CYBER WEEK OFFER 💥 Save 20% on PRO Membership Plan and Video Courses with the coupon CYM23 (Expires in 2 days).
Home / Technical Articles / The story of designing the electrical part of MV/LV power substation
New MV/LV distribution substation
Designing a new MV/LV distribution substation is somewhat complicated and involves a lot of factors you must take care of. This technical article will try to present the essential steps in starting the design process. The beginning is always the hardest part, but once you learn the principles, it will be much easier for the next substations.
The story of designing the electrical part of MV/LV power substation (photo credit: Elektromont servis Brno, spol. s r.o.)
Generally, the article is based on two main parts. The first part is dedicated to the estimation of load you will have in your project (small factory as an example). The second part in more complicated and involves the various network calculations of short circuit and protection coordination.
Note that many people should be involved in obtaining all the necessary information for the project. A good start would be contacting the power supply utility personnel for sizing of the equipment, calibration of protection devices, the design and verification of the earthing system regarding the supply. Then, collecting “true” information about loads could be a painful job, etc.
Ok, let’s dive into estimations and calculations!
Table of contents:
  1. Estimate of the power (supplied to a small industrial factory)
  2. Calculation of short circuit and coordination of protections
    1. Theory behind calculation of the short-circuit current
    2. Power supply network
    3. Transformer
    4. Cables
    5. Calculation of the short-circuit current
    6. Calculation of the contribution of motors
    7. Calculation of the peak current
    8. Sizing and coordination of the protections
1. Estimate of the power supplied to a small industrial factory
Let’s take a small industrial plant as an example (Figure 1). Production involves a stabilized thermal cycle in the furnace for which reason a total black-out is not possible. The plant is also located in a densely populated area.
Single line diagram of the factory
Figure 1 – Single line diagram of the factory
The starting point for the design is the estimation of the consumption of the various users. If in assessing the required power you were to consider the sum of the rated power of all equipment and users you would get a value that is certainly excessive, for two reasons:
  1. Some equipment might not be used at its full power
  2. The equipment will not all be work at the same time
This is taken into account with two coefficients: the utilization factor Ku and the contemporaneity factor Kc.
The ideal would be to have the actual data, as in the case of renovation of an existing installation for which the load diagrams are available. However, in the case of new projects, the load diagram is unfortunately not available.
Therefore one has to estimate the actual load by using factors derived statistically on homogeneous categories of installations as proposed by CEI Guide 99-4, Annex E, presented below.
Table 1 – Load estimation by using factors derived statistically on homogeneous categories of installations
Type of systemType of environment
Individual housing unitsCivil buildings for housingOffices, shops, warehouses, departmentsHotels, hospitalsMedium and high power industrial plants
Lighting66% of the installed power75% of the installed power90% of the installed power75% of the installed power90% of the installed power
Heating100% of the power of the equipment up to 10A + 50% of the remainder100% of the biggest user + 50% of the remainder100% of the biggest user + 75% of the remainder100% of the biggest user + 80% of the second + 60% of the remainder100% of the biggest user + 75% of the remainder
Kitchens100% of the power of the equipment up to 10A + 30% of the equipment over 10A permanently connected100% of the biggest user + 80% of the second + 60% of the remainder100% of the biggest user + 80% of the second + 60% of the remainder
Motors (with the exclusion of lifts, elevators, cranes, etc.)100% of the biggest motor + 80% of the second motor + 60% of the remainder100% of the biggest motor + 80% of the second motor + 60% of the remainderTo be considered on a case by case basis
Water heatersNo contemporaneity is allowed
Socket outlets100% of the biggest user + 25% of the remainder100% of the biggest user + 25% of the remainder100% of the biggest user + 40% of the remainder100% of the biggest user + 75% of the rooms + 25% of the remainder25% of the user installed
Alternatively you can use table 101 of the Standard EN 61439-2:
Table 2 – Values of assumed loading
Type of loadAssumed loading factor
Distribution: 2 and 3 circuits0.9
Distribution: 4 and 5 circuits0.8
Distribution: 6 and 9 circuits0.7
Distribution: 10 and more circuits0.5
Electric actuator0.2
Motors ≤ 100 kW0.8
Motors > 100 KW1.0
In the example provided, the power used on the main LV switchgear is 732 kVA. Considering the values of the rated power of the transformers available commercially, it can be assumed that two transformers 400 kVA transformers will be installed. Apparently, this assumption would be resulting in a more expensive solution than that with only one 800 kVA transformer.
Nevertheless, that can be justified by the need to have a greater continuity of service in case of failures or maintenance.
In this situation the two transformers are loaded at 92% (732/800=0.92) of their rated power, and in the case of an outage of one of the two, it will still be possible to provide 55% of the required power.
The other features of the substation are:
  1. The substation is powered by a buried cable
  2. The transformers are closed in parallel on the secondary so as to guarantee the power supply of the LV installation by both of them
  3. The size of the internal MV network is less than 400 m
Table 3 – Power consumption per departments
2.1 Theory behind calculation of the short-circuit current
To deal with the theory of calculation of short-circuit currents we will refer to the Standard IEC 60909-0 “Short-circuit currents in three-phase AC systems – Part 0: Calculation of currents”. With reference to the electrical network schematized in Figure 2, a short-circuit is assumed on the load terminals.
The network can be studied and represented by using the resistance and reactance parameters of each electrical component. The resistance and reactance values of must be all related to the same voltage value assumed as a reference for calculating the short-circuit current.
The change from impedance values Z1 referring to a higher voltage (U1) to the values Z2, referring to a lower voltage (U2), takes place using the transformation ratio K = U1/U2 according to the following relationship:
Structure of the electrical network taken for calculation of short-circuit
Figure 2 – Structure of the electrical network taken for calculation of short-circuit
The structure of the electrical network in question can be represented through elements in series. In this way an equivalent circuit is obtained like that shown in the following Figure 3 which makes it possible to calculate the equivalent impedance seen from the fault point.
Equivalent circuit for electrical network
Figure 3 – Equivalent circuit for electrical network
An equivalent voltage source (Ueq) is positioned at the point of the short circuit with the value:
Ueq = c × Un / √3
The factor “c” depends on the system voltage and takes into account the influence of the loads and of the variation in mains voltage. The following is the table taken from Standard IEC 60909-0.
Table 4 – Voltage factor c for the calculation of max. and min. short-circuit currents
 Nominal voltage UnVoltage factor c for the calculation of:
Maximum short-circuit currents Cmax(1)Minimum short-circuit currents Cmin
Low voltage
100 V to 1000V
(IEC 60038, table I)
1.05(3)
1.10(4)
0.95
Medium voltage
> 1kV to 35 kV
(IEC 60038, table III)
1.10 AM1.00
High voltage(2)
> 35 kV
(IEC 60038, table IV)
  1. Cmax Un should not exceed the highest voltage Um for equipment of power systems.
  2. If no nominal voltage is defined CmaxUn = Um or CminUn = 0.90×Um should be applied
  3. For low-voltage systems with a tolerance of + 6%, for example systems renamed from 380 V to 400 V
  4. For low-voltage systems with a tolerance of + 10%
2.2 Power supply network
In most cases, the installation will be supplied by a medium voltage distribution network, for which it is quite easy to obtain the value of the supply voltage UnQ and the initial short-circuit current I”kQ.
On the basis of these data and of a correction coefficient for the change in voltage caused by the short-circuit it is possible to determine the short-circuit direct impedance of the network with the following formula:
ZQ = c × UnQ /( √3 × I”kQ)
For the calculation of the network resistance and reactance parameters, if a precise value for value for RQ is not available, the following approximate formulas can be used:
XQ = 0.995 × ZQ
RQ = 0.1 × XQ
2.3 Transformer
The impedance of the machine can be calculated using the rated parameters of the machine itself (rated voltage UrT; apparent power SrT; short circuit voltage at the rated current in percent ukr) using the following formula:
ZT = (ukr / 100%) (UrT2 / SrT)
The resistive component can be determined by knowing the value of the total losses. PkrT referring to the rated current according to the following relationship:
RT = PkrT / (3 × IrT2)
The reactive component can be determined with the classic relationship:
XT = √(ZT2 – RT2)
2.4 Cables
The impedance value of these connection elements depends on various factors (technical, constructive, temperature, etc.) that condition the linear resistance R’L and the linear reactance X’L. These two parameters expressed per unit of length are provided by the manufacturer of the cable.
Alternatively, reference values can be found in IEC 60909-2. In general, the resistance values are based on a reference temperature of 20 °C. For different operating temperatures θ the following formula makes it possible to relate the resistance value to the operating temperature.
R’= [1 + α (θ – 20)] × R’L20
where α is the temperature coefficient that depends on the type of material (for copper, aluminum and aluminum alloys 4×10-3 holds true with good approximation). Therefore, in very simple terms we have:
RL= L × R’L and XL= L × X’L
with L the length of the cable line.
2.5 Calculation of the short-circuit current
The definition of the short-circuit resistance and reactance values of the main elements forming a circuit allow the short circuit currents in the installation to be calculated.
With reference to Figure 4, with the method of reducing elements in series the following values are determined:
  • The total short-circuit resistance value R = ∑Ri
  • The total short-circuit reactance value X = ∑Xi
Once the two preceding parameters are known, it is possible to determine the total short-circuit direct impedance Z:
Z = √(R2 + X2)
Once the equivalent impedance seen from the fault point has been determined, one can proceed with the calculation of the symmetrical three-phase initial short-circuit current:
I”k3 = c × Un / √3 Z
Symmetrical three-phase initial short-circuit current
Figure 4 – Symmetrical three-phase initial short-circuit current
The three-phase short circuit is generally considered as the fault which causes the highest currents (except in particular conditions).
In the absence of rotary machines, or when their action is diminished, it also represents the permanent short-circuit current and is the value taken as a reference to determine the breaking capacity of the protection device.
2.6 Calculation of the contribution of motors
In the event of a short circuit, the motor starts to function as a generator and powers the fault for a limited time corresponding to the time required to eliminate the energy that has been stored in the magnetic circuit of the motor.
Through an electrical diagram of the motor with its subtransient reactance it is possible to calculate the numerical value of the motor contribution.
In low voltage, the Standard IEC 60909-0 provides the minimum indications for which the phenomenon must be taken into account, it will be:
∑IrM < 0.01 × I”k
where:
  • ∑IrM represents the sum of the rated currents of the motors connected directly to the network where the short circuit occurs.
  • I”k is the initial three-phase short-circuit current determined without contribution of motors.
If it has to be taken into account, the impedance of the motors may be calculated using the formula:
Motor impedance formulae
where:
  • Urm is the rated voltage of the motor
  • IrM is the rated current of the motor
  • SrM is the rated apparent power of the motor (SrM = PrM/(ηrM cosφrM)
  • ILR/IrM is the ratio between the locked rotor current and the rated current of the motor.
The current ILR is often a value that is difficult to obtain an therefore it is common practice to consider this value as a multiple of the rated current of the motor. The typical values of the ratio ILR/IrM vary from 4 to 6.
Finally, for groups of low voltage motors connected via cables we can, with good approximation, use the relationship:
RM/XM = 0.42 with XM = 0.922 ZM
2.7 Calculation of the peak current
The short circuit current I”k can be considered to consist of two components:
  1. A symmetrical component is with sinusoidal wave form and in fact symmetrical in relation to the horizontal time axis.
  2. A unidirectional component iu with exponential trend due to the presence of an inductive component.
    This component is characterized by a time constant τ= L/R (“R” indicates the resistance and “L” indicates the inductance of the circuit upstream of the failure point) and is extinguished after 3-6 times τ.
During the transitional period, the unidirectional component makes the short-circuit current asymmetric, characterized by a maximum value, referred to as the peak value, which is higher than what it would be with a purely sinusoidal magnitude.
In general we can say that, considering the effective value of the symmetrical component of the short-circuit current Ik, the value of the first peak current may vary from:
√2 I”k to 2√2 I”k
After the transitional period, the short-circuit current becomes practically symmetrical. An example of the current trend is shown in the following Figure 5.
Symmetrical component of short-circuit current
Figure 5 – Symmetrical component of short-circuit current
The Standard IEC 60909-0 provides useful indications for calculating the peak current. In particular, it indicates the following relationship:
ip = k × √2 × I”k
where the value of k can be evaluated with the following approximate formula:
k = 1.02 + 0.98 × e-3R/X
or through the following charts that show the value of “k” as a function of the parameter “R/X” or “X/R” (see Figure 6).
Parameter "k" for calculating short-circuit peak current
Figure 6 – Parameter “k” for calculating short-circuit peak current
2.8 Sizing and coordination of the protections
Knowledge of certain parameters is fundamental for sizing the installation. Calculations and the study of protection coordination has been published earlier in several other technical articles, so this won’t be covered here.
Please refer to the following articles:
Properly engineered and installed selective coordination between LV circuit breakers
Proper selection and overcurrent coordination of LV/MV protective devices
Coordination problems in electrical networks that lead to nuisance CB tripping
Sources:
  1. Technical guide The MV/LV transformer substations (passive users) by ABB
  2. Schneider Electric Low voltage expert guides no. 5 – Coordination of LV protection devices
  1. [email protected]
    May 22, 2022
    Great article!
    Could you clarify what K2 symbolises in figure 2?
    After looking in IEC 60909-0 I am unsure whether it represents negative sequence impedance correction factor or a line-to-line short circuit?
    Thanks in advance!
  2. Shrikant
    Oct 06, 2020
    Sir,
    Can we add a Bus coupler at Figure-1 ?
    Regards.
  3. Edvard
    Oct 01, 2020
    Thank you Shashi.
  4. Shashi
    Jan 16, 2020
    Awesome Writing! Have been always a great fan of your great articles.
  5. Sandesh Choudhari
    Jan 16, 2020
    Amazing
Leave a Reply to Sandesh Choudhari
  ⁄  one  =  4