Commissioning process for LV switchgear

Purchasing low voltage switchgear is not that easy, it’s not like purchasing a new TV or laptop. You have to be very experienced and deadly serious when specifying and ordering LV switchgear, but also during the commissioning and testing. This article is the guidance on the items that should be inspected, checked, and tested during the commissioning of an LV switchgear and associated circuit breakers.

Things you MUST know when commissioning low voltage switchgear and circuit breakers
Things you MUST know when commissioning low voltage switchgear and circuit breakers (photo credit: bakkersliedrecht.com)

The commissioning process for low voltage switchgear and circuit breakers involves evaluations, verifications, and checks that determine whether the proper switchgear and circuit breaker specifications and installation requirements are met.

Tests are also performed that determines whether the electric power distribution system will operate properly and safely after installation.

When the low voltage switchgear and circuit breakers are inspected and tested satisfactorily during the commissioning process, the system should operate in accordance with the manufacturer’s specifications for its maximum useful life.

Table of Content:

  1. Evaluating LV switchgear and CBs upon receipt
    1. Visual Inspection
    2. Verification Against Specifications
      1. Low voltage Switchgear Nameplate
      2. Circuit Breaker Nameplate
  2. Evaluating LV switchgear and CBs installation and testing
    1. Visual Inspection
      1. Suitability
      2. Physical damage
      3. Alignment
      4. Cleanliness
      5. Arc chute assembly
      6. Contacts
      7. Mechanism/Linkage
      8. Lubrication
    2. Mechanical Inspection
      1. Bolt Torque
      2. Door Operation
      3. Rack In – Rack Out
      4. Open/Close Operation
    3. Electrical inspection

1. Evaluating LV switchgear and CBs upon receipt

The installation of low voltage switchgear and circuit breakers is a process that occurs over a period of time. The installation begins with an identified need for a new low voltage power distribution installation (e.g., a new facility). Power is necessary for the new facility to function, so a switchgear and circuit breaker installation is designed. After the design is approved, the switchgear and circuit breakers are ordered.

Once the switchgear and circuit breakers are received from the manufacturer, they must be evaluated to ensure that they are proper for installation.

The purpose of the evaluation is to verify that correct low voltage switchgear and circuit breakers were received from the manufacturer and that the proper installation specifications and parameters were met.

This section will describe how low voltage switchgear and circuit breakers are evaluated upon receipt.

  1. Visual Inspection
  2. Verification Against Specifications

1.1 Visual Inspection

When low voltage switchgear and circuit breakers are received from the manufacturer, a visual inspection should be performed. The purpose of the visual inspection is to verify that the switchgear and circuit breakers that were received from the manufacturer are in good physical condition and that all of the requested parts and accessories are present.

Because of the damage that can occur to the moving parts that are associated with low voltage switchgear and circuit breakers during installation, only a cursory inspection is performed at the receiving point.

During the cursory inspection, the inspection personnel look for obvious equipment damage and determine whether all necessary support equipment (e.g., racking lever, and technical manuals) are present.

A detailed inspection of the low voltage switchgear and circuit breakers is performed when they are completely installed at the site or facility.

Engineer performing verification of LV switchgear against specifications
Figure 1 – Engineer performing verification of LV switchgear against specifications

Go back to Content Table ↑


1.2 Verification Against Specifications

When a new facility or facility modification is at the equipment installation stage, the design of the installation has already been completed. The type of low voltage switchgear and circuit breakers that are selected for a specific power system should be shown in the drawings, prints, or specifications for the installation.

The purpose of verifying low voltage switchgear and circuit breakers against the specifications is to ensure that the equipment that is is being installed meets industry standards.

Generally, the verification against specifications consists of a determination of whether the type and rating of the equipment that is to be installed match the size and type of the equipment that is required for the installation. Usually, this determination is accomplished by reading an electrical plan that identifies the low voltage switchgear and circuit breaker sizes and types.

The Engineer inspects the manufacturer’s nameplate data on each switchgear compartment and circuit breaker, and he compares them to the requirements on the electrical plan to determine whether the correct equipment is being used.

In some situations, the Electrical Engineer must rely on his knowledge of the correct application of switchgear and circuit breakers sizes and types to determine whether the correct equipment is being used. The data sheets that were used to order the switchgear from the manufacturer should also be consulted.

Take a look at the example of the LV switchgear datasheet:

Download Datasheet

Go back to Content Table ↑


1.2.1 Low voltage Switchgear Nameplate

All low voltage switchgears should have a nameplate that is clearly visible on the front of the switchgear. The nameplate should contain manufacturer-type information. The information that describes the type of switchgear should consist of the manufacturer’s name, the type designation, and the serial number.

Because switchgear may contain different assemblies at various voltages, nameplates should be present at each switchgear segment.

CB Nameplate Information

In accordance with ANSI C37, the manufacturer and rating information that should appear on the low voltage switchgear nameplate should contain the following ratings:

  • Rated frequency
  • Rated maximum voltage
  • Rated insulation level
  • Rated continuous current
  • Rated short-time current
  • Rated short-circuit current

LV switchgear is designed for and should be marked with the maximum voltage at which the switchgear can be applied. The rated maximum voltage level of the low voltage switchgear is the highest RMS voltage for which the switchgear is designed, and the rated maximum voltage is the upper limit for operation.

The rated insulation level of low voltage switchgear at each maximum voltage rating is equal to the low-frequency one-minute withstand voltage of 2.2 kV.

Low voltage switchgear nameplate
Figure 2 – Low voltage switchgear nameplate

Low voltage switchgear is designed for and should be marked with the continuous current that the switchgear is capable of carrying and the fault current values that the switchgear is capable of interrupting without damage to the switchgear.

Specific current ratings for low voltage switchgear are as follows:


Rated Continuous Current at 50/60 Hz

The rated continuous current at 50/60 Hz is the amount of current that can be continuously carried by the switchgear primary circuit components (e.g., buses, bus connections) without exceeding switchgear equipment allowable temperature rise.

Examples of switchgear equipment are primary or secondary circuit components, insulation, and switchgear structural components.


The Rated Short-Time Current

The rated short-time current is the designated limit of available current at which the switchgear must interrupt the current within the required time at the rated maximum voltage.

The required time is termed the “rated short-time duty” and corresponds to two periods of one-half second current flow that are separated by a 15-second interval of zero current.

The Rated Short-Circuit Current

The rated short circuit current of low voltage switchgear is the designated limit of available current at the rated maximum voltage that the switchgear must be required to withstand for a period of no less than four cycles.

Go back to Content Table ↑


1.2.2 Circuit Breaker Nameplate

All circuit breakers must have a nameplate that is clearly visible on the front of the breaker. The nameplate should contain circuit breaker manufacturer-type information. The information that describes the type of circuit breaker should contain the manufacturer name, the type designation, and the serial number.

In accordance with ANSI C37, the manufacturer and rating information that should appear on the circuit breaker nameplate should contain the following rating information:

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Good to know: – Save 50% on all video courses with Enterprise plan.

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.