Home / Technical Articles / Automatic transfer switch (ATS) between two low-voltage utility supplies
ATS to Emergency / Standby Source
Multiple utility services may be used as an emergency or standby source of power. Required is an additional utility service from a separate source and the required switching equipment.
Automatic transfer switch between two low-voltage utility supplies
Automatic transfer switch between two low-voltage utility supplies (photo by Giffen Switchgear, UK)
Figure 1 shows automatic transfer between two low-voltage utility supplies. Utility source 1 is the normal power line and utility source 2 is a separate utility supply providing emergency power. Both circuit breakers are normally closed. The load must be able to tolerate the few cycles of interruption while the automatic transfer device operates.
Automatic switching equipment may consist of three circuit breakers with suitable control and interlocks, as shown in Figure 2.
Circuit breakers are generally used for primary switching in which the voltage exceeds 600 V. They are more expensive but safer to operate, and the use of fuses for overcurrent protection is avoided.
Figure 1 - Two-utility source system using one automatic transfer switch
Figure 1 – Two-utility source system using one automatic transfer switch
Relaying is provided to transfer the load automatically to either source if the other one fails, provided that circuit is energized. The supplying utility will normally designate which source is for normal use and which is for emergency.
If either supply is not able to carry the entire load, provisions must be made to drop noncritical loads before the transfer takes place. If the load can be taken from both services, the two R circuit breakers are closed and the tie circuit breaker is open.
This mode of operation is generally preferred by the supplying utility and the customer.
The three circuit breakers are interlocked to permit any two to be closed but prevent all three from being closed. The advantages of this arrangement are that the momentary transfer outage will occur only on the load supplied from the circuit that is lost, the loads can be balanced between the two buses, and the supplying utility doesn’t have to keep track of reserve capacity for the emergency feeder.
However, the supplying utility may not allow the load to be taken from both sources, especially because a more expensive totalizing meter may be required. A manual override of the interlock system should be provided so that a closed transition transfer can be made if the supplying utility wants to take either line out of service for maintenance or repair and a momentary tie is permitted.
If the supplying utility will not permit power to be taken from both sources, the control system must be arranged so that the circuit breaker on the normal source is closed, the tie circuit breaker is closed, and the emergency-source circuit breaker is open.
If the utility will not permit dual or totalized metering, the two sources must be connected together to provide a common metering point and then connected to the distribution switchboard. In this case, the tie circuit breaker can be eliminated and the two circuit breakers act as a transfer device (sometimes called a transfer pair).
Under these conditions, the cost of an extra circuit breaker can rarely be justified.
Figure 2 - Two-utility source system in which any two circuit breakers can be closed
Figure 2 – Two-utility source system in which any two circuit breakers can be closed
The arrangement shown in Figure 2 only provides protection against failure of the normal utility service.
Continuity of power to critical loads can also be disrupted by:
  1. An open circuit within the building (load side of the incoming service)
  2. An overload or fault tripping out a circuit
  3. An electrical or mechanical failure of the electric power distribution system within the building
It may be desirable to locate transfer devices close to the load and have the operation of the transfer devices independent of overcurrent protection. Multiple transfer devices of lower current rating, each supplying a part of the load, may be used rather than one transfer device for the entire load.
The arrangement shown in Figure 2 can represent the secondary of a double-ended substation configuration or a primary service. It is sometimes referred to as a “main-tie-main” configuration.
Availability of multiple utility service systems can be improved by adding a standby engine-generator set capable of supplying the more critical load. Such an arrangement, using multiple automatic transfer switches, is shown in Figure 3 .
Figure 3 - Diagram illustrating multiple automatic double-throw transfer switches providing varying degrees of emergency and standby power
Figure 3 – Diagram illustrating multiple automatic double-throw transfer switches providing varying degrees of emergency and standby power
Reference: ELECTRICAL ENGINEER’S PORTABLE HANDBOOK – ROBERT B. HICKEY, P.E. (Purchase book at Amazon)
37 Comments
  1. Bill Trombley
    Apr 18, 2021
    I need diagrams to add 2 ATS Switches for, and a generator at, a secondary building. The generator will be providing backup power for that same building as well as the Main building which both 120/240V residential services are fed from. The ATS Switches will be one at each end of the underground conduit feeding the secondary building. Both distribution (Main) panels in the buildings were wired from the secondary of the Meter after the main Service Drop. I hope someone will send diagrams my way. It will be much appreciated, as I have been unable to find them on the internet through regular searches. Thank You!
  2. AMEH WILLIAMS
    Feb 16, 2021
    I NEED A SCHEMATIC DIAGRAM FOR THREE INCOMER 3PHASE AND 1 OUTGOING
Leave a Reply to AMEH WILLIAMS