Installation options for capacitor banks
In an low voltage electrical installation, capacitor banks can be installed at three different levels:
Capacitor banks – installation options, protection and connection
Capacitor banks – installation options, protection and connection (photo credit: power-star.co.za)
  1. Global installation
  2. Segment (or group) installation
  3. Individual (or single) installation
After installation ways, we’ll discuss about protection and connection of capacitors banks.
This installation type assumes one capacitors compensating device for the all feeders inside power substation.
Global installation of capacitors
Figure 1 – Global installation of capacitors
This solution minimize total reactive power to be installed and power factor can be maintained at the same level with the use of automatic regulation what makes the power factor close to the desired one.
This type of compensation method demands capacitor banks to have wide range of power regulation, which can be determined by 24h measurements at the place of installation of the circuit breaker.
What’s good in this solution //
  1. No billing of reactive energy
  2. This is the most economical solution, as all the power is concentrated at one point and the expansion coefficient makes it possible to optimise the capacitor banks
  3. Makes less demands on the transformer
But, the downsides are :
  • The losses in the cables (RI2) are not reduced.
  • This is not the best solution for large electric systems, especially when the distance between the source and nonlinear receivers is long. The longer distance, the bigger losses in transmission system.
Go back to capacitors installation options ↑
Segment installation of capacitors assumes compensation of a loads segment supplied by the same switchgear. Capacitor bank is usually controlled by the microprocessor based device called power factor regulator.
Beside, segment installation practice demands protection for capacitor banks.
Figure 2 – Segment installation of capacitors
In this case, capacitor banks are connected to the busbars, which supply a group of loads.
  1. No billing of reactive energy.
  2. Makes less demands on the supply feeders and reduces the heat losses in these feeders (RI2) Incorporates the expansion of each sector.
  3. Makes less demands on the transformer.
  4. Remains economical.
But, the downside is : – Solution generally used for very widespread factory supplies.
Put in practice by connecting power capacitor directly to terminals of a device that has to be compensated. Thanks of this solution, electric grid load is minimized, since reactive power is generated at the device terminals.
Individual installation of capacitors
Figure 3 – Individual installation of capacitors
This method does not require controlling devices, since capacitor banks are being switched on and off by means of the same switch as the device.
  2. From a technical point of view this is the ideal solution, as the reactive energy is produced at the point where it is consumed. Heat losses (RI2) are therefore reduced in all the lines.
But, the downsides are:
  1. Capacitor is not being used when the feeder load is not operating.
  2. Most costly solution, given:
    • The high number of installations
    • The fact that the expansion coefficient is not incorporated
Protection and connection of capacitors
Operating device
In the case of loads with ultra-fast cycles (welding machines, etc.), the conventional system for operating capacitors (electromechanical contactors) is no longer suitable. High-speed switching compensation systems using solid state contactors are necessary.
The switching current of a capacitor depends on:
  1. The power of the capacitor
  2. The short-circuit power of the mains supply to which it is connected
  3. Whether or not any capacitor banks that have already been activated are present
Given these parameters, it is essential to use quick make and break operating devices (switch, contactor, etc.). When selecting operating devices, the user must be made aware of the choice of equipment available (for operating capacitors).
Contactors are specially designed by contactor manufacturers for operating capacitors and in particular for assembling automatically controlled capacitor banks. These contactors have auxiliary poles combined in series with preload resistors that will limit the inrush current during activation.
Installation options for capacitors and tips for protection and connection
Installation options for capacitors and tips for protection and connection (photo credit: esugitama.blogspot.rs)
Protection
In addition to the internal protection devices incorporated in the capacitor:
  • Self-healing metallised film
  • Internal fuses
  • Overpressure disconnection devices
it is essential to provide a protection device external to the capacitor.
This protection will be provided by:
  1. Either a circuit breaker:
    • Thermal relay, setting between 1.3 and 1.5 × In
    • Magnetic relay, setting between 5 and 10 × In
  2. Or GI type HRC fuses, rating 1.4 to 2 × In
Example //
In = capacitor nominal current
In = Qc / √3 U
Example: 50 kVAr;  400 V three-phase
In = 50/1.732 × 0.4 = 72 A
Connection – sizing the cables
Current standards for capacitors are defined so that capacitors can withstand a permanent overcurrent of 30%. These standards also permit a maximum tolerance of 10% on the nominal capacitance.
Cables must therefore the sized at least for: Icable = 1.3 × 1.1 (Inominal capacitor)
i.e. Icable = 1.43 × Inominal
References //
  • Reactive energy compensation and power quality monitoring by Legrand
  • Reactive Power Compensation – Master thesis by Jakub Kępka at Faculty of Electrical Engineering
12 Comments
  1. Ayekple Mawuena
    Mar 27, 2021
    Diagram of the capacitor bank
  2. Riaz
    Feb 03, 2020
    capacitor bank position in main distribution swich gear panel
  3. Bunty
    Feb 03, 2020
    H t capacitor bank improve ment for transmission line
  4. Muhammad Abdullah Khalid Seyal
    Feb 02, 2020
    Excellent effort.
  5. Ebenezer Quayson
    Nov 16, 2019
    Please I need help on how to connect capacitor bank. Diagrams and real pictures
  6. Given Mutale
    Aug 03, 2019
    I would to be your agent in Zambia. Our company is dealing in energy management
  7. Maher
    Aug 17, 2018
    Hi Edvard
    I read everything in this website about power savers and capacitors .
    we have 3 phase electricity line
    can you tell me how i can make capacitors bank for this electricity
    regards
  8. Rajarsi Chakraborty
    Mar 26, 2017
    When selecting operating devices, the user must be made aware of the choice of equipment available (for operating capacitors). Can’t understand properly this line. Can u explain pls? TIA.
  9. Servesh yadav
    Mar 26, 2017
    Great article!! detailed one…thanks for posting!
  10. Abderrahmane
    Mar 25, 2017
    how much is the cost benefice
    having capacitors.spare parts+failures+maintenece VS paying the reactive power bill
  11. David Renshaw
    Mar 20, 2017
    Edvard, would you alter the first line of the example to read: In = capacitor current [i.e. not ‘voltage’]
      Hooh, thanks David! Typo fixed!