Methods Of Neutral Earthing

Neutral earthing systems are very similar to circuit breakers in that they do nothing until something in the system goes wrong! There are several methods for system earthing which can be generally divided into three main categories: Insulated earthing, Solid earthing (the most common system arrangement), Impedance earthing through resistor and reactanse or arc-suppresion coil (Petersen coil).

Comparison Of Neutral Earthing Methods
Comparison Of Neutral Earthing Methods (photo credit to ISSCO GROUP)

Table of contents:

  1. Insulated earthing
  2. Solid earthing (the most common system arrangement)
  3. Impedance earthing through resistor, reactanse or arc-suppresion coil (Petersen coil)
  4. Comparison table

INSULATED NEUTRAL SYSTEM (No Intentional Earthing)

Insulated neutral system scheme
Insulated neutral system scheme

The neutral is not earthed directly. In reality,the electrical system is earthed through the system capacity to earth.

The earth fault causes a few amperes fault current due to the cable capacitance current, and the voltage of healthy phases will not rise above the line to line voltage. So, the system can operate with present earth fault improving the system continuity and supply.

The detection of fault location is very difficult. The main detection components is a voltmeter. This method is typically used for LV networks.

Go to Index ↑


SOLIDLY EARTHED OR DIRECT EARTHING

Direct earthing scheme
Direct earthing scheme

The neutral of power transformers or generator is directly connected to station ground.

The Fault current = the three phase symmetrical short-circuit current and can rise from 20 to 30 times the nominal current. The over-voltage in the healthy phase will not exceed the line to earth voltage.

No limitation of fault current when the system is solidly earthing.

Go to Index ↑


IMPEDANCE EARTHING

The purpose of this method is to limit the fault current for greater safety. There are three type of impedance earthing through:

  1. Resistor,
  2. Reactance or
  3. Arc suppression coil (petersen coil).

Go to Index ↑


1. EARTHING THROUGH RESISTOR

Earthing through resistor scheme
Earthing through resistor scheme

The neutral is connected to earth through one resistors. The fault current is limited to chosen value: If=V/R

R = resistance value of resistor (W)
V = line to earth voltage (kV)

A system properly earthed by resistor is not subject to destructive transient over voltages.

The reasons for limiting the current by resistor may be one or more of the following:

  • To reduce burning and melting effects in faulted electric equipment,
  • To reduce mechanical stresses in circuits and apparatus carrying fault currents,
  • To reduce electric shocks hazards are blast to personnel caused by stray ground fault currents in the ground return path.
There are two classes, High resistance value or low resistance value, distinguished by the level of ground fault permitted to flow (No recognized standards for the level of earth fault current that defines these two classes).

In practice there is a clear difference.

  • High resistance value typically uses earth fault current levels of 10 A or less.
  • Low resistance value typically uses ground fault current levels above 10 A and up to 3000 A .

Both classes are designed to limit the earth fault current and to keep the system free from transient over voltages (maintained to a safe level). However, the high resistance method usually does not require immediate clearing of a earth fault since the fault current is limited to a very low level, the protective scheme associated with high resistance value is usually detection and alarm.

The low resistance method has the advantage of immediate and selective clearing of the earthed circuit, but requires that the minimum earth fault current be large enough to positively actuate the applied earth fault relay.

Go to Index ↑ | Go to Earthing through impedance ↑


2. EARTHING THROUGH REACTANCE

Earthing through reactanse scheme
Earthing through reactanse scheme

The neutral is connected to earth through reactor .

The ground fault that may flow is a function of the neutral reactance, the level of the fault current is often used as a criteria for describing the degree of grounding.

In this method the ground fault current should be at least 60% of the three phase fault current to prevent serious transient overvoltages. This is considerably higher than the level of fault current desirable in the system using resistor, and therefore reactance grounding is usually not considered as an alternative to the system using resistor.

This system is used when the system neutral transformer is not available (DELTA connected system) in such case the reactor is used as transformer grounding to obtain the neutral .

Go to Index ↑ | Go to Earthing through impedance ↑


3. EARTHING THROUGH ARC-SUPPRESSION COIL (Petersen Coil)

Earthing through arc-suppresion coil scheme
Earthing through arc-suppresion coil scheme

An earthing reactor connected between the neutral of a system and earth and having a specially selected, relatively high value of reactance in such that the reactive current to earth under fault conditions balances the capacitance current to earth flowing from lines so that the earth current at the fault is limited to practically zero

If the ground fault is in air, such as an insulator flash-over, it may be self extinguishing. This method of grounding is used primarily on 110 kV systems, consisting largely of overhead transmission or distribution lines.

Since systems of such construction are rarely used in industrial or commercial power systems.

Go to Index ↑ | Go to Earthing through impedance ↑


Comparison Table

Methods Of Neutral Earthing
Methods Of Neutral Earthing

X0: Zero-Sequence reactance of the system
X1: Positive-Sequence reactance of the system
R0: Per phase zero-sequence resistance of the system
XC0: Distributed per phase capacitive of reactance to ground the system
V: Line to ground voltage

Go to Index ↑

Reference: Microelettrica Scientifica – M.S. Resistances

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

7 Comments


  1. stanley
    Nov 25, 2021

    the Peterson coil is used above the operating conditions of 110kv, while the resistance earthing is reduced to 33kv and below


  2. Kate Sambhaji S
    Aug 12, 2018

    Thanks for these article of earthing methods and comparison. Select of the earthing method also can do these article using fault level calculator and then.
    I except more articles in details so that fundamental is clear
    Thanks
    Kate


  3. c.shanmugam
    Jul 08, 2015

    how to earthing a swimming pool


    • Grilow
      Jun 04, 2019

      how to earthing a swimming pool – any help please


  4. arun
    Feb 17, 2015

    Superb initiative to help engineers


  5. bobishmp
    Sep 17, 2013

    A Neutral free 1:1 transformer can actually protect us? In such a system can i touch the phase line while standing on the roof? Please clear my confusion..!


    • Aqeel Mohammed Hammadi
      Nov 10, 2023

      No you can not touch live lines in unearthed network because you may get shocked due to the capactive current .

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context