Grounding Design Issues

This guide examines issues in the design of AC substation grounding systems. The grounding design for substations constructed on high resistivity soil is specifically examined. Here, potential physical rectification systems are presented and evaluated for their efficacy in terms of safety and cost efficiency.

A Handbook to Solving Problematic Cases in AC Substation Grounding Systems
A Handbook to Solving Problematic Cases in AC Substation Grounding Systems

The CYMGRD program, a finite element analysis tool for AC substation grounding, is utilized for an in-depth evaluation of the various schemes. A supplementary software application is created to execute the formulations of the pertinent AC substation standards (IEEE, IEE, and Turkish National Regulations).

This program’s output is compared with the finite element analysis of high-resistivity-soil rectification techniques to assess the correctness of the formulations in these standards.


Problematic Gounding Case #1

This problem is presented to examine discrepancies across soil models. The uniform soil model is utilized to represent the earth’s structure as a single layer of unlimited thickness.

However, this is not what happens in practice. From a geological standpoint, the Earth is composed of several layers, resulting in differing soil qualities.

To examine this disparity, a real GIS grounding scenario is used, utilizing accurate Wenner four-pin test findings with closely aligned measurement values. The area of the region is constrained, although the resistivity readings of the soil are relatively low.

Additional required data are provided:

  • Maximum fault current in 154kV System: 31,5 kA
  • Fault Current Through the mat: 20 kA (r is taken as 0.65)
  • Minimum area of conductor: 120 mm2 (minimum)
  • Rod diameter (d): 2,5 cm
  • Rod Length (L): 250 cm (minimum)
  • Depth of conductors (h): 50 cm (minimum)
  • Step length: 1 m
  • Fault Duration (ts): 0,5 s
  • Human impedance: 1000 Ω
  • Surface layer resistivity (Crushed rock): 2500 Ω.m (maximum)
  • Surface layer height: 15 cm
  • 74m × 50m Grid size
  • One over head line connected to station
  • Resistivity values which are acquired from Wenner-four-pin test results are given in Table 1 A, B, C are different horizontal paths in the region and D is the vertical path in the center of the region.

Table 1 – Wenner test results for uniform soil problem

a (m)ABCDAverage
2127209179191176.5
4138241185204192
6118236128161160.75
8120242133145160
10122242129165164.5
1212912195160126.25
14133183130140146.5
16152184120172157
18159166148–154.33
20151175103–143
22169206115–163.33
24154222103–159.67
26158152112–140.67
28156170131–152.33
3016019992–150.33
32177230160–189
Total Average:158.51

Two separate solutions are given here. Solution 1 includes a designed grid in a uniform soil model composed of rods and grid conductors given in Turkish standards. First grounding parameters are observed without overhead line effect (current division factor) on the design.

Then, this effect is considered and parameters are recalculated. The enhancement of the design is observed.

Solution 2 includes the same grid configuration except the soil model. In this case, two layer soil model is used and grounding parameters are observed and compared with Solution 1.

Desired design solutions must have GPR around 20kV and R value around 1 Ω according to National Grounding Design Standards with step & touch voltages in safe margin according to IEEE Guide for Safety in AC Substation Grounding IEEE Std. 80.

Solution 1

In order to obtain uniform soil model, Wenner-four-pin test results have to be considered. A graph that is composed of average resistivity values obtained from different electrode spacings is drawn to calculate approximate soil resistivity and it is given in Figure 2.

Since all the results close to each other, taking the average value of all results for different electrode spacings can be used to determine the soil resistivity as it is given in Table 1. Uniform soil resistivity value is computed as 158,51 Ω and in Figure 2, this average value is drawn as a line.

Figure 2 – Sample design soil resistivity determination

Sample design soil resistivity determination
Figure 2 – Sample design soil resistivity determination

An initial grid configuration is designed by the author and it is given in Figure 3 There are 76 rods in this design and total length of grid conductors used in design is 2508 m. With the given grid configuration, Thapar-Gerez method ground resistance (R) is determined to be 1.33 Ω.

On the other hand, FEM analysis compute ground resistance (R) to be 1.11 Ω for the same grid design.

Figure 3 – Sample grid design

Sample grid design
Figure 3 – Sample grid design

Ground potential rise (GPR=R·IG) of the given grid design is computed by ground resistance (1.11 Ω) and grid current (IG = 20kA). Moreover grid current is calculated by division factor (S f = 1), reduction factor (r = 0.65) and decrement factor (Df = 1.0313). These values are chosen according to national standards and none of them are computed explicitly for this specific problem.

From these calculations, GPR is calculated to be 22973 Volts. Maximum permissible touch potential is calculated as 877 Volts and Figure 4 shows the touch, step and surface potential distributions along the grounded area.

Figure 4 – Potential distributions of sample design

Potential distributions of sample design
Figure 4 – Potential distributions of sample design

In Figure 4, step potential distribution is always under maximum permissible step potential (2841 Volts). On the other hand, touch potential in the region is not safe because value of touch potential is bigger than maximum permissible touch potential for most of the points.

In Figure 5, touch potential distribution is given in three dimensional view.

Figure 5 – Touch potential distribution of sample design

Touch potential distribution of sample design
Figure 5 – Touch potential distribution of sample design

In this figure, all regions are in the danger of high touch potential. Therefore, it can be observed that the design has to be enhanced. For the enhancement of design, division factor is recalculated for this special substation configuration without omitting overhead line impedance.

Title:A Handbook for Solving Problematic Cases in AC Substation Grounding Systems – Mustafa Güçlü Aydiner
Format:PDF
Size:2.0 MB
Pages:118
Download:Here 🔗 (Get Premium Membership) | Video Courses | Download Updates

Good Reading – Mechanical Check, Visual Inspection and Electrical Test of the Substation Grounding System

Mechanical Check, Visual Inspection and Electrical Test of the Substation Grounding System (1)

Mechanical Check, Visual Inspection and Electrical Test of the Substation Grounding System (2)

Premium Membership

Get access to premium HV/MV/LV technical articles, advanced electrical engineering guides, papers, and much more! It will help you to shape up your technical skills in your everyday life as an electrical engineer.
50% Discount - Save 50% on all 110+ video courses with Enterprise Membership plan.

More Information

2 Comments


  1. Francisco Távora
    Feb 11, 2026

    Highest, and very opportunes, considerations about earthing systems in electric power substations !


  2. Mohsni abdelmajid
    Apr 14, 2025

    Good coursed

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context