Home / Technical Articles / Conductor Types Used For Overhead Lines
Aluminium and its alloys conductor steel reinforced
The international standards covering most conductor types for overhead lines are IEC 61089 (which supersedes IEC 207, 208, 209 and 210) and EN 50182 and 50183 (see Table 1).
Conductor Types Used For Overhead Lines (on photo: Transmission Line 69KV Upper and 25KV Lower Near Cypress Area, Canada – by Wolf Read via Flickr)
For 36 kV transmission and above both aluminium conductor steel reinforced (ACSR) and all aluminium alloy conductor (AAAC) may be considered. Aluminium conductor alloy reinforced (ACAR) and all aluminium alloy conductors steel reinforced (AACSR) are less common than AAAC and all such conductors may be more expensive than ACSR.
Relevant national and international standards
StandardTitleComment
IEC 61089Round wire concentric lay overhead electrical stranded conductorsSupersedes IEC 207 (AAC), 208 (AAAC), 209 (ACSR) and 210 (AACSR)
EN 50182Conductor for overhead lines: round wire concentric lay stranded conductorSupersedes IEC 61089 for European use. BSEN 50182 identical
EN 50183Conductor for overhead lines: aluminium–magnesium–silicon alloy wires
BS 183Specification for general purpose galvanized steel wire strandFor earth wire
BS 7884Specification for copper and copper–cadmium conductors for overhead systems
Historically ACSR has been widely used because of its mechanical strength, the widespread manufacturing capacity and cost effectiveness.
For all but local distribution, copper-based overhead lines are more costly because of the copper conductor material costs. Copper (BS 7884 applies) has a very high corrosion resistance and is able to withstand desert conditions under sand blasting.
All aluminium conductors (AAC) are also employed at local distribution voltage levels.
From a materials point of view the choice between ACSR and AAAC is not so obvious and at larger conductor sizes the AAAC option becomes more attractive. AAAC can achieve significant strength/weight ratios and for some constructions gives smaller sag and/or lower tower heights. With regard to long-term creep or relaxation, ACSR with its steel core is considerably less likely to be affected.
Jointing does not impose insurmountable difficulties for either ACSR or AAAC types of conductor as long as normal conductor cleaning and general preparation are observed. AAAC is slightly easier to joint than ACSR.
Figure 1 illustrates typical strandings of ACSR. The conductor, with an outer layer of segmented strands, has a smooth surface and a slightly reduced diameter for the same electrical area.
Conductor arrangements for different CSR combinations
Figure 1 – Conductor arrangements for different CSR combinations
Historically there has been no standard nomenclature for overhead line conductors, although in some parts of the world code names have been used based on animal (ACSR – UK), bird (ACSR – North America), insect (AAAC – UK) or flower (AAAC – North America) names to represent certain conductor types.
Aluminium-based conductors have been referred to by their nominal aluminium area. Thus, ACSR with 54 Al strands surrounding seven steel strands, all strands of diameter d 3.18 mm, was designated 54/7/3.18; alu area 428.9 mm2, steel area 55.6 mm2 and described as having a nominal aluminium area of 400 mm2.
In France, the conductor total area of 485 mm2 is quoted and in Germany the aluminium and steel areas, 429/56, are quoted. In Canada and USA, the area is quoted in circular mils (1000 circular mils 0.507 mm2).
Within Europe standard EN50182 has coordinated these codes while permitting each country to retain the actual different conductor types via the National Normative Aspects (NNAs).
Table below explains the EN 50182 designation system.
Conductor designation system to EN50182:2001
  1. A designation system is used to identify stranded conductors made of aluminium with or without steel wires.
  2. Homogeneous aluminium conductors are designated ALx, where x identifies the type of aluminium. Homogeneous aluminium-clad steel conductors are designated yzSA where y represents the type of steel (Grade A or B, applicable to class 20SA only), and z represents the class of aluminium cladding (20, 21, 30 or 40).
  3. Composite aluminium/zinc coated steel conductors are designated ALxISTyz, where ALx identifies the external aluminium wires (envelope), and STyz identifies the steel core. In the designation of zinc coated steel wires, y represents the type of steel (Grades 1 to 6) and z represents the class of zinc coating (A to E).
  4. Composite aluminium/aluminium-clad steel conductors are designated ALxIyzSA, where ALx identifies the external aluminium wires (envelope), and yzSA identifies the steel core as in 2.
  5. Conductors are identified as follows:
    1. A code number giving the nominal area, rounded to an integer, of the aluminium or steel as appropriate;
    2. A designation identifying the type of wires constituting the conductor. For composite conductors the first description applies to the envelope and the second to the core.
The development of ‘Gap type’ heat-resistant conductors offers the possibility of higher conductor temperatures.
The design involves an extra high strength galvanized steel core, and heat-resistant aluminium alloy outer layers, separated by a gap filled with heat-resistant grease. To maintain the gap, the wires of the inner layer of the aluminium alloy are trapezoid shaped. Depending on the alloys used, temperatures of up to 210°C are possible, with a current carrying capacity of up to twice that of hard-drawn aluminium.
This offers particular value where projects involve upgrading existing circuits.
Resource: Transmission and Distribution Electrical Engineering by Dr C. R. Bayliss CEng FIET and B. J. Hardy ACGI CEng FIET
9 Comments
  1. Noel Bako
    Jul 20, 2021
    just into few small projects, Constructions of power lines using 11m wooden poles
    to construct 11kv distribution lines. this is very helpful to me.
    need more guide lines.
  2. Steven Stonebanks
    Nov 11, 2020
    Hi I am trying to identify a conductor from a river crossing 36 segmented outer 74 aluminium inner and 90 steel core.
  3. Vimal kumar
    Sep 29, 2018
    Zebra Al conductor size
  4. india
    Feb 21, 2018
    Very very useful to us and i was gathered more information in this portal thank you
  5. Raj Kumar G
    Jan 02, 2016
    Hi, Could you help me in understanding how the conductor sizes are decided for substation and transmission line. For example: In a 132KV transmission substation ACSR Zebra is used whereas the transmission line is of ACSR Panther why this difference?
  6. Rajesh
    Jul 29, 2014
    Hi
    Can you help ,
    I need an expert engineer to facilitate a training programme on overhead transmission line maintenance and fault finding., the programme, to be hosted on the last week in September 2014.
    I await your response.
    Kind Regards
    Rajesh
  7. Kumaravel R
    Jan 30, 2014
    Very useful information for design of transmission line.
    • Francisco Távora
      Feb 20, 2021
      Tipos e secções de cabos elétricos nus e de cabos elétricos isolados, usados na INDIA, para redes elétricas de baixa tensão, de11 kV, 33 kV e 66 kV. e respetivas características principais (datasheet).
      Agradecimentos antecipados e melhores cumprimentos (best regards).
      • Francisco Tavora
        Mar 22, 2021
        Dear Sirs,
        For suppervise Final Projects includes in Electrical Engineering degree at Polytechnic Institute of Leiria/Portugal, I await, if possible, availables data sheets with main technical characteristics about standards conductors useds in India for overhead distribution and transmission electric power lines construction..
        Preliminaries thanks and best regards,
        Francisco Tavora
Leave a Reply to Vimal kumar
  −  four  =  3
MV Switchgear Components
