Black Friday Deal💥
Save 20% with a coupon BLCK20 on PRO Membership Plan and all courses at the EEP Academy! Learn from experienced engineers!
Home / Technical Articles / Troubleshooting dead circuit by testing continuity with disconnected supply
Dead circuit testing methods
Dead circuit testing is testing performed with the power disconnected from the circuit. The main benefit of disconnecting power supply while tests with an external energy source are performed is to eliminate hazardous risks to the environment or the person conducting the test.
Troubleshooting dead circuit by testing continuity with disconnected supply (photo credit: visionsensorsmag.com)
Both continuity test and insulation test can be performed in the dead circuit test. Let’s try to describe them in details:
  1. Continuity test
  2. Insulation test
1. Continuity test
This is to be performed on a dead circuit for checking continuity. Using an Audible Continuity Tester can do it. This tester consists of a battery as a source of energy, an audible device, and two test leads.
Figure 1 shows an example of this test with an audible continuity tester.
Continuity test with audio tester
Figure 1 – Continuity test with audio tester
By this test, the continuity of an electrical circuit is checked to ensure that the electrical path is complete. If the path is continuous, then an audio sound is emitted to confirm path continuity and the non-existence of an open circuit. In some devices, along with the audio indication, an LED or some other visual indication is provided.
Similarly, an ohmmeter or multimeter can also be used to check continuity. An ohmmeter or multimeter consists of a battery as a source of energy, along with a meter to display the value of resistance. Figure 2 shows an example of this test with an ohmmeter.
In an ohmmeter, the scale is calibrated from zero to an infinite range of resistance. When the meter shows a zero reading, it indicates that the path between two test leads has zero resistance. This, in turn, indicates that the path is a continuous one.
If the path or the conductor is open, then it will show resistance value as infinite.
Continuity test with ohmmeter
Figure 2 – Continuity test with ohmmeter
In short, continuity testing is used to check the following purposes:
Integrity of cables
  • Integrity of electrical circuit path
  • Integrity of the earthing system (i.e., electrical continuity and low-resistance value to earth)
  • Accurate wiring of a control and power circuit to the correct terminals
  • Differentiate active and neutral conductors before connecting them to a device
  • Check for wrong wiring interconnections between different control and power circuits. Thus indirectly, checking for short circuit paths
  • Integrity of switches, fuses, and other devices
A few words of caution are warranted here. Checking for continuity in a control circuit can give erratic results due to the existence of parallel circuits. It is better to disconnect appropriate terminals to ensure correct results. Continuity test in power circuits can be tricky!!
Often, a circuit where there is an open circuit fault can register excellent continuity with a low power tester or ohmmeter. But when a voltage is applied, current may not flow.
The reason for this is that the circuit may be partially continuous (Example: a partially burnt cable where one or two conductor strands may be making contact) but when feeding a heavy load it will behave as a high impedance.
This type of fault will be detected by testing on load using voltage measurements.
Go back to dead circuit testing continuity methods ↑
2. Insulation test
This is another test performed on a dead circuit only. The objective is to check for insulation of cables or a power circuit. The device used to check integrity of insulation is known as an Insulation Resistance Tester. Generally, this is used during the installation of high voltage power cables and terminations.
In Figure 3, a general motor circuit is shown with breaker, fuses, and overload relay. To check insulation of the circuit (excluding motor), disconnect the power supply by opening the breaker.
Insulation test with insulation resistance tester
Figure 3 – Insulation test with insulation resistance tester
Then, isolate the motor from the circuit through terminals T1, T2, and T3. First checking insulation resistance between earth and T1, then earth and T2, and finally earth and T3 checks insulation resistances of conductors, as well as other devices.
If the insulation resistance of any branch shows zero or a very low reading, then it can be concluded that there is an insulation failure!
This test is also used in fault finding, to check for earthed motors or cables and for checking insulation failure of conductors. Individual phases of three-phase motor winding can be insulation-tested only if all six leads of the winding are brought out. The winding being tested should be connected to the tester’s output with the other two windings connected together and to the earthed frame of the motor.
Where only three leads are available, the insulation of the machine winding as a whole can only be tested with reference to the earthed frame of the motor.
These insulation testers are also often incorrectly called ‘Meggers’ (by manfacturer MEGGER) and have a built-in energy source (either DC generator or battery) to produce test voltages of rating 500 V DC or more.
This is required since the electrical circuit to be tested applies voltage of different ratings.
For example, when the insulation resistance of HV cables is checked, 1000 V minimal voltage is applied, whereas for a domestic circuit 500 V is sufficient for testing.
NOTE! Testing on a live circuit requires extreme caution and should be restricted to LV circuits.
Precautions should be taken to prevent inadvertent contact of the technician with live parts. The probes and tools must be insulated with minimum exposure of conducting parts. This will minimize inadvertent bridging of two terminals which are at different potentials which can cause a short circuit and arcing leading to burn injuries to the technician.
Resource: Practical Troubleshooting of Electrical Equipment and Control Circuits – M. Brown
(Get it from Amazon)
  1. Mak justus
    Sep 14, 2021
    This content was really helpful
  2. Taylor Hansen
    Dec 22, 2020
    I like how you mentioned that the insulation test checks the integrity of insulation cables. My brother needs to fix his power circuit and breaker at his warehouse next month. He should find a professional to do some electrical testing for his facilities.
Leave a Reply to Taylor Hansen
2  +  one  =
ETAP technical webinars