Home / Technical Articles / Basic Stand-Alone Application of Reclosers
Overcurrent protection
Reclosers are self-contained fault interrupting and reclosing devices, specifically designed for overcurrent protection in secondary distribution systems. Reclosers are situated in selected locations within the overhead distribution network.
Basic Stand-Alone Application of Reclosers (photo credit: Spanish via Flickr)
With the correct protection setting and MV fuse selection coordination, concerning the whole supply loop from the supplying primary distribution substation feeder to the fuse-protected distribution transformer, it is possible to achieve a discriminative fault isolation function.
Traditionally, the recloser units do not have any remote communication facilities. To enhance the system monitoring and restoration facilities, the reclosers can be equipped with remote communicating protection and control units.
The recloser assembly consists of the fault-breaking primary unit, typically pole-mounted with brackets, and a control cabinet mounted near the ground level. Both three-phase and single-phase units are used, depending on the secondary distribution operation and protection philosophy. The current measuring is carried out with internally mounted bushing current transformers.
The switching device is typically either a vacuum-type or oil-type of a circuit breaker with nominal currents up to 1250A and a rated voltage up to 38kV. The breaking capacity of the circuit breaker can reach up to 16kA.
Figure 1 – Typical recloser’s breaking unit (vacuum type) on the left and control cabinet on the right
ABB's recloser type 'OVR-3' - A three phase 15-38 kV, 630-1250 A
Figure 1 – ABB’s recloser type ‘OVR-3’ – A three phase 15-38 kV, 630-1250 A, magnetic actuated, no oil or SF6, and no electronics on the HV side, PCD controller with power supply capable of 48-hour carryover
Automatic fault isolation functionality
Following principal system diagrams describe one basic “stand-alone” application of reclosers.
The below described automatic fault isolation functionality has been achieved with the correct coordination of protection and auto-reclosing scheme settings. Red color marks for a closed switch and green color marks for an open switch.
Furthermore, a solid line marks for an energized line and a dashed line marks for a de-energized line.
In the first diagram, the two feeders are supplied from two separate primary distribution substations with the tie recloser open.
System status just before fault appears in the marked location
Figure 2 – System status just before fault appears in the marked location
The second diagram shows a permanent fault situation on the first feeder. As a result of the fault, the feeder in the substation has made an unsuccessful autoreclosing attempt and has locked out with the breaker open.
System status after unsuccessful autoreclosing of the supplying feeder in substation 1
Figure 3 – System status after unsuccessful autoreclosing of the supplying feeder in substation 1
In the third diagram, the sectionalizing recloser has opened, isolating the faulty section of the feeder.
Sectionalizing recloser has opened, isolating the faulty section of the feeder
Figure 4 – Sectionalizing recloser has opened, isolating the faulty section of the feeder
In the fourth diagram, the tie recloser has closed energizing the healthy section of the looped feeder.
System status after tie recloser has closed
Figure 5 – System status after tie recloser has closed
Gridshield Recloser Overview (VIDEO)
Reference // ABB’s Distribution Automation Handbook – Elements of power distribution systems
  1. Engr Chitambo
    Jul 17, 2015
    well keep up the good works, very useful information indeed
  2. suraj
    Jun 26, 2015
    very good website
Leave a Reply to suraj