Search

Premium Membership ♕

Join EEP PREMIUM today to unlock professional articles, specialized guides, and 50% discount on academy courses (lifetime access included)

Home / Technical Articles / Current sensors as the eyes of RCD and tips for their correct installation

Estimated Study Time: 10 minutes

Residual current devices (RCDs)

All residual current devices are made up of at least two components. First component act as the eyes of RCD – sensors – must be able to supply an electrical signal which is useful when the sum of the currents flowing in the live conductors is different from zero.

Current sensors as the eyes of RCD and tips for their correct installation
Current sensors as the eyes of RCD and tips for their correct installation (photo credit: NLCPR.com)

Second component, the brain is measurement relay – compares the electrical signal supplied by the sensor with a set-point value and sends, with a possible deliberate delay, the opening order to the associated breaking device.

Let’s talk now about an eyes of residual current device (RCD) – Sensors.


Types of current sensors in RCD operation

Two types of sensors are normally used on AC circuits:

  1. The toroidal transformer, which is the most common for measuring leakage currents.
  2. The current transformers, used in HV and MV and sometimes in LV.

The toroidal transformer

This covers all the live conductors and is thus excited by the residual magnetic field corresponding to the vector sum of the currents flowing through the phases and the neutral. Induction in the toroid and the electrical signal available at the terminals of the secondary winding are thus the image of the residual current.

This type of sensor is used to detect residual currents from a few milliamperes to several dozen amperes.

Toroidal transformer
Figure 1 – Toroidal transformer

Go back to contents ↑


The current transformers (CT)

To measure the residual current of a 3-phase electrical circuit without neutral, three current transformers must be installed as shown in figure 2.

The vector sum of the phase currents yields the residual current
Figure 2 – The vector sum of the phase currents yields the residual current

The three CTs are parallel-connected current generators, causing circulation between A and B of a current which is the vector sum of the three currents and thus the residual current.

This circuit, known as the Nicholson circuit, is commonly used in MV and HV when the earth fault current can reach several dozen or even several hundred amperes.

During use, care must be taken with the CT accuracy class: with CTs of 5 % class, it is prudent not to set earth protection below 10 % of their nominal current. The HV electrical installation standard NF C 13-200 specifies 10%.

Medium voltage SM6 metering cubicle GBC
Figure 3 – Current and voltage transformers in medium voltage SM6 metering cubicle GBC (photo credit: schneider-electric.be)

Go back to contents ↑


Special cases

1. High power supply

The Nicholson CT circuit, which would be useful in LV when the conductors are large cross- section bars or cables for the transmission of strong currents, does not allow, even with coupled CTs, settings that are compatible with protection of people (threshold I∆n ≤ UL / Ru).

There are a number of solutions:

Solution #1

If the problem occurs in a main switchboard downstream of the transformer, the following may be considered:

Either installation of a toroid at the supply end of the installation on the earthing connection of the transformer LV neutral (see fig. 4). This is because, according to the Kirchhoff node law, the residual current detected by (N) is strictly the same as that detected by (G) for a fault occurring in LV distribution,

Toroid N delivers the same information as toroid G
Figure 4 – Toroid N delivers the same information as toroid G

Or installation of a toroid on each outgoer, all parallel-connected to a single relay (see fig. 5). When the measurement relay (normally electronic) only needs a very weak electrical signal to operate, the toroids can be made to operate as “current generators”.

When parallel-connected, they give the image of the vector sums of the primary currents.

Toroids placed on the outgoers and parallel- connected to a single relay compensate the impossibility of placing a toroid on the incomer
Figure 5 – Toroids placed on the outgoers and parallel- connected to a single relay compensate the impossibility of placing a toroid on the incomer

Although this circuit is laid down in the installation standards, the approval of the RCD manufacturer is preferable. However, for discrimination reasons, it is preferable to use one RCD per outgoer.

Go back to contents ↑

Solution #2

If the problem arises with parallel-connected cables which cannot all cross a toroid, a toroid can be placed on each cable (including all the live conductors), and all the toroids can be parallel-connected (see fig. 5).

Layout of toroids on parallel-connected large diameter single-line cables
Figure 6 – Layout of toroids on parallel-connected large diameter single-line cables

However the following must be noted:

  1. That each toroid detects n turns in short-circuit (3 in the figure) which may reduce sensitivity.
  2. If the connections represent impedance differences, each toroid will indicate a false zero phase-sequence current. However proper wiring considerably limits these currents.
  3. That this circuit implies for each toroid that the output terminals S1-S2 be marked according to the energy flow direction. This solution calls for the approval of the RCD manufacturer.

2. High power outgoer

To ensure a reliable, linear toroid “response”, the live conductors must be placed as close as possible to the centre of the toroid so that their magnetic effects are completely compensated in the absence of residual current. In actual fact, the magnetic field developed by a conductor decreases in proportion to distance.

Thus in figure 7 , phase 3 causes at point A a local magnetic saturation and thus no longer has a proportional effect.

Incorrect centering of conductors in the toroid is responsible for its local magnetic saturation at point A, which may be the cause of nuisance tripping
Figure 7 – Incorrect centering of conductors in the toroid is responsible for its local magnetic saturation at point A, which may be the cause of nuisance tripping

The same applies if the toroid is placed near or in a bend of the cables that it surrounds (see fig. 8). The appearance of a stray residual induction, for strong currents, will generate on the toroid secondary a signal that may cause nuisance tripping.

The risk increases as the RCD threshold drops with respect to phase current, particularly on a short-circuit.

The toroid must be far enough from the cable bend so as not to be the cause of nuisance tripping
Figure 8 – The toroid must be far enough from the cable bend so as not to be the cause of nuisance tripping

In problem cases (Max. Iph. / high I∆n), two solutions can be used to counter the risk of nuisance tripping:

  1. Use a toroid that is far larger than necessary, for example with a diameter that is twice the one just right for conductor insertion.
  2. Place a sleeve in the toroid.

This sleeve must be made of magnetic material in order to homogenize the magnetic field (soft iron – magnetic plate), (see fig. 9).

A magnetic sleeve placed around the conductors, in the toroid, reduces the risk of tripping due to the magnetic effects of the current peaks
Figure 9 – A magnetic sleeve placed around the conductors, in the toroid, reduces the risk of tripping due to the magnetic effects of the current peaks

When all these precautions have been taken: centering of conductors,  large toroid, and magnetic sleeve, the ratio max. Ι phase / I∆n may reach 50,000.

Go back to contents ↑


Using an RCD with built-in toroid

It must be pointed out that RCDs with built-in toroids provide contractors and operators with a ready-made solution since it is the manufacturer who studies and works out the technical solutions. This is because he:

  1. Masters the problem of centering the live conductors and, for weak currents, can anticipate and properly distribute several primary turns around the toroid.
  2. Can “operate” the toroid at higher induction in order to maximize the energy sensed and minimize sensitivity to stray inductions (strong currents).

Go back to contents ↑

Reference // Residual current devices in LV by R. Calvas (Schneider Electric)

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

2 Comments


  1. Emmanuel
    Mar 29, 2024

    I am a project supervisor from Nigeria I will like to be your student.


  2. Suhas Buddhisagar
    May 13, 2017

    R/s :

    I am 66 , from India , retired Electrical Engineer, cannot repay your debt as Guru , wish to work as trainee
    with minimum subsistence allowance.

    Regards

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.