Home / Technical Articles / Differences between Shunt Reactor and Power Transformer
Main Differences
Shunt Reactor and Transformer both appear similar in construction. Reactors are also often equipped with Fans for cooling similar to Power Transformers.
However, there are major differences between the two. While a Power Transformer is designed for efficient power transfer from one voltage system to another, a shunt reactor is intended only to consume reactive VArs (or in other words it can be stated as to produce lagging VArs).
Thus, there are more than one winding on a Power Transformer with magnetic core which carry the mutual flux between the two. In reactor there is just one winding. The core is not therefore meant only to provide a low reluctance path for flux of that winding to increase the Inductance.
In case of a Power Transformer, primary Ampere-Turns (AT) is sum of exciting AT and secondary AT. AT loss (in winding resistance, eddy loss and hysteric loss) is kept to as minimum as possible. Exciting AT is small compared with the secondary AT. Rated current is based on the load transfer requirement.
Detailed view of an iron core divided by air gaps
Magnetizing current is small and is negligible value when compared with the secondary rated current. Further, since mutual flux is main flux which results in transformation, leakage flux is kept small and will be based on fault current limitation.
In case of a Shunt Reactor due to absence of other windings, all primary AT is equal to the exciting AT. Similar to a Power Transformer, loss in AT (in winding resistance, eddy current and hysteresis) are also kept to minimum by design. Magnetizing AT is major component of a Shunt Reactor. Reactor magnetizing current is its rated current.
Since a Shunt Reactor magnetizing current is large, if it is designed with Iron alone as a Power Transformer, there will be large hysteresis loss. Air gaps in Iron core are provided in a Shunt Reactor to reduce this loss and to minimize the remanent flux in the core.
Thus a Shunt Reactor may also be constructed without iron (air-core).
By construction, a Shunt Reactor can be oil immersed or dry type for both with and without iron core.
Dry type Reactors are constructed as single phase units and are thus arranged in a fashion to minimize stray magnetic field on surrounding (in the absence of metallic shielding). When such an arrangement is difficult, some form of magnetic shielding is required and designed with care to minimize eddy current loss and arcing at any joints within the metallic loops. One of the advantages of dry type reactor is absence of inrush current.
Oil immersed reactors can be core-less or with gapped iron core. These are either single phase or three phase design with or without fan cooling. These are installed within tanks which hold oil & act as metallic magnetic shields.
In some cases, a Shunt Reactor may have additional small capacity winding which can provide power for small station power loads. Since Shunt Reactor rating is normally based on MVAr rating, this added station load VA shall be accounted for in designing the Reactor for such applications.
Types of shunt reactors
Shunt reactors are used in high voltage systems to compensate for the capacitive generation of long overhead lines or extended cable networks.
The reasons for using shunt reactors are mainly two
The first reason is to limit the overvoltages and the second reason is to limit the transfer of reactive power in the network. If the reactive power transfer is minimized i. e. the reactive power is balanced in the different part of the networks, a higher level of active power can be transferred in the network.
Reactors to limit overvoltages are most needed in weak power systems, i.e. when network short-circuit power is relatively low.
Voltage increase in a system due to the capacitive generation is:
ΔU(%) = QC x 100 / Ssh.c
where:
Qc is the capacitive input of reactive power to the network
Ssh.c is the short circuit power of the network
With increasing short circuit power of the network the voltage increase will be lower and the need of compensation to limit over-voltages will be less accentuated.
Reactors to achieve reactive power balance in the different part of the network are most needed in heavy loaded networks where new lines cannot be built because of environmental reasons. Reactors for this purpose mostly are thyristor controlled in order to adapt fast to the reactive power required.
Especially in industrial areas with arc furnaces the reactive power demand is fluctuating between each half cycle.
In such applications there are usually combinations of:
  1. Thyristor controlled reactors (TCR) and
  2. Thyristor switched capacitor banks (TSC).
These together makes it possible to both absorb, and generate reactive power according to the momentary demand.
Four leg reactors also can be used for extinction of the secondary are at single-phase reclosing in long transmission lines. Since there always is a capacitive coupling between phases, this capacitance will give a current keeping the are burning, a secondary arc.
By adding one single-phase reactor in the neutral the secondary arc can be extinguished and the single-phase auto-reclosing successful.
Resource: Shunt Reactors and Shunt Reactor Protection – S.R. Javed Ahmed
16 Comments
  1. Rajesh P Kalekar
    Jan 30, 2020
    R/Sir, I have 6.6kv ,31.5micro farad 3 nos. (1450kvar) capacitor connected per phase another point connect with reactor n reactor end point is star contact and it’s unearthed. I would like to to earth it for ref protection.is this correct or wrong method. I will use CT in earth strip for ref protection relay but I have daubt that modification can be happened nonsense tripping. Actually I am not sure so I am discussing please
  2. Nandeeshaiah M.S
    Dec 02, 2019
    Dear Engineer brother, you have provided fruitful electrical engineering information with technically proved information as a ready recon-er, which are very needed in an emergency situation. Keep it up and provide other information in the electrical field.
    Thanks and regard.
  3. Ibrahim
    Sep 04, 2018
    My request is : can you guys help about IBT transformer (lecture notes).
  4. Chirag Rangnani
    May 31, 2018
    Greetings Mr. Edvard Csanyi. Thank you for such a concise and clear article for difference between power transformers and shunt reactors. Can you give a brief detail about the protection system for shunt reactor system?
  5. tony Stewart
    May 22, 2017
    knowing a reactor with inductance L and DCR has a time constant L/DCR what is the highest Q ratio that is practical or safe? As I see it, all DC batteries are low Q underdamped Supercaps and Reactors are low Q chokes. comments?
  6. Carlos Bayer
    Oct 04, 2016
    Dear sir:
    Please your assistance. Typically shunt reactors are wye connected to earth. Some engineers when specify reactors ask for the zero sequence impedance from the manufacturer. However no secondary windings are present on reactors so zero sequence currents cannot be exist because they are not compensated (standard delta- wye or wye- wye transformers allow to flow zero sequence currents when stars are earthed). Is it possible to get the zero sequence impedance?
    Thanks in advance and regards
  7. Prakash G Godbole
    Aug 09, 2016
    Dear Edvard
    The article is quite informarive and useful . i have one query
    can we connect 30 MVAR REACTOR on 60 MVA Transformer
    Will it not consume most of the transformer power .
    ur reply is awaited
    Prakash
  8. kamran
    May 18, 2015
    how to check the oil test in shun reactor
  9. Anantha Kumar Rajamani
    May 07, 2015
    We use 33kV Outdoor Metal Enclosed Capacitor Banks, primarily of 2 types of ratings, namely 5MVAR and 20MVAR in our distribution networks (5 stages of 1MVAR each and 5 stages of 4MVAR each – respectively). A typical stage circuit comprises of:
    HRC Fuses + Stage CB + Overload CTs + Inrush Reactors + the Capacitor Banks connected in double-star configuration.
    Can you please advise, as to how does one arrive at the numerical value of the inrush reactors? Please throw some light.
  10. ramesh shah
    Apr 11, 2015
    Can you please provide circuit diagram of shunt reactor connected to transmission line
  11. Tony
    Aug 19, 2014
    I need Reactor shunt, what your contact person in Indonesian,thanks
    • HARDIK SHAH
      Aug 26, 2015
      Dear Sir,
      Hello.
      Let me introduce myself,My name is Hardik Shah & We are India based company and manufacturing all type of Electric Transformer products.
      As we are top manufacturers of the shunt reactors Oil-Immersed and Air-Core Dry type,I want to expand my business in Indonesia.
      We are top exporter from India for the same product in North America,Europe,Asia-Pacific,South America,Middle east,Africa.
      If you feel any query,please revert without hesitation,we surly workout.
      My website is : http://www.ntplindia.co.in
      With Best regards,
      Hardik Shah
      Director at NTPL.
      +91 99250 33009
      Available on WhatsApp.
  12. K Venkateswar Reddy
    Jul 16, 2014
    Dear Sir,
    I want to know weather Power transformer can be made have a tertiary winding for reactor? If so can I have little details please.
  13. PREMASEKHAR.R
    Dec 22, 2013
    EEP is doing a great job , by publishing technical articles in a nutshell which provides a summary and giving a feeling that we have got in our mind a clear idea about the matter which is explained in the reffered book/s.
    Keep going and we are expecting more and more
    Mr.Edvard
    Congrats for this wonderful job
  14. surendranath
    Sep 19, 2012
    loved this portal it has lots of worthy information i appreciate it and if you want any help i am ready to help you. hats off to your effort
      Thanks Surendranath! You can help in any way, from suggestions to writing technical articles. One thing is sure – 25K+ members will be very gratefull to you!
Leave a Reply to Ibrahim