several aspects need to be investigated:
  • Animal type, size, and tendencies
  • Equipment voltage rating and clearance from electrical ground
  • Natural surroundings
  • Method animals enter substation
  • Influences attracting the animals
  • Barrier methods available to keep the animal out
  • Deterrent methods to repel the animals
  • Insulation options
Animal Types
Clearance Requirements
The following table has been developed to aid in establishing minimum phase-to-ground and phase-tophase clearances for the associated animals. This table is for reference only.
TABLE 1 Typical Clearance Requirement by Animal
Animal TypePhase-to-PhasePhase-to-Ground
Squirrel18″ (450 mm)18″ (450 mm)
Opossum/Raccoon30″ (750 mm)30″ (750 mm)
Snake36″ (900 mm)36″ (900 mm)
Crow/Grackle24″ (600 mm)18″ (450 mm)
Migratory Large Bird36″ (900 mm)36″ (900 mm)
Frog18″ (450 mm)18″ (450 mm)
Cat24″ (600 mm)24″ (600 mm)
Squirrels
In North America, a common culprit causing bridging is the squirrel. Although there are many varieties of squirrels, it can be assumed that the nominal length of a squirrel is 18″ (450 mm). Using this dimension, you can evaluate equipment and clearances to determine areas where bridging could occur between potential and ground or phase-to-phase. Clearances for modern substation equipment rated 35 kV and above will normally be sufficient to eliminate squirrel-caused problems; however, distances between phases and between phase and grounded structures should be examined.
There are several schools of thought regarding the reason squirrels often enter substations. One explanation offered is the proximity of trees and vegetation near the substation site that may attract squirrels. Some utilities report that removal of this vegetation had no effect on the squirrel-caused outages.
Experts have theorized that the animals’ path is predetermined and the construction of a structure will not deter a squirrel from following his intended route. Others believe that the animals are attracted by heat or vibration emitted from the electrical equipment. Regardless of the reason, squirrels are compelled toward intrusion. The entry into the substation does not always occur over, under, or through the outer fence of the site. Squirrels are very adept at traveling along overhead conductors and often enter the substation in this manner. Because of this fact, perimeter barriers are often ineffectual in preventing squirrel entry.
Birds
Birds create several problems when entering an electrical substation. The first and most obvious is the bridging between phase-to-ground or phase-to-phase caused by the wingspan when flying into or exiting the structure. Another problem is the bridging caused by debris used to build nests. Many times material such as strands of conductors or magnetic recording tape may be readily available from the surrounding area and be utilized by the birds. This conductive debris is often dragged across the conductor/busbar and results in flashovers, trips, or faults.
The third problem is contamination of insulators caused by regurgitation or defecation of the birds. When this residue is allowed to remain, it can result in flashovers from potential to ground across the surface of the porcelain or polymer insulator by essentially decreasing the insulated creepage distance. The fourth possibility is commonly known as a “streamer outage.”
Streamers are formed when a bird defecates upon exiting a nest that has been built above an insulator. The streamers may create a path between the structure and conductor/bus, resulting in a flashover. Birds will tend to make nests in substations in an effort to eliminate possible predators from attacking the nest for food. The construction of nests in substations can, in turn, attract other animals such as snakes, cats, and raccoons into the area searching for food.
Snakes
Snakes are a major contributor to substation outages. In some areas, snakes are responsible for virtually all substation wildlife outages. Because of their size and climbing ability, snakes can reach most parts of a substation without difficulty. Snake-proofing substations can sometimes create problems rather than solving them. Snakes typically enter substations hunting birds and eggs. Eliminating these predators can lead to an increase in the bird population inside the substation boundaries.
This bird infestation can then lead to bird-induced problems unless additional measures are taken.
Raccoons
Raccoons are excellent climbers and can easily gain access to substations. Unlike snakes, raccoons will occasionally enter substations for no particular reason except curiosity. Because of their large size, raccoons can easily bridge phase-to-phase and phase-to-ground distances on equipment with voltage ratings up to 25 kV.
SOURCE: C.M. Mike Stine, Sheila Frasier – Animal deterrents/security
  1. Shiv Prasad
    Dec 08, 2021
    I am facing monkey menace in electric sub stations of rating 33KV and 66KV in New Delhi Municipal area it New Delhi India where the monkey population in increasing day by day and the ESS are situated near dense populated areas
  2. Manuel Santos
    Nov 13, 2012
    Sorry! I’m a little late to this party.
    I‘d like to ask a question, where older substations do not meet the (TABLE 1 Typical Clearance Requirement by Animal) what is your opinion on covers for the particular connection point to increase the contact distance so that animals do not cause outages?
  3. ANEESH KUMAR SHANDILYA
    Sep 07, 2011
    It is an informative and a very relevant article. I will like more information on the failures due to reptiles, specifically lizards and rats. In the industries having the indoor switchgear panels used ofor power distribution and motor starters at 33KV/ 11KV/ 6.6 KV/ 3.3 KV with VCB/ SF6 bkrs, the faults occur due to entry of the lizards and rats. They may cause faults also in motor & transformer terminal boxes and enclosed bus ducts. I request you to elobrate on the various recommended practicies to avoid the failures due to entry of the reptiles. This is a common problem in the tropical climate countries.
Leave a Reply to Manuel Santos