Home / Technical Articles / 4 example calculations of compensation for reactive power
Reactive power
First, let’s say some words about basics of the reactive power in system. Reactive current arises in every electrical system. Not only large loads, but smaller loads as well require reactive power. Generators and motors produce reactive power, which causes unnecessary burdens to and power losses in the lines.
4 example calculations of compensation for reactive power (photo credit: mavinelectric.files.wordpress.com)
Figure 1 shows the block diagram for the network loading.
Equivalent circuit diagram of a network with different loading: a) Equivalent circuit; b) Phasor diagram
Figure 1 – Equivalent circuit diagram of a network with different loading: a) Equivalent circuit; b) Phasor diagram
Reactive power is necessary to generate magnetic fields, e.g. in motors, transformers and generators. This power oscillates between the source and the load and represents an additional loading.
Power supply companies and the consumers of this electrical energy are interested in reducing these disadvantages as well as possible. On the other hand, non-linear loads and phase-controlled inverters cause harmonics, which lead to voltage changes and a decrease in the power factor. In order to reduce these harmonics, series resonant (filter) circuits are used.
Now, let’s take few examples to calculate the following:
  1. Determination of Capacitive Power
  2. Capacitive Power With k Factor
  3. Determination of Cable Cross-Section
  4. Calculation of the c/k Value
Example 1 – Determination of Capacitive Power
A load has an effective power of P = 50 kW at 400 V and the power factor is to be compensated from cosφ = 0.75 to cosφ = 0.95. Determine the required capacitive power. The power and current before compensation are:
S1 formulae
The power and current after compensation are:
S2 formulae
The required capacitive power  is:
Qc formulae
Go back to calculations ↑
Example 2 – Capacitive Power With k Factor
The capacitive power can be determined with the factor k for a given effective power. The k factor is read from a table 1 – Multipliers to determine capacitor kilovars required for power factor correction (see below) and multiplied by the effective power. The result is the required capacitive power.
For an increase in the power factor from cosφ = 0.75 to cosφ = 0.95, from the table 1 we find a factor k = 0.55:
Required capacitive power Qc
Example 3 – Determination of Cable Cross-Section
A three-phase power of 250 kW, with Un = 400 V, at 50 Hz is to be transmitted over a cable 80 m in length. The voltage drop must not exceed 4% =16 V. The power factor is to be increased from cosφ = 0.7 to cosφ = 0.95. What is the required cable cross-section?
P formulae
The current consumption before compensation is:
Current consumption before compensation
The current consumption after compensation is:
Current consumption after compensation
The effective resistance per unit length for 516 A is:
Effective resistance per unit length
According to Table 2 (see below) we must choose a cable with a cross-section of 4 × 95 mm2. The effective resistance per unit length for 380 A is:
Here, a cable cross-section of 4 × 70 mm2 is required. As this example illustrates, the improved power factor leads to lower costs because of the reduced cross-section.
Example 4 – Calculation of the c/k Value
Given a 150 condenser battery, i.e. 5 stages of 30 each, a supply voltage of 400 V, and an instrument transformer with a k of 500 A/5 A, how large is the c/k value? The ratio c/k is given by.
Ratio c/k formulae
Tables
Table 1 – Multipliers to Determine Capacitor Kilovars Required for Power Factor Correction
Table 2 – Resistance per unit length for (Cu) cable with plastic insulation
References
  1. Analysis and design of low voltage power systems by Ismail Kasikci (Purchase hardcover from Amazon)
  2. Power factor correction – A guide for the plant engineer by EATON
16 Comments
  1. amin
    Feb 16, 2021
    Let’s say we had a heater was drawing 10 Amp before power compensation or power factor correction. What will happen to that specific load after correction? will it still draw 10 Amp right since we can not change the Amp for that specific load. Then how lowering the total Amperage wouldn’t affect that load? On other hand, when we lower the total amp what happens to each specific load in terms of their nominal current?
  2. JoMed
    Apr 10, 2020
    Very informative and detailed
  3. JoMed
    Apr 10, 2020
    Very informative
  4. Zeeshan Bacha
    Feb 01, 2020
    Thanks sir you are improve aur knowledge.
  5. Thanks
    Aug 19, 2019
  6. Yann saidi
    Aug 19, 2019
    Thank you a lot
  7. andda
    Apr 10, 2019
    How do we know how many and what kvar load is needed to compensate reactive power .Is there any table ?
  8. ARNEL CORPUZ
    Jan 08, 2018
    thank you for this. this is very helpful.
  9. Tomáš
    Feb 17, 2017
    Hey, I do not think that the pic b is correct. There are strange angles at Ur.
    cos phi = 1 means 0 deg between current and voltage so it is not capacitave nor reactive load but pure resistive.
    • mensur
      Jan 31, 2020
      yes…..cos= 1
      means there is no reactive power.
      but he is right when we look at the graph diagram, coz of having some degree on cosine.
      thank you sir
      amazing explanation.
  10. Abass
    Jan 24, 2017
    Many thanks Edvard.
  11. Josè Severino Queiroz
    Jan 23, 2017
    This is a good and practical method to get better the performance of the system mainly the losses and voltage regulations. Thank you..
  12. Aleksandar Kovac
    Jan 23, 2017
    very good.
  13. Amine
    Jan 20, 2017
    very nice thank you
  14. gamal
    Jan 20, 2017
    Thank for usefull report
Leave a Reply to amin