Overvoltage problems and prevention

Electric insulation in energized systems is continuously under stress. Electric systems are subject to disturbances of many types which unavoidably produce overvoltages. However, the application engineer has at his command many system design principles which will greatly curb the magnitude of overvoltages.

Eight most damaging overvoltages in industrial systems (root causes and prevention)
Eight most damaging overvoltages in industrial systems (root causes and prevention)

It is important to note that AC systems are subject to many types of overvoltages not to be found in DC systems; hence AC systems deserve more careful consideration of the overvoltage problem.


Overvoltage sources

There are many varied sources of overvoltages of sufficient magnitude to be damaging to the insulation of AC industrial power distribution systems. In this article, the mechanism by which the more prominent overvoltages are created will be described and preventative measures suggested.

Treatment of the following will be included:

  1. Static overvoltage
  2. Physical contact with a higher voltage system
  3. Resonance effects in series inductive-capacitive circuits
  4. Repetitive intermittent short circuits
  5. Switching surges
  6. Forced zero-current interruption
  7. Autotransformer connections
  8. Lightning

Of these, most are the result of effects directly within the electric system itself. In contrast, lightning (a vicious source of an overvoltage) is communicated to the electrical system from nature’s powerhouse in the heavens above.


1. Static overvoltage

Wind-blown sand or dust can become highly charged and impart relatively high voltage to exposed overhead electric conductors. Moving belts running on non-metallic pulleys can also develop high voltages by static means which may, in turn, be communicated to electric system conductors if electric enclosing frames arc improperly grounded.

The rate at which electric charge is communicated to electric system conductors by static means is extremely low. Even rather high-resistance ground connection on the electric system will discharge these static currents to the ground as fast as they are received with negligible overvoltages.

In addition to grounding the electric service system, it is important that electric machine frames and all metallic enclosures which contain electric circuit conductors be effectively grounded (see article below).

Suggested Course – Earthing and Grounding in Power Systems: Calculations, Design and Measurements

Earthing and Grounding in Power Systems: Calculations, Design and Measurements

Go back to the Contents Table ↑


2. Physical contact with a higher voltage system

If the conductors of a high-voltage electrical circuit come in contact with those of a lower voltage circuit, then the same potential will exist on both circuits at the point of contact. If the low-voltage circuit does not have its neutral grounded, its potential will be increased to that of the high-voltage system or flashover will occur.

If the low-voltage system is anchored close to ground potential as by the use of a solidly grounded neutral, high values of current may flow from the high-voltage system, but a much lower voltage will appear than with an isolated neutral system.

Accidental contacts between primary and secondary voltages on industrial systems are guarded against by the use of metal enclosures and metal barriers that separate conductor systems of different operating potentials. In some cases, overhead circuits have both primary and secondary on the same pole, but substantial clearances reduce the danger of accidental contact to a minimum.

Occasional cross-ups have occurred between primary and secondary on overhead circuits, and a few cases are known where failure has occurred between primary and secondary inside a transformer.

Figure 1 – Overvoltage on 480V ungrounded system resulting from contact with a higher voltage system

Overvoltage on 480V ungrounded system resulting from contact with a higher voltage system
Figure 1 – Overvoltage on 480V ungrounded system resulting from contact with a higher voltage system

Figure 1 illustrates this type of fault connection. It can be responsible for dangerous overvoltages on ungrounded low-voltage systems.

The most effective protection against that type of overvoltage is grounding of the low-voltage system with the grounding impedance made low enough to accept the maximum line-to-ground fault current of the high-voltage system without biasing the neutral of the low-voltage system by a dangerous amount.

Go back to the Contents Table ↑


3. Resonance effects in series inductive-capacitive circuits

(Limited to AC systems)

Ungrounded-neutral AC systems are most commonly subject to overvoltages originating from this cause. It is important to recognize that ungrounded-neutral systems are actually capacitively coupled to the ground rather than truly divorced from the ground.

They are ungrounded in the sense that no interconnection with the ground has purposely been made, but every element of the electric system incorporates some capacitance to the ground which constitutes an inherent capacitive impedance interconnection between the electric system conductors and ground.

Every ungrounded electric system contains the essential elements presented in the diagram of Figure 2. The electrical behaviour of any single-phase conductor relative to the ground can be determined by a much simpler equivalent circuit, as indicated in the lower sketch of Figure 2.

Figure 2 – Elemental composition of an ungrounded system

Elemental composition of an ungrounded system
Figure 2 – Elemental composition of an ungrounded system

In terms of this simpler equivalent circuit, it will be possible to understand readily the effect of connecting different types of impedance between line and ground as shown in Figure 3. It becomes evident that the connection of any value of either resistance or capacitance between a single line and the ground produces no dangerous overvoltages.

The potential on the phase to which the impedance is connected progressively diminishes from a normal value to zero. The potential to the ground on the remaining two phase conductors will be increased to full line-to-line value at the time the first phase conductor has been reduced to zero potential.

This represents an overvoltage of only 73%, which is not dangerously high and will normally produce no dangerous effect unless continued for a long time.

The connection of an inductive reactance between line and ground, on the other hand, can be responsible for the production of serious overvoltages to the ground. It is the ratio of the inductive reactance of the line-to-ground circuit to the total capacitive reactance of the system to ground which controls the degree of overvoltage.

The highest overvoltage will occur when these two reactances are equal, and at this point, they may be as much as ten times normal. It is significant to note, however, that over a two-to-one range of reactance, overvoltages of three times normal or more would be produced.

Figure 3 – Overvoltages on ungrounded systems resulting from a high-inductive-reactance connection between line and ground

Overvoltages on ungrounded systems resulting from a high-inductive-reactance connection between line and ground
Figure 3 – Overvoltages on ungrounded systems resulting from a high-inductive-reactance connection between line and ground

The unintentional connection of an inductive reactance between a phase conductor and ground can occur in a number of ways, some of which are illustrated in Figure 4. The operating magnetic coil of a motor starter contactor may be inadvertently connected between phase and ground by a ground short circuit in the control wire to the push-button station or the slip of a maintenance man’s screwdriver.

Any time that the inductive-reactance value (which becomes connected from phase to ground) falls in the danger region indicated in Figure 3, dangerous overvoltages to the ground will be produced which are communicated over the entire metallic conductor system of that operating voltage.

Overvoltages originating from this case can be completely suppressed by a relatively light-resistance ground on the electric system neutral.

Figure 4 – Examples of unintentional high-reactance connections between line and ground (click to zoom)

Examples of unintentional high-reactance connections between line and ground
Figure 4 – Examples of unintentional high-reactance connections between line and ground

A grounding resistor of about the same ohmic value as the total charging capacitive reactance to the ground is sufficient to eliminate overvoltages almost completely. It will be evident that there is good reason to adopt electric system neutral grounding with a much lower value of grounding resistance for other reasons.

Figure 3 has been computed on the basis that the inductive reactance is linear. If this reactance incorporates an iron core which during the mode of operation being considered should encounter magnetic saturation, the performance will be somewhat different. Under such conditions, the effective reactance of the inductive circuit can become much lower than the unsaturated reactance, and the voltage will tend to oscillate automatically between voltage limits which cause the effective inductive reactance to match the capacitive-reactance value.

This character of operation has been named ferroresonance (see a case study). The maximum voltage so developed may not be so high as would be produced by a linear reactor but, may still be in excess of two or three times normal. Substantial overvoltages may result from ferroresonance when the unsaturated reactance is many times the capacitive reactance to the ground.

The application of grounded-Y potential transformers on ungrounded systems with a Y or broken-delta secondary connection can be responsible for damaging overvoltages as a result of resonant or ferroresonant action since the magnetizing reactance of the potential transformers becomes connected from phase conductors to ground.

These system voltage oscillations will not occur if the electric system neutral is grounded. Freedom from this particular type of voltage oscillation can be obtained even with ungrounded-neutral operation by using potential transformers with a line-to-line voltage rating and the application of shunting resistors on the secondary windings as is outlined in Figure 5.

Figure 5 – Grounded-Y broken delta potential transformers for a ground indicator or zero-sequence voltage detector

Grounded-Y broken delta potential transformers for a ground indicator or zero-sequence voltage detector
Figure 5 – Grounded-Y broken delta potential transformers for a ground indicator or zero-sequence voltage detector

To ensure freedom from unwanted line-to-ground ground voltage oscillations:

  1. Select PTs T1, T2 and T3, with the line-to-line rated voltage
  2. Apply a secondary loading resistor with a resistance not greater than 40% of the transformer magnetizing reactance.

Important Note – The loading resistance can be applied to each secondary but will then consume power and liberate heat continuously (Learn more).

Series-capacitor melders are occasionally applied, particularly in the case of large-size machines because of their ability to reduce the kVA demand and improve the operating power factor to substantially unity.

However, the series-capacitor welder presents a definite voltage hazard to an ungrounded-neutral AC supply system. During welder operation, the voltage across both the series capacitor and the welding transformer primary will be several times the rated line-to-line voltage. The physical electric connections and the associated vector voltage relationships are indicated in Figure 6 below.

Figure 6 – Overvoltages on ungrounded systems as a result of o ground contact on a series capacitor welding machine

Overvoltages on ungrounded systems as a result of o ground contact on a series capacitor welding machine
Figure 6 – Overvoltages on ungrounded systems as a result of o ground contact on a series capacitor welding machine

Should a fault to ground occur at the junction between the series capacitor and the welding transformer (point P), the location of ground potential will tend to become that of this junction point instead of the centre of the AC system voltage triangle.

The total system capacitive impedance to the ground would generally be expected to be high, relative to that of the welder series capacitor, and thus offers practically no opposition to this shift in the location of ground potential.

In the case illustrated in Figure 6, it will be evident that the potential of the A-phase conductor may be elevated to about 2000 V to ground, which is about seven times normal. As in the other cases, this overvoltage is communicated to all equipment metallically interconnected at this common operating voltage.

All these resonant inductive-capacitive overvoltage hazards can be eliminated by electric system neutral grounding.

Go back to the Contents Table ↑


4. Intermittent ground faults

Substantial overvoltages can be developed in ungrounded AC industrial systems by sputtering or intermittent ground-faulting connections. The intermittent character of the short-circuit path may be the result of:

  1. Vibration which causes an electrical conductor to make contact intermittently with the ground,
  2. Scattering particles of molten conductor metal which intermittently establishes a conducting path to ground, or
  3. Successive breakdown and seal off of the separating space between conductor and ground.

In the last case involving a fixed separation between conductor and ground, a progressively increasing breakdown voltage across this gap is an essential element in the build-up of severe overvoltages.

Intermittent ground-fault conditions on low-voltage ungrounded-neutral systems have been observed to create overvoltages of five or six times normal quite commonly. An unusual case involved a 480 V ungrounded system. Line-to-ground potentials in excess of 1200 V were measured on a test voltmeter. The source of trouble was finally traced to an intermittent ground fault in a motor-starting autotransformer.

About two hours elapsed while the source was being located, during which time between 40 and 50 motors broke down.

Electric systems which are grounded through reactance of too high an ohmic value (X0 more than ten times X1) are also subject to overvoltage by this same mechanism acting in a little different form. An understanding of the manner in which a discontinuous electric connection can be responsible for the generation of overvoltages can be most easily acquired by examining the case of a sputtering or intermittent line-to-ground fault on an ungrounded-neutral system.

In Figure 7, at A is shown the vector voltage pattern of a three-phase AC system as it would operate under normal balanced conditions. The voltage vectors Ea, Eb, and Ec rotate about the neutral at synchronous speed. The electric neutral is a point of central symmetry and remains constant at ground potential if the individual phase voltages are pure fundamental-frequency sine waves.

Figure 7 – Overvoltages on ungrounded systems due to repetitive momentary contact between one line and ground

Overvoltages on ungrounded systems due to repetitive momentary contact between one line and ground
Figure 7 – Overvoltages on ungrounded systems due to repetitive momentary contact between one line and ground

Should the A-phase conductor become grounded, the system voltage triangle would become displaced as illustrated in B. At the phase position illustrated in B, the A-phase voltage is at its maximum value at which instant the charging current to ground (90° ahead of the voltage) is passing through zero.

In case the short circuit contains a small gap or an arc, the arc current would become extinguished at this point. Note that the trapped charge on the line-to-ground capacitance will tend to maintain the voltage triangle in the same displaced position. In other words, the potential of the neutral (relative to ground) would tend to remain at a DC potential equal to the crest value of the a-c voltage wave.

All this merely says that there will be little tendency for any voltage to reappear across the gap in the short circuit immediately following the current zero which occurs at B.

During the next half-cycle, however, the AC generated voltages will reverse their polarities (vectors rotate 180°), which would cause the three-phase vector voltage pattern to assume the position shown in the upper part of C.

Note that during this one-half cycle time interval, the potential of the A-phase has progressively increased from zero value to about twice the normal line-to-neutral crest voltage relative to ground potential. This value of the line-to-ground potential of the A-phase may be sufficient to break down the gap in the ground-fault circuit and re-establish the connection between the A-phase and ground. If so, the A-phase potential will tend to be suddenly yanked to ground potential.

Inevitably there will be some system reactance in the A-phase conductor to the ground short-circuit point which would result in an oscillation of the A-phase-conductor potential between +2 and −2 at a frequency probably 20 to 100 times normal. If the short circuit consisted of a solid metallic connection, this oscillation would decay to zero, leaving the A-phase conductor at ground potential.

Note that associated with this high-frequency transitory oscillation will be a corresponding transitory charging current to the ground.

This transitory charging current to ground, or restrike current, will again reach zero value when the system voltage swing is at the maximum excursion in the negative direction, as shown in the lower part of C.

Suggested Course – Learn to Read and Analyze Circuit Breaker Schematics and Control Wiring Diagrams

Learn to Read and Analyze Circuit Breaker Schematics and Control Wiring Diagrams

Go back to the Contents Table ↑


5. Switching Surges

Circuit switching operations constitute abrupt changes in circuit parameters and can be responsible for the creation of overvoltages although generally of short duration and not in excess of two to three times normal. It will be important to recognize that normal AC switching interrupters
offer very little opposition to the flow of circuit current during the course of current flow but do act to build up dielectric strength rapidly during a normal current zero and prevent reestablishing current flow during the following half cycle.

As a result of this action, it is unnecessary that the stored magnetic energy in the inductance of the circuit is disposed of during interruption.

Interruption takes place at a normal current zero, at which time the stored magnetic energy is zero. A qualitative understanding of the mechanism whereby such overvoltages are generated will be useful.

Of first consideration is the amount of voltage change that would tend to appear across the switching contacts if they were switched open. For example, in Figure 8, a line-to-line short-circuit condition between phases A and B is illustrated. With the circuit breaker still closed, the potential of a’ and b’ must be common and will lie midway between potentials ea and eb, as indicated in the vector diagram.

With the vector relationships shown in the figure, the current in the faulted circuit will be going through zero, which affords an opportunity for the circuit breaker to make an interruption if the contacts have parted.

If the current flow is interrupted at this current zero, the potential of a’ tends to return to ea while that of point b’ tends to return to eb.

Figure 8 – Overvoltages due to interruption of line-to-line short circuit at current zero

Overvoltages due to interruption of line-to-line short circuit at current zero
Figure 8 – Overvoltages due to interruption of line-to-line short circuit at current zero

There will inevitably be inductive capacitive constants that cause this return to take the form of an oscillation of relatively high frequency. This causes the potential of points a’ and b’ to overshoot their final value by about an equal amount.

In this illustrative example, the potential of point b’ would transitorily swing to a value of 1.73 times normal crest voltage in the positive direction while that of the point a’ would make a corresponding swing to 1.73 times normal crest value in the negative direction.

Circuit breakers that introduce substantial resistance drop during current flow tend to reduce the magnitude of switching transient voltages. As a result of the higher power factor of the short circuit, the point at which a current zero is reached will approach more closely to the point at which a voltage zero would also be reached, which thus lessens the magnitude of voltage that tends to appear across the contacts immediately following current zero.

Another form of switching transient which develops overvoltage primarily on the utilization machine on contact closing is illustrated in Figure 9.

Here illustrated is an open-cycle autotransformer starting arrangement. It has been assumed that 65% voltage has been applied on the starting connection and the machine rotor brought up to near synchronous speed. The motor was then disconnected from the starting tap preparatory to reconnection across full-line voltage.

During this interval, it is possible that the internally generated voltage within the motor has dropped to 50% of the rating and has slipped back in angle so as to be 180° out of phase with respect to the supply system.

Figure 9 – Possible switching overvoltage when motor running breaker closes open-cycle autotransformer start

Possible switching overvoltage when motor running breaker closes open-cycle autotransformer start
Figure 9 – Possible switching overvoltage when motor running breaker closes open-cycle autotransformer start

At this point, the potential difference appearing across each of the three line-switching contacts is one and a half times normal line-to-neutral voltage as indicated by the vector relationships. Suppose that the line-switching unit is now closed and that pole 1 is the first to make contact. The potential of motor terminal R would tend to abruptly assume the potential ea but the inevitable transitory overshoot would carry it on up to 250% normal with respect to ground.

The potential of the motor terminals A and C would tend to be carried along and suffer a transitory excursion to 325% voltage with respect to ground unless contacts 2 and 3 close at almost the same instant as contact 1. Closed-cycle starting arrangements such as reactor starting or Korndörfer autotransformer starting to minimize the overvoltages which may be developed in this manner.

One of the most severe sources of switching overvoltages is associated with the separation of two system sections which have become unsynchronized and are switched apart when the generated voltages in the two sections are nearly 180° out of phase. The elements of this case are illustrated in Figure 10, which shows a synchronous motor that has pulled out of step and the internally generated voltage of which is 180° out of phase with respect to the system.

The main supply system on the left is considered to be operating with grounded neutral and contains a much smaller reactance than the motor circuit shown on the right. All three poles of the switching interrupter have been maintained in a closed position up to the time indicated by the vector diagram.

Figure 10 – Possible overvoltages when interrupting the synchronous motor during out-of-step conditions

Possible overvoltages when interrupting of synchronous motor during out-of-step conditions
Figure 10 – Possible overvoltages when interrupting of the synchronous motor during out-of-step conditions

It has been assumed that, in the course of pull-out operation, the demagnetizing reactive current which has been flaming in the motor stator windings has caused the internally generated voltage ahead of transient reactance in the motor to be depressed to 50% of normal value. With the vector system in the position shown, the current in the A-phase is going through zero, which affords an opportunity for interruption if the contacts have parted.

If the current in the A-phase conductor is interrupted at this point, the potential of the motor A-phase terminal (point a2)will tend to jump to the right to its new steady-state position EA.

The inevitable transitory overshoot will cause its potential to swing about an equal distance to the other side of point EA, as shown by the dotted line. At the maximum of this transitory excursion, the potential of point a2 would reach about 3% times the normal crest to the ground in the positive direction.

In contrast to the examples just cited, the more usual switching operation which is involved in separating a normally operating rotating machine or composite system of rotating machines involves very little switching surge voltage. The systems on both sides of the switching interrupters contain internal sources of generated voltage which are of almost the same magnitude and very close to the same phase position. Very little change in potential tends to occur on either side of the switching device at the time interruption takes place.

Arc-furnace circuits can be sources of rather a severe overvoltage if switched off while an arc is in progress within the furnace. As the primary circuit-breaker contacts part, current at the breaker contacts can be forced to zero while current still continues to flow in the furnace arc.

Suggested Reading – MV/HV switchgear (circuit breaker) switching capability and suitability for specific applications

MV/HV switchgear (circuit breaker) switching capability and suitability for specific applications


Thus the circuit breaker accomplishes an interruption of line current with current flow still continuing in the secondary circuit. As the furnace internal current diminishes, the potential across the furnace arc increases in accordance with the normal inverse volt-ampere characteristic of an arc. The arc voltage progressively increases as the current diminishes and can result in a substantial voltage drop as the arc snaps out.

While this voltage may not be high as referred to in the arc-furnace anode, it still may be many times normal operating voltage and will be reflected to the primary side of the transformer by the turn ratio.

The voltage developed at the transformer high-tension terminals may be dangerously high and sufficient to produce flashover.

Go back to the Contents Table ↑


6. Forced-current-zero interruption

The discussion of switching overvoltages so far has considered interruption only at a normal current zero. The term forced current zero or interruption of current zero is used to describe an interrupting mechanism (be it a fuse, switch, section of small wire conductor, etc.) that has the property of developing a large counter voltage in opposition to current flow which can force current to zero value at a time quite different from the normal inherent current zero of the circuit.

Should any element in an electric circuit have the ability to develop a high potential drop during current flow, the potential so developed would appear on connected circuit conductors. The overvoltages so developed would persist until the stored energy in the inductive elements of the circuits has been dissipated (a current zero has been forced).

A high current short circuit created through a length of small wire conductors can be responsible for developing dangerous overvoltages in this manner. As current builds up in such a circuit, stored magnetic energy is being accumulated in all inductive elements of the circuit. When the fusing point of the conductor is reached, the conductor copper tends to separate into a long string of tiny globules of molten copper with a small arc between adjacent globules.

The total voltage drop across the entire section of the conductor may be several times the normal operating voltage of the circuit. During this interval of overvoltage, the magnitude of the current is being diminished; however, the overvoltage will persist until the magnitude of current has been returned to zero value.

Suggested Reading – Dos and don’ts in operating LV/MV circuit breakers, relays, disconnectors and fuses

Dos and don’ts in operating LV/MV circuit breakers, relays, disconnectors and fuses


Because of the overvoltage problems, the vacuum contact switch finds little application. The vacuum switch tends to instantly shut off the current completely that the contacts part. Unless suitable overvoltage suppressors are associated with such an interrupter, high voltages will be developed if applied in inductive circuits. The overvoltages so produced may be sufficient to spark over the outside of the vacuum switch unless some other portion of the circuit breaks down at a lower voltage.

Current-limiting fuses constitute an example of a forced current interrupter. They possess the property of being able to reduce the current to zero value ahead of a normal current zero. Overvoltages are developed during the operation of such an interrupter.

Go back to the Contents Table ↑


7. Autotransformer connections

Autotransformers for interconnecting two electric systems of different insulation levels should be avoided in industrial systems unless both are solidly neutral grounded. The common metallic interconnection between the two systems which is formed by the autotransformer windings tends to subject the lower voltage system to nearly the same transitory voltages as would be expected on the higher voltage system.

There are some exceptions, and a specific example will serve to illustrate nature.

Should a system be planned which is to operate initially at 2400 V and later be converted to 4160 V with all equipment therein containing insulation levels commensurate with 4100 V operating potential, it would be satisfactory to employ a suitable autotransformer for interconnecting this 2400V system with another 4160 V system.

An unusual variation of autotransformer action which has been responsible for system overvoltages in a number of instances is represented by a transformer with extended windings operating on an ungrounded-neutral system such as illustrated in Figure 11.

Applications of this sort are most often found in test areas or developmental areas which contain multipurpose transformers with a multiplicity of taps to permit a wide variety of output, voltages to be obtained.

If operated with system line voltage impressed across a fraction of the total winding, the vector voltage at the end of the winding extension will be as illustrated in Figure 11 because the volts per turn developed in the winding extension will be exactly the same as the volts per turn in the excited winding.

Figure 11 – Overvoltage on ungrounded systems due to a ground connection on the winding extension of an autotransformer

Overvoltage on ungrounded systems due to a ground connection on the winding extension of an autotransformer
Figure 11 – Overvoltage on ungrounded systems due to a ground connection on the winding extension of an autotransformer

Should the end of the winding extension be inadvertently connected to ground or develop a short circuit to ground, the point of ground potential would tend to move away from the centre of the voltage triangle to the potential of the extreme end of the winding extension resisted only by the high system-to-ground capacitance coupling.

It will be evident that, as a result of this action, the presence of any extended winding would cause the potential of one phase conductor to be elevated to more than 173% of normal operating potential.

The degree of overvoltage may be much more severe if greater amounts of winding extension are present. It is important to realize that these overvoltages would be carried to all apparatus connected to the same metallic system. Thus, a ground short circuit on a winding extension of a transformer in a small test area at one corner of a building might impose overvoltages on all equipment fed from the same load-centre substation which might include half the productive machinery in that building.

As has been true so many times before, grounding of the electric supply system-neutral will cure this type of potential overvoltage also.

A system grounding equipment that makes available a ground-fault current that is equal to or greater than the short-circuit current resulting from the short circuit of the extended winding portion of the offending transformer will keep the system line-to-ground potentials within safe bounds. It is quite generally true that transformers of this character to be found in test areas are of relatively small physical size and do not impose restrictive requirements on the necessary system grounding equipment.

As a matter of fact, on all low-voltage-system equipment (600 V and less) it is the standard practice to ground the neutral solidly.

Suggested Course – Electrical Transformer Theory, Design, Construction, Protection and Maintenance

Electrical Transformer Theory, Design, Construction, Protection and Maintenance

Go back to the Contents Table ↑


8. Lightning

The highest overvoltages to which industrial power systems are subjected are those caused by lightning. Limiting these overvoltages by suitable protective measures is essential if costly equipment failures and service interruptions are to be avoided.


Nature of the overvoltages

A lightning stroke to earth represents the sparkover of a highly charged condenser, a cloud forming one plate, the earth the other, and the air between the dielectric. The initial charge has been estimated to be as high as 1 billion volts, and stroke currents as high as 200,000 amp have been measured.

Although lightning may strike directly at the terminals of outdoor electrical equipment, this can generally be avoided by proper shielding. Thus, the overvoltages usually reach the equipment (both indoor and outdoor) through exposed overhead lines which often bring power to the plant or, in some cases, distribute power within the plant.

Direct Strokes and Induced Surges

Lightning may produce an overvoltage on a transmission line either by a direct stroke to the line or by electrostatic induction from a stroke to earth in the vicinity of the line. The probable maximum voltage appearing on a line by a direct stroke is 15 million volts and for an induced surge, 500,000 volts.

These voltages appear between conductor and ground.

Suggested Reading – 5 most important aspects of external protection against the effects of lightning

5 most important aspects of external protection against the effects of lightning


Wave Shapes

Although the voltage surges produced by lightning have high magnitudes, their duration is very short. It is measured in microseconds (millionths of a second). Typically, the voltage rises very rapidly (in 1 to 10psec) to the maximum or “crest,” value and then decays more slowly, reaching 50% of the crest value in 20 to 150 psec.

As illustrated in Figure 12, the shape of a voltage or current, surge produced by lightning (and those produced artificially for test purposes) is
customarily expressed by two numbers.

Figure 12 – Terms ured to describe voltage and current waves

Terms ured to describe voltage and current waves
Figure 12 – Terms ured to describe voltage and current waves

The first is the time from the “virtual zero” of the wavefront to the time the wave reaches the crest value, while the second number is the time from the virtual zero to the time the voltage or current has decreased to 50 per cent of the crest value. The virtual zero of a wavefront is the intersection with the zero axis of a straight line drawn through the points on the front of the wave which are 30% and 90% of the crest value for a voltage wave and 10% and 90% of crest value for a current wave.

Both times are usually expressed in microseconds. To illustrate, a 95 kV 1½ × 40 psec wave is one that has a crest value of 95 kV, rises to crest value in 134 psec from the time of virtual zero, and decays to 50% of crest value (47.5 kV) in 40 psec from the time of virtual zero.


Travelling Waves

The voltage surge produced on a transmission line by lightning does not appear simultaneously at all points on the line; instead, it appears at successively later intervals of time as the distance from the point of the stroke increases. Furthermore, the magnitude and shape (voltage vs. time) of the surge remain approximately the same at all points of a uniform line but are simply displaced in the time phase.

In effect then the surge which appeared as a voltage-time wave on the line where the stroke occurred becomes two identical voltage-distance waves on the line which travel at uniform velocity in opposite directions from the point of origin.

Neglecting all resistances, it can be shown that:

  1. The voltage waves travel along the conductor without change in magnitude or shape with a velocity equal to 1/√LC  fps, where L is the inductance in Henrys per foot of line and C is the capacitance in farads per foot of line.
  2. A current wave accompanies the voltage wave and is of exactly the same shape, that is, at any instant at any point on the line, the current flowing in the conductor is directly proportional to the voltage from conductor to ground.
  3. The constant of proportionality between the current and voltage is called the surge impedance Z and is equal to √LC ohms, where L is the inductance in henrys for any unit length of the line and C is the capacitance in farads for the same unit length. The current in amperes is equal to the voltage in volts divided by the surge impedance in ohms.

The inductance and capacitance of an overhead line are such that the velocity of a current or voltage wave (called the velocity of propagation) is equal to the velocity of light in free space, which is 984 ft per psec. In most calculations, the round number 1000 is used.

The propagation velocity in a cable varies with its construction, but a typical value is 600 ft per psec.

Go back to the Contents Table ↑

Source: Industrial power systems by D. Beeman

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context