Home / Download Center / Electrical Engineering Books and Technical Guides / Electricity generation, t&d guides / Effects of imbalances and non-linear loads in electricity distribution system
Development of calculation model
The practical part of thesis implies creation model of distribution network that will be able to demonstrate the effect of different non-linear loads on power quality. Also the comparison data about power losses and voltage drop in the whole network and each component of it will be obtained.
Model overview
The single-line diagram shown in Figure 1 represents designed distribution system. The electric utility distributes power at 110 kV, which in turn feeds a 20.5 kV distribution system via a 20 kV, 3-phase, 50-Hz, 10MVA distribution transformer.
Further mostly 2000 kVA service transformers are used to step the voltage down from 20.5 kV to 0.4 V. Only in one point of the distribution network a transformer with less capacity (100 kVA) is set up.
So called “basic load” is chosen to make procedure of initial data entering to system simpler. However existing model allows easily change initial load value manually.
Designed distribution network circuit
Figure 1 – Designed distribution network circuit (click to expand diagram)
Equivalent circuit with totally linear load is given in Figure 2. Nodes are numbered for network parameters visualization. Model is designed so that it requires predefined power value of the basic load and for each harmonic.
Impedances of the network units are set up as frequency dependant elements.
Different approaches for evaluation of these dependences are chosen. DC resistances and inductances for lines as well as directory data for transformers are represented in Figure 2 below.
Thus obtaining all these initial data the power flow and voltage drop calculations can be done for each harmonic and eventually for summarized distorted voltages and currents. Obviously only harmonic numbers that are present in load spectrum are under consideration.
Equivalent circuit
Figure 2 – Equivalent circuit (click to expand diagram)
Calculation is held into two stages: power flow and voltage in network nodes calculations.
Power flow is calculated starting from customer side. By knowing the power flow inside network the further voltage in nodes is determined. This second stage calculation starts from the supplier point. In order to obtain accurate results two extra iterations are used. Voltage values in every node from previous iteration are set as the initial data.
There is one difference in comparison the first and the rest iterations. First stage implies the rated voltage levels in network nodes. Correspondingly, no-load losses in transformers will remain as rated for this stage.
When calculating real no-load losses in transformers for further iterations the voltage deviation is taken into account in response to following equation:
Real no-load losses in transformers
Where
  • P0 – is no-load losses in a transformer,
  • U2fact – is secondary voltage of a transformer,
  • U2rated – is rated secondary voltage of a transformer.
Proposed calculation model requires the knowledge of network elements impedances for each frequency that is calculated.
Title:Effects of imbalances and non-linear loads in electricity distribution system – Nikita Lovinskiy at Lappeenranta University of Technology, Faculty of Technology, Electrical Engineering
Pages:104
  1. NGET SOVANN
    May 13, 2026
    I would like to thank you for sharing this knowledge with me.
  2. OBIORA Jonah
    Sep 16, 2023
    I will love a research in this area of power
  3. Shantha de Silva
    Dec 11, 2019
    Your articles are concise and informative for field engineers who look for information when they need theoretical analysis and field experiences.
  4. Mamo Damte
    Dec 10, 2019
    Nice distribution transformer load discussion
  5. Santosh Purushottam Patil
    Dec 10, 2019
    Dear sir
    Please sir busbar flow current and cable